Solving poorly pitched pipe

Options
Fizz
Fizz Member Posts: 579
Last extension of supply main in single pipe(parellel system) is pitched wrongly. Wondering if a 1" copper(no,no) tubing draining into parallel return would help? See pix. Pipe in question is to left of wire, return is drop-down to right which runs parallel to supply, then drops at boiler. Radiator attached at end of supply main has moderate hammer toward end of cycle, and a rushing or flowing water sound afterwards.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 27,188
    No way to rehang the whole thing so it pitches properly? Any handy wet returns to drip into? It's kind of hard to tell from the picture -- but you may have trouble getting enough pitch on your new pipe to help much. And that new pipe has to be threaded iron -- as you note, no copper -- and no plastic, either. It will have steam in it.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Could you raise the last radiator, and therefore correct the slope?—NBC
  • Fizz
    Fizz Member Posts: 579
    No way to rehang pipe, nearest wet return is at boiler which isn't practical. Radiator is at highest point.
  • Chris_L
    Chris_L Member Posts: 354
    You may not need to rehang the whole pipe.

    What is the size of the pipe that improperly pitched? And have you identified the low point in it where condensate is collecting?

    Have you tried putting a hanger in that position and lifting the pipe up? You'd be surprised what a little push on a 1" pipe can do.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,044
    @Fizz
    so your saying that the pipe to the left of the small wire it the hammer pipe? And the steam supply is coming from the right? Just trying to figure this out.

    If I am looking at this right cut a tee into the pipe where it hammers with the branch of tee looking straight down. 3/4" would be the minimum size 1" would be better. Drop out of this tee do to a level below the boiler water line. 90 over at that level until your underneath the steam supply pipe. 90 up and put a tee into the steam supply looking down and tie into that. Check the pitch on that steam supply and make sure that section is pitched back toward the main. This is a loop seal.

    But that is a lot of work.

    My first choice would be to rework/rehang that steam supply to make it work. Looks to me like it could be done with a little creativity
  • JUGHNE
    JUGHNE Member Posts: 11,542
    IIWM, I would remove the insulation and raise the pipe up.
    If needed a little floor joist notching might be in order.
    But for more than an inch of notching, I would make a "sister sandwich" on the floor joist. That is putting a 2' length of 1/2" plywood the height of the joist on each side of the joist, centered on the pipe. Glue and screw the hell out of it. Then you can cut more out of the bottom of the joist ….maybe 2-3", depending upon the height of the joists.
    This is a guideline only....not scientific....but have done it and no problems. You are close to the end of the joists so it is not as if you are in the middle of the span.
  • Fizz
    Fizz Member Posts: 579
    Pipe in question is an 11/2", and is a new pipe put-in last May. Tech said that's best he could do with-out major pipe work. The pipe replaced had a greater downward pitch and a leak, thus replaced. The radiator attached is 2nd floor and already raised several inches, there's no more space to play with.
    PIpe is pard of a 20' run before it 90 degrees 11' to boiler where it drops below water line.
    Most recent service guy told me he has pipe-guy that's creative, so I will contact him to get some feedback.
  • Fizz
    Fizz Member Posts: 579
    Latest on piping: Pipe guy came yest, was very good and said best solution is to put a 11/4" tee, drop it down below water level and make it a wet return to boiler. That's what we agreed to. He considered a loop seal, and some other ideas, but he felt wet return is best. He wasn't pushy , very knowledgeble and reasonable. In the interim of the past month, also noticed a poorly pitced run of about 6' which he will correct again with some creative piping.
  • BobC
    BobC Member Posts: 5,554
    If it's ok with him, post his name so we can make use of his talent - it's becoming a rarity.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Fizz
    Fizz Member Posts: 579
    Will check.
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Actually a loop seal would probably work too and allow the pipe to remain up high except the loop seal. If you never run over 2psi, a 5’ loop will work at that point in the header. I just replaced a loop seal today on a 2 pipe Moline system with a lower basement ceiling without enough fall for gravity returns. So the “dry” return was wet at the ceiling most of the way until it dripped to the boiler. Kept the pipes off the floor.
  • Fizz
    Fizz Member Posts: 579
    Piping done over week-end. Dropped 1" pipe from T installed at end of trouble pipe to floor and ran to boiler, tapping-into drip from return. Also re-piped poorly pitched run-out on short supply.
    Will test tonite for any issues.
  • Fizz
    Fizz Member Posts: 579
    Since above piping fix notice when t-stat calls for heat, boiler pressure runs between 1-2oz, and heat shuts-off by satisfying t-stat, prior to fix, the last few minutes pressure would rise to 15-20oz and shut-off on pressure at times.
  • Fizz
    Fizz Member Posts: 579

    Re-visit to dropped return. What I've noticed is steam runs down dropped line from tee. Is this normal. All else is good. What has been a constant is with single pipe heat, the main must fill first before rads…this has never been the case. The main vents were at end of mains when we moved here, there is no room for putting vent 10-12" before end, so I added piping extending out and up. Current vents are MOM's. I tried BigMouth and Gorton#2 to no avail. The return of problem line rarely gets steam to vent, other line does. Is this concerning?

  • dabrakeman
    dabrakeman Member Posts: 979

    Couple more pictures from further back would be helpful.

  • Fizz
    Fizz Member Posts: 579

    hope these help

    image.png
  • Fizz
    Fizz Member Posts: 579
  • Fizz
    Fizz Member Posts: 579
  • ethicalpaul
    ethicalpaul Member Posts: 8,603

    This wet return has been redacted for privacy reasons

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Intplm.4GenPlumberold_diy_guy
  • 4GenPlumber
    4GenPlumber Member Posts: 107

    I'm sorry…what are we looking at, and what is the actual problem?

  • ChrisJ
    ChrisJ Member Posts: 17,266

    I'm almost positive my 2005 Samsung A920 took better pictures than those.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ethicalpaul
    ethicalpaul Member Posts: 8,603
    edited February 4

    Hi @Fizz we are just teasing a bit. It can sometimes be difficult for us to get a good handle on what is going on from a distance.

    It sounds like you have a good understanding that there can be no areas in the system where water gets trapped, and it sounds like you have identified an area where water is getting trapped.

    Running a "drip" down from the trapped area via a copper pipe all the way down to the "wet return" would be a potential fix. Are you looking to do this work yourself, or are you looking for a contractor to do it for you?

    OK I carefully read everything again noting the dates of the posts…I can now see that you had someone add a "drip" for you and you are concerned that steam seems to travel down the drip. It shouldn't if it's going all the way down to the water level. Is it?

    And it seems like you have some venting questions, but I can't quite figure out what you're asking. Do you know how to determine if a vent is operational?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • pecmsg
    pecmsg Member Posts: 7,006

    We need more pictures and clearer pictures from further away and several angles.

    Have tou actually put a level on the pipes?

  • Fizz
    Fizz Member Posts: 579

    Minored in photograp

    image.png

    hy in college…

  • Fizz
    Fizz Member Posts: 579
  • pecmsg
    pecmsg Member Posts: 7,006

    how’s the pitch on the upper pipe?

  • Fizz
    Fizz Member Posts: 579

    The drip does run back to boiler below water line. As for the vent issue, it may not be a vent issue, possibly sludge not allowing steam to get to main line vent first prior to filling attached radiation.

  • Fizz
    Fizz Member Posts: 579

    Upper pipe pitched back up to end of insulation. Prior to drip, water would pool and result in swooshing and hammer. No longer a problem in that respect. just curious as to steam filtering down drip.

  • ethicalpaul
    ethicalpaul Member Posts: 8,603
    edited February 5

    Steam shouldn't be able to travel through a trapped air section of pipe like in the picture above. The steam could heat the pipe via conduction and the steam could eventually heat some of the air in the pipe…

    What makes you think the steam is traveling down the pipe? There is condensate running down that pipe that could be quite warm.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Fizz
    Fizz Member Posts: 579

    The only reason I have is the temperature on touch is equal to supply pipe. You're probably right, as the drips from main do same.

    Thanks