EDR boiler size round up or round down
GW
Member Posts: 4,989
I hate to ask a question for the bazillionth time, I have a job where i'm right between a 3 and a 4, I think some of you all go to 20% when the pipes are insulated?
Thanks for the comments
The pickup factor can be excessive sometimes @GW. When piping is insulated I feel comfortable rounding down. If it isn’t insulated, you can always measure the pipe length/diameter etc.0
Is this for a steam or hot-water system?All Steamed Up, Inc.
Consulting0 -
Well it’s in strictly steam @Steamhead, but i guess we shouldn’t assume.0
Lol steamer, pick up is .33 in the manufacture sizing charts. But if we’re talking 15 or 20 then that means smaller. Thanks0
In addition to the above, if it is low mass convectors, then definitely round down. With convectors, it seems if the boiler is sized using conventional methods it tends to bounce off the pressure control during standard heat calls, creating a lot of short cycling. The newer low mass radiators can tend to do that more too, but not nearly like convectors.To learn more about this professional, click here to visit their ad in Find A Contractor.0
Thanks it’s good old USA cast iron rads.0
If you round down and still have some pickup I would say you are ok.0
You know what they say "assume" means..............Danny Scully said:Well it’s in strictly steam @Steamhead, but i guess we shouldn’t assume.
What model series of boiler do you plan to use? It may be possible to use a 4 section and down-fire it, which might result in better efficiency.All Steamed Up, Inc.
Consulting0 -
Merry Christmas to all heat people
I’m at 450 sq ft
One local vendor doesn’t carry lots of oil steam. I normally go with peerless . One other vendor does have the Smith, so I’ll probably go with the 4 section and be a bit oversized0 -
If its oil, you can't beat the MegaSteam.Bob Boan
Both the Peerless and Smith small steamers seem pretty good0
Peerless EC-03 puts you right there at 446 sq ft.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......-1 -
good call yet all the rads are out in the openSuperJ said:If the rads are painted a metallic color or enclosed with some sort of limiting cover, would be safe to downsize accordingly?
hummm I missed that lemme see if the vendor can grab one from one of their branch stores, thanksDave0176 said:Peerless EC-03 puts you right there at 446 sq ft.
TRVs can work. But pricey.
Some baffles between sections or attached to the bottom of the radiator would reduce capacity.
Some black silicone coated canvas cut to shape might work. Can glue with RTV.0 -
- 110 Chimneys & Flues
- 978 Plumbing
- 387 Solar
- 17 Recall Announcements
