Steamer Installation
EzzyT
EzzyT Member Posts: 1,377
This was an oil to gas conversion and the oil boiler looked liked it hadn’t been serviced in years from just looking inside the combustion chamber.
This is Richardson System that was botched over the years, we tried our best to bring it back to it glory.
Some of the radiators still has the original Richardson return elbows. The sunrads that’s where installed along with the copper and steel finned baseboard was most likely done 30+ years ago and they had no return elbows nor any traps.
So we ripped out the baseboard installed cast iron radiator that we had in stock that needed to be gone to make room at the shop and installed new valves with traps on the sunrads and new radiators that we installed.
We also had replaced a decent amount of copper piping on the steam mains.
Need to go back to do skimming and wanding.
The Shur Stop Fire extinguishers will be added to our collection of unique Things we come across.
E-Travis Mechanical LLC
Etravismechanical@gmail.com
201-887-8856
Intplm.kcoppIronmanDZoroethicalpaul
  • pbennett45
    pbennett45 Member Posts: 15
    Thanks for an outstanding job Ezzy.
    Ezzy did some beautiful work and was a wealth of knowledge. After doing the boiler on a single pipe system in our first house with a "not a steam guy" plumber ten years ago and THEN finding this site and Dan's books and learning all about single pipe, Ezzy did a great job bringing me up to speed quickly on the two pipe system in the new house!
    Great work and very easy and helpful to work with. The many recommendations on this board don't lie!
    DZoro
  • Intplm.
    Intplm. Member Posts: 2,813
    Always nice to see beautiful work.
    Nice Job !
  • Ironman
    Ironman Member Posts: 7,849
    Excellent!
    Bob Boan
    pecmsg Member Posts: 6,753
    Deadman:
    "See there's still a few of us down there!"
    2 Thumbs Up EzzyT
    Intplm.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    What sort of filter is on the makeup feed line?—NBC
  • EzzyT
    @pbennett45 Thank you for allowing us to do the work in your home much appreciated.
    @Intplm. @Ironman @pecmsg thank you guys.
    @nicholas bonham-carter the filter itself isn’t installed yet just the housing but it is a Caleffi in-line demineralize filter unit.
    201-887-8856
  • AMservices
    AMservices Member Posts: 611
    Raising the bar on the auto feed piping.
    Nice work! As always
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 698
    Great work, as always. You’re great at what you do and an inspiration to the rest of us.
    Never stop learning.
    Ironman
    Steamhead Member Posts: 18,184
    Nice Job !
    Ironman said:
    Excellent!
    pecmsg said:
    Deadman:
    2 Thumbs Up EzzyT
    These.
    Consulting
    Jamie Hall Member Posts: 26,791
    I've had the privilege of watching @EzzyT at work. Not only is the finished job beautiful -- in all senses -- but the working itself is a joy to watch.
  • EzzyT
    Thank you gentlemen for the kind words.
    201-887-8856
  • clammy
    clammy Member Posts: 3,242
    As always Ezzy awesome work attention to detail on the mark ,it doesn’t get any better buddy got to say ETDFW meaning ezzy Travis does fine work don’t throw that out much but u had It coming . As always keep up the excellent work if only they all where so pretty Peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
  • clammy
    Side note don’t see many of those sur stops much I think most where thrown out or broken now a days it’s like 1 outta 100 and I ll see one usually in a barely lite basement cause it’s never seen light lol peace and good luck clammy
    NJ Master HVAC Lic.
    Mahwah, NJ