Is this the way they're going in now?

Options
Double D
Double D Member Posts: 467
edited January 14 in Strictly Steam

Does Smith allow all welded near boiler piping?

Peerless and Weil McLain let you know where in the near boiler piping they would prefer to see threaded.

Is there any info out there about the Smith boilers?

My guess is that header will be filled with water before the first radiator gets heat.

1000017665.png
mattmia2Corktown

Comments

  • mattmia2
    mattmia2 Member Posts: 16,730

    it looks like someone gave them a drip but they didn't use it. probably very likely all the water will end up in one boiler or the other too.

    Double D
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,163

    The Smith 28 series has 5" risers. The header size varies but is at least 5" with more than 1 riser. This varies with the # of sections

    Smith doesn't mention threaded or welded piping but the manual appears to show threaded fittings with a union.

    I don't even think they make 5" unions so that is wrong. 5" flanges are available.

    In spite of what many on here will post 99% of all contractors are not going to thread 5" or 6" pipe..Just not going to happen.

    There drawing does show 2 elbows at the top of each riser also something that is seldom done.

    Double D
  • 109A_5
    109A_5 Member Posts: 3,976
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Double DHVACNUTIntplm.Corktown
  • Double D
    Double D Member Posts: 467

    On a pumped return for multiple boilers, what is the purpose of the F&T on the equalizing line?

    1000017672.png
  • HVACNUT
    HVACNUT Member Posts: 7,434

    I wonder how much those yellow handled valves are, and are they necessary. Are they for balancing?

  • dabrakeman
    dabrakeman Member Posts: 1,007

    Is this actually running right now? Colliding steam going into the main riser is wrong and it does seem that drip needs to be hooked up per the manual.

  • Double D
    Double D Member Posts: 467

    @dabrakeman

    This boiler installation in not finished. They have some corrections to make before they run it. My guess is the colliding header would be full of water before the first radiator gets heat.

  • mattmia2
    mattmia2 Member Posts: 16,730

    probably isolation so you can run off of one boiler while servicing the other.

    HVACNUT
  • 109A_5
    109A_5 Member Posts: 3,976

    I'm thinking they are more orange. I bet they are expensive. Looks like it is a King valve.

    No F & T traps in the equalizer like the manual shows.

    If they don't put the F & T trap (or some type of drip) in under the paralleling header, yeah it will fill with condensate, faster if they don't insulate it. looks like there is a plug there now.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • HVACNUT
    HVACNUT Member Posts: 7,434

    They still have lot of work to do. Orange? No. I'll give you Mustard color though.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,163
    edited January 15

    A trap on the equalizer is an overflow trap. It is used when you have multiple boilers connected to the same system where the boilers alternate or one acts as a standby. With the valves open to the header on both boilers and one boiler operating the idle boiler act as as a condenser and fills up with water to an overflow condition if the burner fires you could damage the boiler. The overflow trap should be piped to put this condensation back into the boiler feed tank.

    The stub is on the main header for the trap to drain the header. The supplies to the main header should not be colliding but if only one boiler runs at a time its fine.

    Double DCorktown
  • Double D
    Double D Member Posts: 467

    @EBEBRATT-Ed

    Thank you very much for that explanation. I don't get into doing jobs that big but from time to time, a friend or customer will show me what they have going on in their boiler room.

    It is my understanding from time to time they will be running both boilers at the same time. I brought the colluding header to their attention before I posted. They do intend on addressing that issue. The installing company said they were also going to use threaded 90s at the boiler risers. (Ouch, 5" 90s, get out the chain wrenches. When I get an update I'll let you all know.

  • 109A_5
    109A_5 Member Posts: 3,976

    @HVACNUT These right ? If my Mustard looked that color I would not eat it. I do agree it is not as orange as the color of an Orange, the fruit.

    image.png

    These below are Yellow along with the Caution tape.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    EdTheHeaterMan
  • HVACNUT
    HVACNUT Member Posts: 7,434
    Screenshot_20260114_201219_Samsung Internet.jpg

    Shine a light on it. Its yellow. Are we really doing this?

    Double DEdTheHeaterMan
  • ratio
    ratio Member Posts: 4,234

    A removable cap on the bottom of the drip might be a good idea as well.

    Double D
  • Grallert
    Grallert Member Posts: 1,117

    Yellow is a primary color. Red is a primary color. Orange is some combination of the two. I bet there is at least a % of red in that yellow. Someone needs to climb up there and get a sample. LOL

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

    Double DEdTheHeaterMan
  • Double D
    Double D Member Posts: 467
    edited January 17

    Rather than using 5" threaded 90s on the boiler risers, the mechanical contractor is suggesting unsing these. One on each boiler riser and one on the equalizing line for each boiler.

    I've seen the these used on hot water heating but never on low pressure steam. There are flex connectors rated for low pressure steam.

    Does anyone see any problem using them?

    1000017692.png
  • 109A_5
    109A_5 Member Posts: 3,976

    " Rather than using 5" threaded 90s "

    So they are going to use a straight flex coupler and bend it to 90 degrees ? If so is there a bend radius specification ? In general that seems like a bad idea.

    Or is the flex coupler pre made as a 90 ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,163
    edited January 18

    Don't let him use those they will fail. They are made for linear expansion and contraction not bending and twisting.

    they probably choked on the price of a 5" 90 or they can't get them.

    Look online and search for 5" threaded elbows.

    You will be looking for a while, probably not available.

    Most contractors weld everything 2 1/2 and up

    ethicalpaulbburd
  • mattmia2
    mattmia2 Member Posts: 16,730

    you can put the flex coupler in a straight section of vertical pipe where the pipe needs to move for expansion, i wouldn't want to see them used as a 90 regardless of if they are preformed that way or not

    ethicalpaulSteamhead
  • dabrakeman
    dabrakeman Member Posts: 1,007

    We had a guy up in the UP Michigan thread and fit 5".

  • pecmsg
    pecmsg Member Posts: 7,053

    Rather than using 5" threaded 90s on the boiler risers, the mechanical contractor is suggesting unsing these. One on each boiler riser and one on the equalizing line for each boiler.

    I'd be looking for a different contractor!

    Larry Weingartenmattmia2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,163

    I am not saying 5" can't be threaded but 5" was always a size with limited availability. I urge anyone to go on the internet and look for 5" malleable or CI fittings…….see how long it take to locate some

    PC7060
  • Double D
    Double D Member Posts: 467

    @EBEBRATT-Ed

    The engineer of the building these boilers are being installed was told by the mechanical contractor that it would take 2 months to get the 5" 90s, so he did some checking himself. He was able to find a local supply house (Ferguson) that had 3-5" malleable 90s in stock and they showed they had 11 in California. They told him they could get them here in 5 days. Good to know in case I might need them.

    CLamb
  • ChrisJ
    ChrisJ Member Posts: 17,371

    Why would the price of the 90's bother them? Wouldn't that just be added into their quote for the job?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Double D
  • ratio
    ratio Member Posts: 4,234

    If the sell price is too high they might not get the job.

  • pumpcontrolguy
    pumpcontrolguy Member Posts: 32

    We use these all the time to help reduce vibrations and very slight misalignment on pump piping, these are not meant to bend more than a few degrees. They are for very minor offsets, small expansions, contractions, vibrations. Do not even think of trying to use them as a bent 90!

  • Double D
    Double D Member Posts: 467

    @pumpcontrolguy

    I'm not thinking the mechanical contractor was going to try using them as 90s, one on each boiler riser and one on the equalizers drop. He would like to leave his 2 welded 90s in place.

    If it were me, I would be using the treaded 5" 90s. The flexible connectors wouldn't be an option for me.

  • ChrisJ
    ChrisJ Member Posts: 17,371

    Isn't that similar to what's often used on car exhaust?

    They sure seem to hold up under those condiitons…… 1200-1400F exhaust and being blasted by road debris / salt etc.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 16,730

    I think the exhaust stuff is different. The stuff for water and steam is a plastic tubing of some sort reinforced with stainless braid to keep it from deforming when it softens under heat and to increase the pressure rating.

    The exhaust stuff I think is just densely woven stainless because the one piece of it I used as part of a catalytic converter had soot work its way out through it.

    ChrisJ
  • CLamb
    CLamb Member Posts: 348

    The exhaust flexible pipe I've seen is braided metal on the outside and a corrugated pipe on the inside.

    ChrisJ
  • Double D
    Double D Member Posts: 467

    I stopped by the job to get some close-ups of the king valves they were using in case anyone is interested.

    1000018096.jpg 1000018095.jpg 1000018090.jpg
    mattmia2
  • Double D
    Double D Member Posts: 467

    They removed the piping to the colliding header and put it in a pile outside the boiler room. They also removed the welded 90s on the boiler risers and used threaded 90s. The welded equalizers were also removed and replaced with threaded pipe & fittings. Time will tell but it appears they are going to take the 6" from each king valve and bring them straight up into the existing 12" header.

    1000018098.jpg 1000018100.jpg 1000018093.jpg 1000018094.jpg 1000018092.jpg 1000018089.jpg
  • Double D
    Double D Member Posts: 467

    As I suspected, they are going to pipe the boilers into the existing header eliminating the factory recommended common header. Should I suggest getting something from the manufacturer or does this write-up sound like something that will work? It appears to have been drafted by a sales rep.

  • Double D
    Double D Member Posts: 467
    edited March 4

    One thing I forgot to mention is this is a vacuum system. Thanks to @Pumpguy Dennis Pataki for his help on the vacuum side of the system. It has been working great since 2020.