install a LWCO in a Old gas furnace

Jsencion
Jsencion Member Posts: 6
Hi everyone! I'm electrician and I'm new with boiler wiring, I have a old gas furnace in a residential place, it's have few components that I made my research on internet about them, I can not figure out the a way to add a New LWCO to the Old furnace that doesn't have one, this is the wiring diagram and the brand of the LWCO to be install, is somebody can give a hand I appreciate it please

Comments

  • pecmsg
    pecmsg Member Posts: 4,776
    An Electrician cant figure this out...................

    Break the primary circuit!
    Jsencion
  • Jamie Hall
    Jamie Hall Member Posts: 23,177
    Yeah... except that control looks like it's for 24 volts. Therefore...

    Break the gas valve circuit!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    JsencionHVACNUTethicalpaul
  • Steamhead
    Steamhead Member Posts: 16,796
    @Jsencion , what model Weil-McLain?

    Steam or hot-water?

    Where are you going to mount the control?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Danny Scully
    Danny Scully Member Posts: 1,416
    What good is a LWCO on a furnace…😉
    GroundUpmattmia2PC7060
  • Jsencion
    Jsencion Member Posts: 6
    @Steamhead is a Weil- mclain yes, steam. Here the picture you can see where is Mounted 
  • Jsencion
    Jsencion Member Posts: 6
    @Steamhead im sorry, hot water
  • Danny Scully
    Danny Scully Member Posts: 1,416
    Why 2 LWCO? 
  • Jsencion
    Jsencion Member Posts: 6
    @Danny Scully is just one, the other device inside is a high limit control
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    @Jsencion

    You need to power the LWCO with 24 volt power constant hot.. Then wire the LWCO switch in series with your high limit control shown on the diagram.

    If there is a jumper between the power contact and the switch contact in the LWCO take it out. Look at the instructions.

    Bump the relief valve on top of the LWCO to get any air out.

    Jsencion
  • Danny Scully
    Danny Scully Member Posts: 1,416
    I wasn’t talking about the aquastat, I was talking about the 2nd LWCO.


    HVACNUT
  • HVACNUT
    HVACNUT Member Posts: 5,804
    I believe that model M&M is 115v powered. Switching can be either line or low volt 
  • realliveplumber
    realliveplumber Member Posts: 354
    That round lwco is too low. It should be above the boiler, and should shut the boiler down before there is no water in the boiler.