What is wrong with this steam boiler piping

Options
exqheat
exqheat Member Posts: 214
John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.

Comments

  • 109A_5
    109A_5 Member Posts: 4,056
    image.png

    Header won't drain into the equalized properly. Header may not have the proper distance above the water line. A drop header may have been a better choice. However if you are not having any issues I would not worry about it. Is the main parallel or counter flow ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    STEAM DOCTORMad Dog_2
  • Steamhead
    Steamhead Member Posts: 18,509

    I'd still repipe the problem at the left arrow. Water backing up there may cause banging, and corrosion may accelerate.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    IronmanMad Dog_2109A_5