"smoke" from chimney -- cracked boiler?
nickr
nickr Member Posts: 48
edited November 2021 in Strictly Steam
My single-pipe steam system works, but I noticed the other day this white stuff billowing from my chimney -- does this mean my boiler is cracked? It wasn't a very cold day.
  • STEVEusaPA
    Probably.
    SuperTech
    Steamhead Member Posts: 18,453
    Is it refilling a lot?
    Consulting
    EBEBRATT-Ed Member Posts: 20,137
    Are you burning oil or gas?
    mattmia2 Member Posts: 16,644
    flood it and see if water leaks out
    SuperTechpecmsgEdTheHeaterMan
  • nickr
    Gas fired boiler. The only time I've had to refill it is when I drain a bit out to get the sludge out.
  • ChrisJ
    ChrisJ Member Posts: 17,343
    Do you have an autofeeder?
  • nickr
    Nope. Just a valve that I open to fill it up.
    @nickr
    Sometimes steam boilers leak above the water line and send steam up the chimney and you won't see any water on the floor.
    The way to check for this is with a cold boiler add water and overfill it until the supply pipe coming out of the top of the boiler gets cold then shut the water off and let it sit for an hour or so.. Look inside and around the boiler. No water? Drain it down to normal and run it
  • nickr
    @nickr
    If I do this and don't see any water in or around the boiler, am I in the clear?
    Jamie Hall Member Posts: 27,311
    The best test is... how much water are you adding daily/weekly/monthly?
    @nickr
    Between the flood test and what @Jamie Hall posted you will know
  • nickr
    The strange thing is -- I don't have to add water. I have to take it away. Left to run unattended, the water line eventually rises above the recommended level so I've got to periodically drain some water to keep it at the recommended level. I don't have an automatic water feeder -- just a stupid hand valve that I open up when I need to add water. I keep it closed otherwise.
    Could a too-full boiler be the cause of steam coming out of the chimney?
    ethicalpaul Member Posts: 8,725
    Your stupid hand valve must be leaking by, or if you use this boiler to heat your domestic hot water, that coil could have a leak.
    A too-full boiler shouldn't affect your chimney output....but how full are we talking?
    MaxMercy
  • nickr
    The hot water heater is separate. The cheap water valve must have a leak.
    This morning, the glass water level indicator was full all the way to the top -- no air. So I've gotta assume the boiler was completely full. About a week ago I had drained some water from the boiler to set the water level to the preferred/indicated level.
    What @ethicalpaul said.
  • SlamDunk
    SlamDunk Member Posts: 1,802
    Which brings us back to the steam coming out of the chimney....The fresh water may have rotted through the boiler's crown. May be a pin hole now.
    I'd say it was at least completely full. After the glass is full, there's no telling how much higher the water went until it starts spewing out of your radiator vents.
    SlamDunk makes a great point...how long (weeks? months?) have you been draining this excess water?
  • nickr
    Just bought the house in July. Previous owner said it had to be drained every week but I thought he was talking about sludge removal.
    It was only recently that I noticed the need to drain it; but then again we haven't had the heat on for very long so I wasn't poking around down there until recently.
  • Intplm.
    Intplm. Member Posts: 3,002
    @nickr
    Sometimes you can take the top skin off of the boiler and spot the leak that way. Do this when the boiler is cooled. If you don't see an obvious leak you will have to flood the boiler to see if it's leaking.
  • nickr
    Update: we flooded the boiler yesterday and didn't spot any leak. So hopefully it's not cracked.
  • MaxMercy
    MaxMercy Member Posts: 601
    Make sure you address the water ingress. Fresh water brings oxygen which will rot the boiler.
  • nickr
    The technician thinks one of the returns is clogged (it was slower to heat up than the other return) and so there may be a slow trickle of water back into the boiler from that return, causing the illusion of water ingress from a bad valve. But this guy thought that main vents are not supposed to close even when steam hits them. And the return that heated up more slowly has a new main vent on it (the old one didn't work) whereas the return that does heat up either doesn't have a main vent or has an old and likely clogged one on it.
  • MaxMercy
    Sure, but that doesn't explain why you have to continually drain the boiler since you don't have an automatic feed and you're not adding water manually.
  • nickr
    True. This summer once the boiler's cold I'm going to mark the water line with tape and see if the level changes in 48 hours. If it does, time for a new valve.
  • ChicagoCooperator
    ChicagoCooperator Member Posts: 363
    One comment I'd like to make on the white smoke from flues - a few weeks ago we had extremely mild and humid weather, but still heating weather, and a lot of the adjacent buildings with both steam and other (I would assume all gas, I've never seem a fuel oil truck here that I can remember [Chicago]) systems were billowing/spewing white smoke - all of us couldn't have sprung leaks at the same time, so definitely do whatever tests needed to verify a leak is present.