install a LWCO in a Old gas furnace
Jsencion
Jsencion Member Posts: 6
Hi everyone! I'm electrician and I'm new with boiler wiring, I have a old gas furnace in a residential place, it's have few components that I made my research on internet about them, I can not figure out the a way to add a New LWCO to the Old furnace that doesn't have one, this is the wiring diagram and the brand of the LWCO to be install, is somebody can give a hand I appreciate it please
    pecmsg Member Posts: 7,282
    An Electrician cant figure this out...................
    Break the primary circuit!
    Jsencion
    Yeah... except that control looks like it's for 24 volts. Therefore...
    Break the gas valve circuit!
    JsencionHVACNUTethicalpaul
    Steamhead Member Posts: 18,710
    @Jsencion , what model Weil-McLain?
    Steam or hot-water?
    Where are you going to mount the control?
    Consulting
  • Danny Scully
    Danny Scully Member Posts: 1,465
    What good is a LWCO on a furnace…😉
    GroundUpmattmia2PC7060
  • Jsencion
    @Steamhead is a Weil- mclain yes, steam. Here the picture you can see where is Mounted
  • Jsencion
    @Steamhead im sorry, hot water
  • Danny Scully
    Why 2 LWCO?
  • Jsencion
    @Danny Scully is just one, the other device inside is a high limit control
    EBEBRATT-Ed Member Posts: 20,482
    @Jsencion
    You need to power the LWCO with 24 volt power constant hot.. Then wire the LWCO switch in series with your high limit control shown on the diagram.
    If there is a jumper between the power contact and the switch contact in the LWCO take it out. Look at the instructions.
    Bump the relief valve on top of the LWCO to get any air out.
    Jsencion
  • Danny Scully
    I wasn’t talking about the aquastat, I was talking about the 2nd LWCO.
    HVACNUT
    HVACNUT Member Posts: 7,526
    I believe that model M&M is 115v powered. Switching can be either line or low volt
  • realliveplumber
    realliveplumber Member Posts: 354
    That round lwco is too low. It should be above the boiler, and should shut the boiler down before there is no water in the boiler.
