Problem with excessive noise in recently installed Lochinvar Noble boiler
Many thanks for advice or information.
It's not normal. Theirs something amiss either with the boiler itself or the installation, and that's something for you to work on with the installer. How to get them to do that? That depends a great deal on you r relationship with them.Br. Jamie, osb
Thank you so much. I’m going to measure the frequencies and decibel levels so I have proof it has a problem. As a woman, it is hard to be taken seriously.
Jamie is correct, If the installer is having trouble figuring it out, have him call Lochinvar Technical support.
That boiler is for the most part pretty quiet, on 100% fire may have the sound of air rush in at the outside vent but that's all.
D0 -
It looks like the gas comes in to the bottom from a black rigid pipe that is a little bigger in diameter than the hot water pipes.
Can you record the noise with your phone and post it? Video usually works well."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Instead of recording the sound I had a friend come over and measure the boiler’s sound levels. The decibels are within normal range but it is emitting frequencies in the 16,000 to 20,000 hertz range. This explains why the dog won’t eat or drink when it is on and even though this is beyond the range of normal hearing, I find it irritating. Plus, such high frequencies can damage your hearing. For comparison purposes we measured the sound level of a similar type of boiler a neighbor has which is brand new but not the same brand. Its frequency levels are extremely low and don’t even get close to this. Has anyone run into this problem?0
@mswhite
You need to try and isolate the noise. Stay in the basement and observe it. Turn your thermostat up high. Go to the basement and shut the boiler off when it stops then re start it observe when it makes noise. The boiler will start a just purge for a period of time with no flame Is it making noise then? Then the burner will ignite. Is it making the noise only when the gas flame is burning??. Does it make the noise when the flame goes out and it post purges? etc etc1 -
Thank you. I did this. It makes the noise constantly after I turn it on. It seems to cycle every second or 2 going from a low level frequencies to 16000 to 17000 hertz and sometime 20,000 hertz. When gas goes off it just makes swish and no more noise.0
@mswhite
Sounds like a combustion issue. Is any of the gas piping connected to this boiler flex type piping. I asked this before0 -
was boiler dialed in with a combustion analyzer0
It needs to be set up with a combustion analyzer. Set high, and then low fire readings to the factory specifications in the installation manual. When this has been done and the issue were to continue, then contact the factory for further adjustments.
D0 -
I don't know anyone that troubleshoots sound by measuring the frequency. If you can post an audio, someone here has probably heard the same noise and help diagnose.
Incorrect combustion and harmonics through the gas lines are common causes of noise in these kinds of boilers."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
The problem with the vibration is the diverter motor small electric motor that switches boiler from Dhw to space heat0
Hi,
I have the same problem, unit 6 months old. Replaced Grundos internal pump, did not solve the issue. Used mechanics stethoscope to determine origin of noise. Seems to be loudest from blower assembly on top. Besides the high pitched ringing noise it also make a wooshing sound when it fires. Contractor is very helpful but this is not a no-heat issue so I don't want to keep bugging him. I don't know if this is normal for this type of boiler but it is very annoying since it is right next to my man-cave :>). It has saved me over 25% on my heating bill this winter. Was this problem ever resolved?
Thanks a lot!
A whooshing sound could be the ignition, has the gas or LP pressure been checked at the gas valve. Got a combustion analysis report. That noise should be tunable, made to disappear
Did you contact the Lochinvar rep about the diverter noise?Bob "hot rod" Rohr
In my Mod Con experience, this is the gas valve/air intake components out of whack or just bad. I had a Buderus GB-142 do this about 6 months in. Did all the adjustments to spec via the Tech Support, but they would up just shipping us a new one. Good luck mad Dog