install a LWCO in a Old gas furnace
Jsencion
Member Posts: 6
in Gas Heating
Hi everyone! I'm electrician and I'm new with boiler wiring, I have a old gas furnace in a residential place, it's have few components that I made my research on internet about them, I can not figure out the a way to add a New LWCO to the Old furnace that doesn't have one, this is the wiring diagram and the brand of the LWCO to be install, is somebody can give a hand I appreciate it please
Consulting0 -
@Steamhead is a Weil- mclain yes, steam. Here the picture you can see where is Mounted
@Steamhead im sorry, hot water0
Why 2 LWCO?0
@Danny Scully is just one, the other device inside is a high limit control
@Jsencion
You need to power the LWCO with 24 volt power constant hot.. Then wire the LWCO switch in series with your high limit control shown on the diagram.
If there is a jumper between the power contact and the switch contact in the LWCO take it out. Look at the instructions.
Bump the relief valve on top of the LWCO to get any air out.
I believe that model M&M is 115v powered. Switching can be either line or low volt0
That round lwco is too low. It should be above the boiler, and should shut the boiler down before there is no water in the boiler.