Derate cast iron boiler by removing sections?
Options
RayWohlfarth
Member Posts: 1,494
I have customer with two cast iron sectional steam boilers in two schools. One has a power burner and the other an atmospheric burner. Due to the leaking sections, the customer wants to remove sections and repipe the boiler. On the one with the power burner, they are going to derate the boiler to 75% and the one with the atmospheric burner, they want to derate it to 66%
My question is
Does that void the boiler certification ie UL?
I know the boiler with the power burner will be oversized by 33% I am thinking they should replace the burner
Is the contractor on the hook for changing the boiler? Do they have to get new tags from the manufacturer?
Thanks
Always looking to learn
Ray Wohlfarth
My question is
Does that void the boiler certification ie UL?
I know the boiler with the power burner will be oversized by 33% I am thinking they should replace the burner
Is the contractor on the hook for changing the boiler? Do they have to get new tags from the manufacturer?
Thanks
Always looking to learn
Ray Wohlfarth
Ray Wohlfarth
Boiler Lessons
Boiler Lessons
0
Comments
-
I'm not sure about certifications, but wouldn't you expect the remaining sections to be questionable if some are already leaking?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1
-
@ChrisJ Thats what I told the owner. He could spend all this money to rearrange the sections and the other sections were exposed to the same conditions
Ray Wohlfarth
Boiler Lessons0 -
And I guess you got the ol "No I'm sure they're fine".RayWohlfarth said:@ChrisJ Thats what I told the owner. He could spend all this money to rearrange the sections and the other sections were exposed to the same conditions
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Not sure about the certifications, but you are going to have a jolly time adjusting the combustion parameters to fit the new fire box geometry. You're the test pilot. Have fun.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
To be fair, not very long ago that was a standard part of setting up any boiler, no?Jamie Hall said:Not sure about the certifications, but you are going to have a jolly time adjusting the combustion parameters to fit the new fire box geometry. You're the test pilot. Have fun.
Look at all of the coal to oil and gas conversions that were done.
As far as I know on large commercial boilers everyone has to set the burners up from scratch.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
-
@RayWohlfarth , you and @ChrisJ are correct. If all they want to do is remove leaking sections, and you do so, you own it. They need to completely replace these boilers.
If the existing boilers are oversized, now is the time to right-size the new ones.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Well the jacket has to be shortened/cut. The power burner being to large would/could be an issue. I suppose on the atmospheric you cut/plug off the removed burners.
If both boiler models were sold as smaller boilers with less sections that I think you're ok to proceed. If the boiler inspection gets wind of this they may require a certified hydro which costs a few $$.
We did this with a couple of reused Weil McLain 88s removed 3 sections. The smaller boiler called for the same power burner with some adjustments it has been ok.
If the old boilers are leaking, I would be dubious, ours were in good shape0 -
Ray Wohlfarth
Boiler Lessons0 -
@EBEBRATT-Ed I just found out the boilers are close to 60 years old. I told the customer to replace them and allow the boilers to retire with dignity LOL
Ray Wohlfarth
Boiler Lessons1 -
0
-
If boilers were a bit older then they'd last longer?RayWohlfarth said:@EBEBRATT-Ed I just found out the boilers are close to 60 years old. I told the customer to replace them and allow the boilers to retire with dignity LOL
Around that time manufacturers narrowed water ways.
Really old iron lasted forever.
That's what I was told long ago by that Montreal company that stocked old sections and radiators.0 -
jumper said:
@EBEBRATT-Ed I just found out the boilers are close to 60 years old. I told the customer to replace them and allow the boilers to retire with dignity LOL
If boilers were a bit older then they'd last longer? Around that time manufacturers narrowed water ways. Really old iron lasted forever. That's what I was told long ago by that Montreal company that stocked old sections and radiators.
I think @RayWohlfarth did the best thing for his customerSingle pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
You will never come out ahead messing with sections on a 60-year-old boiler I don't care when it was made or what the quality of the Iron is0
-
jumper said:
@EBEBRATT-Ed I just found out the boilers are close to 60 years old. I told the customer to replace them and allow the boilers to retire with dignity LOL
If boilers were a bit older then they'd last longer? Around that time manufacturers narrowed water ways. Really old iron lasted forever. That's what I was told long ago by that Montreal company that stocked old sections and radiators.
If long ago was 20 years you were told the story that would be back to the 40's .
I believe I recall reading they began mixing old metal into the boiler castings in the mid 60's but @Steamhead and others know more about thatOne way to get familiar something you know nothing about is to ask a really smart person a really stupid question0 -
Well, the customer decided to have another contractor switch sections from both boilers and make a single working boiler. I do hope they get some use but winder how long they will get. Thanks to all for your wisdomRay Wohlfarth
Boiler Lessons0 -
-
-
"They never made them like they used to"..."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
This. You do not need to be involved with such a situation. There are better jobs.RayWohlfarth said:@ratio I hear that
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 424 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements