"smoke" from chimney -- cracked boiler?
Comments
-
-
Is it refilling a lot?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Are you burning oil or gas?0
-
-
Gas fired boiler. The only time I've had to refill it is when I drain a bit out to get the sludge out.0
-
Do you have an autofeeder?nickr said:Gas fired boiler. The only time I've had to refill it is when I drain a bit out to get the sludge out.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
@nickr
Sometimes steam boilers leak above the water line and send steam up the chimney and you won't see any water on the floor.
The way to check for this is with a cold boiler add water and overfill it until the supply pipe coming out of the top of the boiler gets cold then shut the water off and let it sit for an hour or so.. Look inside and around the boiler. No water? Drain it down to normal and run it
0 -
If I do this and don't see any water in or around the boiler, am I in the clear?EBEBRATT-Ed said:@nickr
with a cold boiler add water and overfill it until the supply pipe coming out of the top of the boiler gets cold then shut the water off and let it sit for an hour or so.
0 -
-
0
-
The strange thing is -- I don't have to add water. I have to take it away. Left to run unattended, the water line eventually rises above the recommended level so I've got to periodically drain some water to keep it at the recommended level. I don't have an automatic water feeder -- just a stupid hand valve that I open up when I need to add water. I keep it closed otherwise.Jamie Hall said:The best test is... how much water are you adding daily/weekly/monthly?
Could a too-full boiler be the cause of steam coming out of the chimney?0 -
Your stupid hand valve must be leaking by, or if you use this boiler to heat your domestic hot water, that coil could have a leak.
A too-full boiler shouldn't affect your chimney output....but how full are we talking?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
The hot water heater is separate. The cheap water valve must have a leak.ethicalpaul said:Your stupid hand valve must be leaking by, or if you use this boiler to heat your domestic hot water, that coil could have a leak.
A too-full boiler shouldn't affect your chimney output....but how full are we talking?
This morning, the glass water level indicator was full all the way to the top -- no air. So I've gotta assume the boiler was completely full. About a week ago I had drained some water from the boiler to set the water level to the preferred/indicated level.0 -
What @ethicalpaul said.0
-
Which brings us back to the steam coming out of the chimney....The fresh water may have rotted through the boiler's crown. May be a pin hole now.0
-
I'd say it was at least completely full. After the glass is full, there's no telling how much higher the water went until it starts spewing out of your radiator vents.
SlamDunk makes a great point...how long (weeks? months?) have you been draining this excess water?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Just bought the house in July. Previous owner said it had to be drained every week but I thought he was talking about sludge removal.ethicalpaul said:how long (weeks? months?) have you been draining this excess water?
It was only recently that I noticed the need to drain it; but then again we haven't had the heat on for very long so I wasn't poking around down there until recently.1 -
Update: we flooded the boiler yesterday and didn't spot any leak. So hopefully it's not cracked.0
-
The technician thinks one of the returns is clogged (it was slower to heat up than the other return) and so there may be a slow trickle of water back into the boiler from that return, causing the illusion of water ingress from a bad valve. But this guy thought that main vents are not supposed to close even when steam hits them. And the return that heated up more slowly has a new main vent on it (the old one didn't work) whereas the return that does heat up either doesn't have a main vent or has an old and likely clogged one on it.MaxMercy said:
Make sure you address the water ingress. Fresh water brings oxygen which will rot the boiler.nickr said:Update: we flooded the boiler yesterday and didn't spot any leak. So hopefully it's not cracked.
0 -
Sure, but that doesn't explain why you have to continually drain the boiler since you don't have an automatic feed and you're not adding water manually.nickr said:
The technician thinks one of the returns is clogged (it was slower to heat up than the other return) and so there may be a slow trickle of water back into the boiler from that return, causing the illusion of water ingress from a bad valve.MaxMercy said:
Make sure you address the water ingress. Fresh water brings oxygen which will rot the boiler.nickr said:Update: we flooded the boiler yesterday and didn't spot any leak. So hopefully it's not cracked.
0 -
True. This summer once the boiler's cold I'm going to mark the water line with tape and see if the level changes in 48 hours. If it does, time for a new valve.MaxMercy said:
Sure, but that doesn't explain why you have to continually drain the boiler since you don't have an automatic feed and you're not adding water manually.nickr said:
The technician thinks one of the returns is clogged (it was slower to heat up than the other return) and so there may be a slow trickle of water back into the boiler from that return, causing the illusion of water ingress from a bad valve.MaxMercy said:
Make sure you address the water ingress. Fresh water brings oxygen which will rot the boiler.nickr said:Update: we flooded the boiler yesterday and didn't spot any leak. So hopefully it's not cracked.
0 -
One comment I'd like to make on the white smoke from flues - a few weeks ago we had extremely mild and humid weather, but still heating weather, and a lot of the adjacent buildings with both steam and other (I would assume all gas, I've never seem a fuel oil truck here that I can remember [Chicago]) systems were billowing/spewing white smoke - all of us couldn't have sprung leaks at the same time, so definitely do whatever tests needed to verify a leak is present.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements