Reducing a range hood vent from 6" to 4"
Hello I have bought a 30" 380 CFM Cosmo range hood and it will be placed on a outside wall. The exhaust collar on the top of the hood is 6". The ducting will only have to travel up 12 to 14" and then a 90 Degree elbow to the outside, can I reduce to a 4" duct going outside?
Not according to code. A 4” pipe only carries 1/3 of what a 6” does.
Bob Boan
Depends on how powerful the fan motor is. One of two things will happen,
- The air must move faster thru the smaller duct
- Less air will move at the same velocity thru the smaller duct
My guess is there will be a combination of both. The 380 CFM rating is based on the static pressure per 100 ft of duct. Since you do not have 100 feet of duct, then the static pressure will be much less than the rated capacity.
Here are some calculations to review
Of course you can. Nobody is holding a gun to your head except maybe Mother Nature. It's not something I would do. The outlet of the appliance determines the minimum duct size after that the length of the duct.
You came to this site to find out the right way to do it.
Mid-grade hoods like that usually overstate their CFM capacity and rarely provide the fan curve you would need to figure this out. You will reduce the capacity significantly if you reduce it to 4". I generally increase the duct one size on these unless the run is super short. Another question you might ask yourself is where the 380 CFM will come from if the fan will really move that much? That's a decent amount of air and you don't want to cause a backdraft at other vented appliances.
Albert Einstein0 -
Look into a real exhaust fan.
Fan Tech!
Don't forget makeup air! Once the building atmospheric pressure heads to zero, air movement slows as do cfm's.
What is the code? I see a code that says that 100 cubic feet/min is required. This fan is 380 so even at 1/3 of that it might be compliant. I'm asking for my own education and am not arguing, thank you.
The fan is 380 — but at very low pressure. Do you have any inf9ormation as to how much back pressure the smaller ducting might cause, and how that will affect the fan performance?
Hi @Scottybm , Backing up a bit, my question is about why you want to go to a 4" duct. Is there limited space to run the duct? If so, you may be able to use rectangular duct that does not restrict flow, but still fits where it needs to. Can you give us more info on what you're facing? Thanks.
Yours, Larry
My kitchen ycontractor (who otherwise did a great job) installed a 4 inch duct for my 380 cfm vent. The fan motor burned out in less than a year. I replaced the duct with the a 7 inch as specified by the manufacturer. The 4 inch duct wouldn't allow the fan to removed the smoke from stir frying or pan searing a steak either. You also have a pretty long duct run and a 90 degree. Go with the 6 inch duct. The 4 inch will significantly hurt the performance.
Aside from logic and experience: RTFM!! Read The Factory Manual!
Cosmo is the marketing name for many products. I picked, at random, a "30 inch 380CFM" job. COS-63175 / 63175S manual from Home Depot site:
Page 14 has multiple restrictions. Insurance and Inspection want you to meet "all" factory requirements. 4-inch caps are banned. Backdraft!!
IIRC, the basic $49 fan for cheap bath or kitchen is 70CFM. IMHO this is hardly enough for a fart, and won't keep up with a busy cook's smoke and steam. That's why you got 380CFM. Which BTW is near half the size of my whole-house heat furnace (850CFM). It needs substantial ducting!
