Best spot for a steam radiator in a small room

branimal
branimal Member Posts: 245
I'm renovating a building and I need to choose a spot for a radiator in small room. The most important thing is the radiator doesn't affect furniture place / usability of the room.

It has to go along the wall with the windows.

Options are:
1. under the window b/c people typically don't put furniture in front of the window.
2. In the weird angled corner
3. In the 90 degree corner.

Any thoughts?


Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 26,072
    Mercy. That's not a room, that's a closet. From the standpoint of heating the room, it really won't matter -- radiators circulate warm air (naturally) pretty well. From the standpoint of using the room, though... although option 1 is conventional, I think it's problematic, as that is where someone will have to walk to get into the corner. On the whole, I think I'd go for option 2, and put some sort of clever set of shelves over it, starting about a foot above it....
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    branimal
  • Danny Scully
    Danny Scully Member Posts: 1,462
    That room isn’t even 100 sqft, are you sure it legal?
    branimal
  • branimal
    branimal Member Posts: 245
    yeah its legal. 7 feet in a building with 3 or more bedrooms is legal. The other bedrooms are standard size.
  • KC_Jones
    KC_Jones Member Posts: 5,885
    The only place left for someone to put a typical dresser is in front of the window so option 2 is really the only option, by the numbers.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    branimal
  • Danny Scully
    Danny Scully Member Posts: 1,462
    What’s the heat loss of the room? Could you go with option 2 and use a riser right in that corner as your source of radiation?
    branimal
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Steam or hot water? If steam a small wall mount single section might work well. If hot water, they make some really small panel radiators. I agree, option 2 would be best. Maybe a shorter shingle tube or column radiator like those used for bathrooms.
    branimal
  • branimal
    branimal Member Posts: 245
    Thanks guys.

    Danny - good idea on the riser. The pipe coming up is 1". I'll google heat loss calc and get back.

    Mike - it's single pipe steam system.
  • pecmsg
    pecmsg Member Posts: 6,168
    How do you plan on controlling the heat in that closet?
    Only 2 outside walls, well insulated there wont be much heat loss, any calculations on the total BTU's required?
  • KC_Jones
    KC_Jones Member Posts: 5,885
    You need to do the heat loss on all the rooms. I’ve read some of your other posts and this is like a new system with all the work being done. Room by room heat loss, size the radiation accordingly.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    ethicalpaul
  • ChrisJ
    ChrisJ Member Posts: 16,759
    Since we're all critiquing the room, I'd have the door swing against the wall, not into the room.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    KC_JonesethicalpaulSteve Minnich
  • Leon82
    Leon82 Member Posts: 684
    There was a post here where the guy made his own radiator in the bathroom, very small.

    Maybe the microtube system
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited May 2019
    Any chance for a small piece of cast iron baseboard, properly sized and pitched?

    There was an error rendering this rich post.

    Steve Minnich
  • Alan Welch
    Alan Welch Member Posts: 270
    4. mount on ceiling 5. recess into wall 6. install in floor box between joists.

Welcome