Water, Water, Everywhere, Not a drop of heat......
Gas escaping from old lines, as well as leakage from fracking well heads, is doing more harm to the environment than oil and coal probably combined.
I wonder why the gas company took off the meter, had no gas flow and assumed it was water? Is this normal?There was an error rendering this rich post.
This is the first time I've had any issue with incoming gas supply. They took the meter off to use that incoming pipe to blow back to the main and that was the most convenient access. They assumed it was water because of the 3" of rain we had the day before and they had a similar situation on the other side of town where they had to pump 600 gallons of water out of the main. Since we have never had this situation in this area and, at that point I was the only service call they had, they assumed it was just the feed into my house.STEVEusaPA said:Gas escaping from old lines, as well as leakage from fracking well heads, is doing more harm to the environment than oil and coal probably combined.
I wonder why the gas company took off the meter, had no gas flow and assumed it was water? Is this normal?1 -
@Fred I guess the water just lays in low areas of piping and collects? Sounds like your area is still low pressure.
Our mains run at 50 PSI which may mean they're lined, I'm not sure. I've heard rumor that they boost the pressure after lining the mains to maintain volume.
@ChrisJ , yes, we are on low pressure and they told me we should be getting liners this summer and that the pressure would be upgraded to "Medium" which they said was 40 to 50PSI. I'm not sure if water is laying in low spots or if the main is virtually filled with water. They said they pumped several hundred gallons which sounds like too much for just pooling in low spots but I'm not sure???0
You have to admit, though, that an oil spill is so much messier. You have the smell, and the contaminated ground or concrete, and all that hassle... At least after a gas spill you don't have to worry so much about cleaning things up... Your worries are all over!
If you have leaky pipes in the neighbourhood, get some good gas detectors (get them anyway) and keep your nose working -- and don't forget: if you smell gas, don't turn anything on or off -- get the h___ out of Dodge and call the gas company.Br. Jamie, osb
I would think you would have to have a huge hole in pipe and very low gas pressure to get that kind of ingress.
If you hadn't mentioned the rain, I would have thought they had a very disgruntled customer with a water hose."If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
Some will ALWAYS push for oil Jamie, you know that.Jamie Hall said:You have to admit, though, that an oil spill is so much messier. You have the smell, and the contaminated ground or concrete, and all that hassle... At least after a gas spill you don't have to worry so much about cleaning things up... Your worries are all over!
What gas detectors do you recommend? I tried to find some for a friend and all that I found had horrible reviews, claiming them to be highly unreliable.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Ridgid makes -- or used to make -- a pretty decent one. It's made in China now, though...Br. Jamie, osb
Those old low-pressure gas mains are usually cast-iron. The joints are lead and oakum, just like old-school soil pipe except they use two layers of each and the hubs are deeper.
Most of these old gas systems originally delivered manufactured gas, which had enough moisture in it to keep the oakum wet and expanded. Not so with natural gas, that's why they leak like they do.
I bet @Tim McElwain could tell some stories about this.............All Steamed Up, Inc.
Consulting2 -
Well guess who is paying for all the leaking gas? You bet we are. They certainly are not going to absorb it. And they line their pockets with money instead of lining their pipes like they should be doing.
They need to really step up and get going on their infrastructure rebuilding. 1880s cast iron pipe and wooden pipe in some areas. They need to get with the program.
a few explosions will get things moving. That's what their waiting for.
I just got a letter from the gas co today warning plumbers about clearing clogged sewer lines.
Seems someone cleared a sewer line which was blocked because the gas utility had "horizontal bored" a gas line through the sewer line so the gas line got cut letting gas into the sewer line.
Now the gas company is selling "insurance" against such a catastrophe. What a racket.
maybe oil should make a comeback1 -
@the_donut , hopefully there isn't mud or debris in the line into my house. There was no water at the gas meter when they disconnected it and when they blew it out, they blew back into the main and they then pumped the main out rather than blew it out, so I feel okay with that. I can't speak for all the other houses as some of them are actually at lower levels than mine. I would guess there is some mud/debris laying in the main but I assume when they come to line those pipes they will somehow clean them out as the liner goes in??? We'll see what life holds when that exercise begins.
@EBEBRATT-Ed I agree with you. The kinds of profits these utilities post, year over year, you'd think responsible management would put far more back into the infrastructure than they have, in the past.0 -
What city are you in?0
That's a strange comment, isn't it?EBEBRATT-Ed said:Well guess who is paying for all the leaking gas? You bet we are. They certainly are not going to absorb it. And they line their pockets with money instead of lining their pipes like they should be doing.
Oil will make a comeback if people see it's cheaper and less hassle then natural gas.
That's how the free market is supposed to behave, no?
Gas has great lobbyist, pushing governors up in New England, for one, to try to legislate banning heating oil and switching to gas, despite a few 'issues':
-Nat gas just doesn't have the capacity to serve these towns.
-Big gas wants to run new pipelines, but doesn't want to upgrade/fix the old ones (well they don't want to pay for it).
-Lobbyist have convinced legislators that fracking won't harm the environment. Fracking is banned in most European countries.
-Big Gas wants these pipelines built so they can export product, not make it cheaper for Americans to get natural gas. Prices for nat gas will almost always go up.
They don't even have capacity now. The gas companies switch all their 'heavy' users (interruptibles) over to heating oil when there are sustained cold snaps. This causes a temporary shortage as well as a price spike--everyone loses. So all the 'savings' for discount rates the interruptibles received throughout the year gets eaten up with a 2 week cold snap.
Who knows that ultra low sulfur, renewable BioHeat burns cleaner than natural gas...it's true but hardly anyone knows.
Who knows that the same heating oil is doing less harm to the environment than fracking, old pipes leaking and burning nat gas...also true but no lobbyist convincing politicians.
Funny how a small residential spill of heating oil gets the people in white tyvek wiping off birds, but the airlines dump millions of gallons a year of toxic chemicals into the ground (they call it de-icing a plane), no one seems to care.
I know of all oil's faults too.
But people better hope oil doesn't go away. If it does, there goes your free market-nothing stops the gas/propane prices from sky rocketing.
3 -
It seems like the obvious alternative to natural gas and oil is a cold-climate heat pump. I studied the question with real bills thorugh a winter cold snap, and found that at a low efficiency heat pump (COP 2.45, or HSPF 8.35) is cheaper over an entire year than gas. It's the annual gas price spike that makes all-electric cheaper--just a couple of weeks of 4x-10x higher gas prices erase the savings.0
It's not one size fits all, which it is good to remember when debating this sort of thing. In my humble opinion, a truly professional heating and ventilating and air conditioning professional -- such as many of the folks on this Wall --should be able to, and will, evaluate all the combinations of heating and ventilating options available for a specific project -- even if they don't specialize in that particular type of system -- and recommend what they feel will work best. That is the mark of a professional, rather than a salesperson.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England6 -
Around here (nw Indiana) you need a cop > 4 to break even with natural gas. Issue is the same on infrastructure availability. Basically you don’t have natural gas unless you live in municipal limits.0
ThisJamie Hall said:It's not one size fits all...
This is the perennial problem that comes from one common mechanical (read energy) code. Good luck getting a code for Alaska to match up with a code for Hawaii without either uselessly-vague terms or enough exceptions to make them, in effect, separate codes.
> ThisThis is the perennial problem that comes from one common mechanical (read energy) code. Good luck getting a code for Alaska to match up with a code for Hawaii without either uselessly-vague terms or enough exceptions to make them, in effect, separate codes.
They use heat a lot in Hawaii?
Depends on the size of the shower?You can have it good, fast or cheap. Pick two0 -
I agree to an extent. Like at @Jamie Hall said, every job needs to be looked at, independent of your personal preference and focus the the facility and its workings.
We took over the HVAC agreement of a major NE golf club. 3-4 year complete renovation. Completely gutted and redone to a "T". All heat/cool by WSHP. Not a tree around for 150 yards. And then came the cold. Most of the building couldn't get over 58 degrees. No secondary stages.
That's not exactly the correct design for the circumstances.
There's 2 large Viessmann boilers serving 2 large indirect and a couple of small space heaters in the basement. We're looking into piping in a heat exchanger to increase the incoming water temp. during the winter with an outdoor temp sensor.
It's a shame it wasn't designed correctly.
My point being, even a high efficiency heat pump, water or air, IMO should have a 2nd stage, electric, hydro coil, obviously in the climate that warrants it, and if and when that 2nd stage kicks in, that eats into the savings. And different regions have different electric rates, so those areas with higher rates also save less.0 -
Best I can tell, the record low in Hawaii is around 50 degrees.the_donut said:Depends on elevation.
I've got a feeling they never use heat for a structure.
I don't know that for a fact, just an assumption.
Of course, I'm weird......I often run air conditioning when it's 50 out.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
@BenDplumber , What part of Dayton did you work? I've been here almost 70 years and in this house 27 years this is the first time I've ever experienced this.0
This happened in Denver a few years back, and I told the water department that they needed to do a search of excessive water usage (winter) in the area, and put feets on the streets to track down the disgruntled (former) homeowner who had cross connected his water service with his gas service and shut it down. They never did find the offender, but they did install a float operated condensate drain in the lowest piping they could find. It would take me about $20.00 in parts, and about 1/2 an hour to start filling the gas main in my street. The utlity even provides a place where you can make the cross connection upstream of the meter
With the general knowledge of the fact that pressure flows from high to low, how does water get into the mains? And as it pertains to the ethyl mercaptan, I'm told that dirt filters most of it out, so that you can't detect it...
I'm thinking doppler leak detection equipment... "Un-accounted losses" make up a fairly significant chunk of every gas utility's cost of operation (water companies too) and yes, we the consumers are paying for it.
Hard to believe that something so simple can''t be tracked down and cured...
ME4 -
We replaced a steam boiler over the holidays. The house had several relatively new Mitsubishi mini-split heat pumps, which could not keep the house above 55 degrees during the bitter-cold weather we had in that period. They did keep the house from freezing, but that's about it.
Haven't seen a heat pump yet that could handle very cold weather. That house wasn't comfortable at all until we got the steam going again.All Steamed Up, Inc.
Consulting1 -
Here some old 12-16 inch underground street gas lines are very low pressure and have rust pin holes, they used corrosive soil backfill in some areas. IF have 6 ft of water in soil over the pipe that's ~ 2.6 psi water pressure outside the pipe, So water pressure outside pipe can be higher than gas pressure, and water drips in.
We had a problem in winter. The street lines were deep enough to not freeze the water in them. So water evaporated into the dry nat gas, till it hit the ice cold meter and froze up blocking gas flow. Gas company "solved" that problem by wrapping meter in electric heat tape and insulation (we paid for the electricity). The next year the $300 gas valves on both of the restaurant's big HVACs failed, HVACs were on roof and their valves exposed to winter cold. Took it apart and found it internally corroded. I should have sent them the bill. Send them the bill if your burner valves fail in a year like mine did.
They said if the heat tape didn't work they could install a methanol bubblier to absorb the water out of the gas.0 -
@sean_armsean_arm said:It seems like the obvious alternative to natural gas and oil is a cold-climate heat pump. I studied the question with real bills thorugh a winter cold snap, and found that at a low efficiency heat pump (COP 2.45, or HSPF 8.35) is cheaper over an entire year than gas. It's the annual gas price spike that makes all-electric cheaper--just a couple of weeks of 4x-10x higher gas prices erase the savings.
I am curious what market you are in. Do you mind sharing your numbers. You made a pretty blanket statement that is just not true in most markets.
I just looked back at the original title, sorry I followed this one bit off topic..."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Dual fuel
You are looking at a low elevation station. It snows in Hawaii almost yearly. And trade winds increase heat loss.ChrisJ said:
Of course, I'm weird......I often run air conditioning when it's 50 out.0 -
The Carrier infinity greenspeed is designed to work well down into the single digits. It's not perfect, but it's better than most heat pumps.0 -
> @Gordy said:
> Mark wouldn’t they have to know their unaccounted losses? Consumption is metered. Somehow what’s delivered to the system is a known.
Excellent point. (I don't have nat gas though)
They MUST know what's going out, so they should show the math. And they should be held responsible without raising rates.
Are those figures public record? Might make a good news article for the areas that need repairs most. From what I've read above, the whole thing ain't too purty.0 -
Speaking only for Denver Water and Xcel Energy (providers in Denver), yes, they know what they treat, and what is billed for. Denver water is now fully metered. And yes, it is public record, if you know where to look. Denver water has a very active leak detection program that "listens" to fire hydrants on each end of a block and can determine where the leakage is within feet of actual leak. they can also determine the quantity (approximately) of the leak so they can prioritize repairs, so the press doesn't give them much flack. They also have a fairly extensive main replacement program and got rid of all of the oak stave mains in the older portions of their system.Gordy said:Mark wouldn’t they have to know their unaccounted losses? Consumption is metered. Somehow what’s delivered to the system is a known.
Now Xcel Energy, I can't really speak for them, but they are scrutinized by the public utility commission, so I have to assume that they too know what goes into and out of their systems, and what the difference (unaccounted for losses) is.
Some cities are still not completely metered on the water side, so it becomes a moving target to track down.
ME
Xcel Colorado has a pretty active program that monitors the condition of underground steel gas lines.
I am not sure how it works, but I can tell you they get very surly if you are temporarily supporting a meter you are digging around by using bailing wire to an electrical conduit.
Once the gentleman calmed down a bit, it was determined that a nylon strap was acceptable to his equipment. He was doing a survey and was set up some distance away. We introduced a new element that was screwing up his test."If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
Our system has buried steel pipe that is plastic or epoxy coated.
It is completely insulated from being grounded. (in contact with the dirt)
An insulating bushing or die electric union is used to isolate the house piping from the company's UG lines and meter.
He may have been testing the integrity of the insulated system and your "ground" wire would have really thrown him off track.1 -
How does water leak into a gas line that has gas pressure in it.? In my area, the pipe down the street used to run at 8 psi (supposed to be 15 psi) and reduced to 7 inches at the regulator on the way into the meter. Those pipes were put in in about 1950.
About 10 years ago, those old iron pipes (that were leaking) were replaced by a somewhat larger plastic pipe running at 50 psi. But even at 8 psi, for water to leak into the line, the pipe would have to be under over 18 feet of water if I calculate correctly.0
- 167 Indoor-Air Quality