"smoke" from chimney -- cracked boiler?

nickr
nickr Member Posts: 7
edited November 8 in Strictly Steam
My single-pipe steam system works, but I noticed the other day this white stuff billowing from my chimney -- does this mean my boiler is cracked? It wasn't a very cold day.


Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 5,304
    Probably.
    steve
    SuperTech
  • Steamhead
    Steamhead Member Posts: 14,837
    Is it refilling a lot?
    All Steamed Up, Inc.
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 10,268
    Are you burning oil or gas?
  • mattmia2
    mattmia2 Member Posts: 3,957
    flood it and see if water leaks out
    SuperTechpecmsg
  • nickr
    nickr Member Posts: 7
    Gas fired boiler. The only time I've had to refill it is when I drain a bit out to get the sludge out.
  • ChrisJ
    ChrisJ Member Posts: 11,970
    nickr said:

    Gas fired boiler. The only time I've had to refill it is when I drain a bit out to get the sludge out.

    Do you have an autofeeder?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • nickr
    nickr Member Posts: 7
    ChrisJ said:

    nickr said:

    Gas fired boiler. The only time I've had to refill it is when I drain a bit out to get the sludge out.

    Do you have an autofeeder?
    Nope. Just a valve that I open to fill it up.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 10,268
    @nickr

    Sometimes steam boilers leak above the water line and send steam up the chimney and you won't see any water on the floor.

    The way to check for this is with a cold boiler add water and overfill it until the supply pipe coming out of the top of the boiler gets cold then shut the water off and let it sit for an hour or so.. Look inside and around the boiler. No water? Drain it down to normal and run it

  • nickr
    nickr Member Posts: 7

    @nickr

    with a cold boiler add water and overfill it until the supply pipe coming out of the top of the boiler gets cold then shut the water off and let it sit for an hour or so.

    If I do this and don't see any water in or around the boiler, am I in the clear?
  • Jamie Hall
    Jamie Hall Member Posts: 17,049
    The best test is... how much water are you adding daily/weekly/monthly?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 10,268
    @nickr

    Between the flood test and what @Jamie Hall posted you will know
  • nickr
    nickr Member Posts: 7

    The best test is... how much water are you adding daily/weekly/monthly?

    The strange thing is -- I don't have to add water. I have to take it away. Left to run unattended, the water line eventually rises above the recommended level so I've got to periodically drain some water to keep it at the recommended level. I don't have an automatic water feeder -- just a stupid hand valve that I open up when I need to add water. I keep it closed otherwise.

    Could a too-full boiler be the cause of steam coming out of the chimney?
  • ethicalpaul
    ethicalpaul Member Posts: 3,123
    Your stupid hand valve must be leaking by, or if you use this boiler to heat your domestic hot water, that coil could have a leak.

    A too-full boiler shouldn't affect your chimney output....but how full are we talking?
    1 pipe Peerless 63-03L in Cedar Grove, NJ, coal > oil > NG
  • nickr
    nickr Member Posts: 7

    Your stupid hand valve must be leaking by, or if you use this boiler to heat your domestic hot water, that coil could have a leak.

    A too-full boiler shouldn't affect your chimney output....but how full are we talking?

    The hot water heater is separate. The cheap water valve must have a leak.

    This morning, the glass water level indicator was full all the way to the top -- no air. So I've gotta assume the boiler was completely full. About a week ago I had drained some water from the boiler to set the water level to the preferred/indicated level.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 10,268
    What @ethicalpaul said.
  • SlamDunk
    SlamDunk Member Posts: 1,105
    Which brings us back to the steam coming out of the chimney....The fresh water may have rotted through the boiler's crown. May be a pin hole now.
  • ethicalpaul
    ethicalpaul Member Posts: 3,123
    I'd say it was at least completely full. After the glass is full, there's no telling how much higher the water went until it starts spewing out of your radiator vents.

    SlamDunk makes a great point...how long (weeks? months?) have you been draining this excess water?
    1 pipe Peerless 63-03L in Cedar Grove, NJ, coal > oil > NG
  • nickr
    nickr Member Posts: 7

    how long (weeks? months?) have you been draining this excess water?

    Just bought the house in July. Previous owner said it had to be drained every week but I thought he was talking about sludge removal.

    It was only recently that I noticed the need to drain it; but then again we haven't had the heat on for very long so I wasn't poking around down there until recently.
    ethicalpaul
  • Intplm.
    Intplm. Member Posts: 1,336
    @nickr
    Sometimes you can take the top skin off of the boiler and spot the leak that way. Do this when the boiler is cooled. If you don't see an obvious leak you will have to flood the boiler to see if it's leaking.