Home owner wants to say thanks. Some pics of new install
invermont
invermont Member Posts: 73
There are a bunch of guys here who over the years helped me keep my gb-142 unit running despite a crappy install. Even with high efficiency, I will be almost dead before I make any money back on my investments. Live and learn. Knowledge I can pass onto my children. If I could do it over again I would of gone to school for this stuff. It intrigues me. You guys are full of knowledge, but most importantly you give the average joe hope that there is a solution when it’s 15 degrees outside and you have no heat or hot water. One pic is of my 10 year old gb. Other is a day of getting new boiler in. Added new back flow preventer, pressure regulator,
new expansion tank with better set up, dirt separator, condensate neutralizer. Tomorrow new water tank in better location. Rerouting of exhaust and intake. New boiler is an ibc about half the size of my buderus 142/60. Thank you all and god bless.
Ironman
«1
    HVACNUT Member Posts: 6,853
    Its basically a swap out.
    Most everything else is existing. And I wouldn't exactly say it was "crappy".
  • Zman
    Zman Member Posts: 7,611
    Thanks for sharing.
    I noticed the lack of primer on the vent connections. I am sure you will remedy that when you redo. :)
    Albert Einstein
    HVACNUT
  • ChrisJ
    ChrisJ Member Posts: 16,841
    > @Zman said:
    > Thanks for sharing.
    Maybe.....but you can buy clear primer. I use it on my own stuff because I can get away with it. They also have primer that's clear but glows under a black light.
    kcoppPaul S_3Rich_49
  • Zman
    @ChrisJ
    That may well be the case.
    Using clear primer on venting is a bad idea. You could lose track of which fitting are primed and you will definitely fail an inspection.
    Albert Einstein
  • ChrisJ
    > @Zman said:
    > @ChrisJ
    Do you lose track of which fittings are glued? Being the cement is clear and all...
    Paul S_3
  • Zman
    @ChrisJ
    You should use whichever primer you want....
    Albert Einstein
    Shouldn't it be neither clear nor purple?
    Shouldn't it have been vented with polypropylene?
    Zmanrwhtgdelta T
  • GW
    GW Member Posts: 5,056
    I’m going to take it upon myself to do a purple primer how to video, there’s just some basic tricks. Purple is for pros :)
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    ZmanRich_49HVACguyinMEdelta T
  • invermont
    It is when the exhaust and intake are 1foot from an inside corner.. Ate it up. Almost twice the size I needed for my house. Couple other things that were never done that would of probably doubled it’s life.
  • invermont
    > @Zman said:
    > Thanks for sharing.
    I glue water pipes that carry 136psi. Purple can look nasty if you over run it
  • the_donut
    the_donut Member Posts: 374
    Purple is great for visibility and is fine if you don’t make a mess. I remember working in crawlspace where the only entrance was 40’ in prone position crawling from where I needed to be. The saw slipped and I cut my finger (trying to do the install in one go without measuring and crawling back out). Had a bit of primer dribble into the cut. Feels just like liquid stitch. Would’ve been easier to spot with purple.
  • Rich_49
    Rich_49 Member Posts: 2,781
    edited March 2018
    Purple is your friend . You can hardly see it .
    732-751-1560
    Rich McGrath 732-581-3833
    Ironman4Johnpipe
  • ChrisJ
    edited March 2018
    Let's get back to talking about the ops install..
    invermont
  • GW
    Looks good, I might have taken the 20 minutes to neaten/straighten some of the wiring
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    invermont
  • Ironman
    Ironman Member Posts: 7,726
    edited March 2018
    How about "Hot Glue" which does not require primer?
    We use primer with it regardless.
    Maybe we should start a thread about PVC joining techniques like GW mentioned.
    Bob Boan
  • invermont
    Zman said:
    @ChrisJ
    Zman, Vermont doesn’t have inspectors for residential. The only time your house gets inspected is when you go to sell it. Then it is usually someone who has basically taken online course. It’s a problem.
  • kcopp
    kcopp Member Posts: 4,577
    You will be really happy w/ that set up.
    Very reliable boiler.
    I have a bunch of them in and I have been very happy w/ the results.
    Its a dream to service and it only has 4 moving parts.
  • invermont
    Thanks kcopp, I had them move exhaust and air intake out of the inside of a corner. Exhaust was moved over to be more away from inside corner. Intake was put about a foot around the corner on a different wall. All together about 5 feet from each other. I’m still worried about it sucking on exhaust. In the wind last night I could see some steam blowing around the corner and coming near the intake. I’m wondering if I should have them come back and check on that
  • kcopp
    Can you snorkel it up and have the termination up at a 45 like they show in the book?
  • invermont
    Here is a photo. I read the book. It almost seems I could almost go as high as I want within reason. I don’t think 3 or 4 feet should make a difference. I know one set up shows air at ground and exhaust straight up through 2 story roof if I remember right. They even mentioned something about not worrying about rain getting in because the condensate pump would take care of it
  • invermont
  • kcopp
    You should be fine w/ cross contamination. Especially since its around the corner.
    Personally I would like to see the intake a bit higher of the ground and at 90. You don't want the intake to suck in fluffy snow.
  • invermont
    Was thinking same about the 90. I’m thinking on cutting that 45 off and adding one. There’s a short retaining wall I put in there next to my patio. I’m going to get rid of that to give me some more height on my intake. I was just freaked out watching some wisps of steam blowing down around the intake in the wind last night. Only happens when it’s firing low. I guess you could get that with most set ups
  • rickh
    rickh Member Posts: 22
    IBC states the exhaust cannot be PVC. We use Centhrotherm, usually on both, it looks goofy with 2 different types of piping. Boilers are very reliable
    HVACguyinME
  • kcopp
    Where are you reading that?
    I admit pvc is a less desirable venting material.
    Page 1-5 says it is approved in the US... if you are in NH or NY you may not use pvc,
    ZmanChrisJ
  • invermont
    Not sure of the piping. Just before it enters the house it is dark gray.
  • heathead
    heathead Member Posts: 239
    From IBC manual
    c) Sidewall Direct Vent with separate vent and air pipes shall be terminated as
    follows:
    • Both the inlet and exhaust terminations shall be located on the same plane (side) of
    the building.
    This means it cant be on two different walls. It has to do with air pressure differences when the wind hits the building.
  • invermont
    heathead said:
    From IBC manual
    follows:
    the building.
    I read that. They also show intake at ground and exhaust through the roof of the house. I sent a photo to ibc to see what they say
  • HVACguyinME
    HVACguyinME Member Posts: 25
    Two things, PVC is perfectly fine with venting any IBC, it all depends on AHJ. And the venting on this boiler is not correct, the air intake is on a different plain then the exhaust. Another words the air intake and exhaust need to be on the same side of the house.
    kcopp
    EBEBRATT-Ed Member Posts: 18,216
    @GW I for one need your purple primer video. Anything to do with caulking, glueing , sealing and I am a complete mess.
    LOL where I worked 20 years ago one of my friends who was a tech there go up in a meeting and said to the service manager. "you know Ed is good at a lot of things but don't let him use a F-----g caulking gun"
  • GW
    yes just a couple of simple tips and you can be a purple pro. I'll make a vid someday.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • Rich_49
    That rule does not apply to all appliances
    732-751-1560
  • HVACguyinME
    @Rich_49 That is why I said "IBC"
  • Jean-David Beyer
    I do not, since I am not a heating contractor. But the contractor that installed my mod-con did lose track. They put purple primer on the exhaust, but forgot to put the glue in. Later, the condensate ran into the boiler on the outside of the exhaust pipe and drowned the control board.
    If I were running things, the primer and the glue would have perhaps faint different colors but together, they would be a loud visible color.
    Solid_Fuel_Man
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,644
    @Jean-David Beyer I've often thought that very same thing.
    CPVC cement is bright orange, and I've wondered why it isnt required to have regular PVC cement a color as well.
  • ratio
    ratio Member Posts: 4,061
    There's a few brands around here that have a blue-colored glue (supposed to be water resistant, for gluing in the rain I guess?) that I use, so I can always tell if I glued a joint, or if someone's made any changes to what I did.
    Solid_Fuel_Man
  • HomerJSmith
    HomerJSmith Member Posts: 2,652
    What is the best way of gluing CPVC to PVC? Opinions please.
  • Zman
    This sounds like the making of a new thread. Not really relevant to this guy's install.
    I like this article https://www.commercial-industrial-supply.com/resource-center/gluing-pvc-and-cpvc-together/
    Albert Einstein
  • ChrisJ
    I use clear primer and glue with no issues.
    But I'll admit I don't do many joints at a time and it's on my own time so I can take my time and take as long as I want.
    It's a little different when you're trying to move fast etc.
  • ratio
    AFAIK you can't glue PVC to CPVC—the chlorine changes things enough that they're not all that compatible. I suggest a mechanical joint.
    That said, aroud here the big box stores all carry a glue that's supposed to do the deed, & I have no data to refute that. I have to admit that, if I were rushed or otherwise limited, I would try it…
