What is wrong with this steam boiler piping

Options
exqheat
exqheat Member Posts: 216
John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.

Comments

  • mattmia2
    mattmia2 Member Posts: 16,871

    it isn't right but it probably works fine on that 60-80 year old boiler with plenty of space above the water line.

    ethicalpaulexqheat
  • ethicalpaul
    ethicalpaul Member Posts: 8,833

    Although, if it isn't banging, it isn't backing up, or at the very least if it is backing up, it's not causing banging. Is it banging?

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,241
    edited April 7

    I think this is a trick question:

    What is wrong with this steam boiler piping?

    No Text, No explanation, No other information, Just a picture.

    And being the proverbial Irishman that always answers a question with a question…. My reply:

    "☘️ Whit aire ya talkin' 'bout? ☘️"

    So without context to the question, You need to tell me more about what is happening on the job.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Intplm.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,213

    If the header is level and if it doesn't bang leave it alone the condensate is going back into the boiler. After a cold start very little condensate in a hot header.

    mattmia2Mad Dog_2ethicalpaulexqheat
  • exqheat
    exqheat Member Posts: 216

    I was concerned as well about the constriction created by the smaller coupling going up to the system piping?

    John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.
  • mattmia2
    mattmia2 Member Posts: 16,871

    I'm not sure I see a reducer between the main and the header, but it is normal for the header to be bigger than the main, the header slows down the steam velocity so that entrained water droplets can drop out but once those droplets are gone the steam can move faster.

  • ethicalpaul
    ethicalpaul Member Posts: 8,833

    True that is what the larger header is supposed to be for, but if you watch my videos you will see that:

    1. there are very rarely any drops of water that appear even inches above the boiler.
    2. they are not "entrained" but rather, just get randomly splashed up there. Even on my ridiculous experiments with a 5/8" supply, I never once saw a drop that would stay entrained. They just don't.
    3. they fall out of the steam without any need for larger headers—they just hit the wall of the pipes and are then captured

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    exqheat
  • exqheat
    exqheat Member Posts: 216

    Everyone should be following this link. It's a good refresher for those that can "see the steam".

    John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.
    ethicalpaul
  • Intplm.
    Intplm. Member Posts: 3,030

    If it's not banging then, as mentioned above leave it alone.

    If it is banging you should install one of these, an eccentric coupling to drain the condensation out of the header.

    Black Cast Iron Eccentric Reducer (Domestic)__92174.png
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 16,871

    or a nipple the size of the header and a reducing ell or a nipple and ell and reducer in the vertical…

    ethicalpaulIntplm.EdTheHeaterMan
  • 109A_5
    109A_5 Member Posts: 4,063

    Not convinced an eccentric coupling is best practice. An eccentric coupling would probably be better than it is now. I think an elbow would drain the best.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ethicalpaulIntplm.EdTheHeaterMan