header widths
What is the boiler? What does the installation manual say?
Not quite sure I follow you -- but a first, as @ethicalpaul says follow the manual as a minimum. In any case, do not either bush down or reduce coming up out of the boiler tappings -- whatever size they are, keep that all the way up to the header. Then the header itself -- the horizontal (nearly!) pipe -- should be one size larger (more doesn't hurt, but not same size or smaller) all the way to the equalizer. Turn down to the equalizer either with a reducing elbow or reduce on the way down, as you like.Br. Jamie, osb
Well Jamie, my teeny tiny boiler has 3" tappings because it also comes in much larger versions with the same castings so I wouldn't say to never bush down the tappings.
Double header=drop header?? Maybe post some diagrams. Different people use different terms to refer to different/same things. We don't want anything to be lost in translation.0
Indeed, and I shouldn't talk! Cedric -- a five section Weil-McClain -- has two tappings as well -- and when we put it together, we only used one -- and it works superbly well. Of course, a big drop header... and perhaps more of course, the drop header, in turn, feeds into the left over steam drum of a really big H.B.Smith through four more risers, and only then gets out to the rest of the system. A water droplet doesn't have a chance...ethicalpaul said:Well Jamie, my teeny tiny boiler has 3" tappings because it also comes in much larger versions with the same castings so I wouldn't say to never bush down the tappings.
do you have the made and model of the boiler each manufacture is differentslapp said:I am installing a double header onto a system that only had a single header. The riser from the boiler is 2 in, should I pipe both of them into a 3 inch before it head up to the main? Or keep it 2 inches all the way up?
Hi, thanks, and sorry for not providing some good information in my first go. I have a Burnham Independence IN5 and I am replacing it with an IN6. The IN5 had a massive hole start to rust out. You can see in the pictures that the IN5 is piped with only 1 2 inch header. I was told that I should be using both (double header). So when I replace it with the IN6 I am going to do both. You can see that there is some old plumbing from the previous boiler. The blue Line in the pictures. That stuff will NOT budge, I tried heat, 36 inch wrench, smooth hand...nothing, and I don't want to crack it or I will be in for a larger job than I need right now. I never would reduce the size of the headers...never, I get that. But if I have Two 2 inch headers coming up from the boiler, should I get them into a 3 inch, or build everything 2 inch all the way to the 3 inch and bushing it there? I will also take the time to insulate etc.
Exactly this question.pecmsg said:Why are you going larger?
Also that piping is a nightmare, I hope you’re redoing it per the manual.
Also if my boiler rusted like that one I’d be trying a different brandNJ Steam Homeowner.
As others have asked do you need an IN6? It’s 175,000 Btu input and 450 sqft steam, it’s a big boiler. Have you done an EDR on the house radiators. This will determine the size boiler needed?DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......2 -
Yeah the house radiators call for 458 sqft of steam, I routinely have 1 to 2 rooms turned off because they are not in use. Currently I get a lot of half warm radiators and on cold days it runs 24 hours. From the looks of the piping the previous owner added on two rooms to the house and didn't add anything to the boiler. Thanks for the help and opinions here. I think I have a way forward.1
Sounds good. Don't worry about half warm radiators, focus only on the sqft of radiation vs boiler.
Looking back at your posts, I think you are calling steam supply risers "headers". In your diagram above, the header is the horizontal pipe that the steam supplies tie into.
So you are going from a header with a single steam supply to a new boiler with both steam supplies utilized.NJ Steam Homeowner.
With the current boiler, did the entire house stay comfortable?
Half warm radiators is moot and running for 24 hours could be good, IF it keeps up and keeps the entire house comfortable.
- 50 Industry Classes