Question about glycol

RayWohlfarth
RayWohlfarth Member Posts: 1,635
We suggested installed glycol in a small office building's hydronic heating loop. The customer had frozen coils several times. The owner called and cancelled it, saying it would create leaks throughout the system because the piping was thirty year old black iron. An expert advised them not to do it. Is that true? Will glycol create leaks? Thanks
Ray Wohlfarth
Boiler Lessons

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,432
    From my experience..no!  I've used that Cryotek for over 35 yrs never an issue.  Maybe some cheaper or corrosive mixtures are harmful.  Mad Dog 🐕 
    ethicalpaul
  • pecmsg
    pecmsg Member Posts: 5,187
    No, a weak solution of glycol and water does no damage. The PH level must be checked and adjusted accordingly.

    If it did how is it used in ice rinks that hold 1000's of gallons?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,205
    Agree with the above posts. Glycol can be a headache and the PH has to be checked it can turn acidic but Ice Rinks are a perfect example as @pecmsg mentioned.

    Freeze stats should be used on the coils but the control techs in this era don't always do what they should do.

    In the old days with pneumatic controls if the freeze stat tripped you would send the NO heating valve wide open, shut down the fan and close any OA dampers to prevent a freeze.

    Would it be possible to repipe and just use Glycol in a new piping loop that just serves the coils with a heat exchanger in between so you don't have to glycol the entire building?
  • WMno57
    WMno57 Member Posts: 1,408
    Glycol doesn't wear out, meaning it doesn't lose its freezing protection. The additive package of corrosion inhibitors (CIs) do wear out. CIs must be compatible with all components in the system
    True for automotive and hydronics. Automotive is ethylene glycol and hydronics is propylene glycol. They both include additives for corrosion protection. There is no lifetime ethylene glycol for automotive. Some last longer than others, but eventually the corrosion inhibitors lose their ability to protect.
    In automotive you usually flush and fill. In hydronics you can do annual testing and replenish the corrosion inhibitors as needed.
    Many race cars don't use glycol. Straight water has better heat transfer. Water makes less of a mess on the racetrack.
    I like EBEBRATT-Ed idea of not glycoling the entire system, just the freeze prone items.
    GroundUp
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,635
    Thank you sirs I appreciate it Isolating the coils would be expensive as they are also the pipes that feed the perimeter baseboard heat. I appreciate the suggestions
    Ray Wohlfarth
    Boiler Lessons
  • pecmsg
    pecmsg Member Posts: 5,187
    @RayWohlfarth
    There is no need to keep the freeze protection very low. Even a little goes a long way. The issue if as you get near the freeze point the solution gets thick. That in turn doesn't play well with pump seals. I'd rather replace a seal or 2 then frozen coils and pipes!
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,635
    Great point @pecmsg Thanks
    Ray Wohlfarth
    Boiler Lessons
  • hot_rod
    hot_rod Member Posts: 22,953
    Define the word “leak”
    That green fuzzy meringue build up you see around connections that have had glycol added is that a leak? Or only if it drips on your head?

    The integrity of the threaded connection has much to do with it.

    DowFrost is a PG
    DowTherm is an EG

    Larger systems that do not have potable water interface often chose DowTherm.
    lower cost, better heat transfer.

    EG has been used for aircraft deicers due to cost, but it also breaks down quicker than PG in the bio ponds and can be flushed down drains.

    once inhibitors are added either PG or EG it become a higher toxicity, EG more so. I certainly would not drink hydronic PG

    although food grade PG is in your toothpaste and many food products 

    We had a Dow glycol engineer on Coffee with Caleffi years ago, he talked about the various pros and cons

    Maybe a better wording is it is “more prone to leaking out of some connections”

    For example, put glycol and press connections in the search box above for some real life experiences 😮
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • hot_rod
    hot_rod Member Posts: 22,953
    Keep in mind the pump spec also. This example for a 200' loop of 3/4 copper
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • retiredguy
    retiredguy Member Posts: 969
    edited January 19
    @Ray, my concern with glycol is that it makes the water more slippery and could potentially seep out of any connections that are not perfect. Also, consider what all the other guys have written. I would rather have a weak glycol solution which would be less slippery and still offer freeze protection.
    Zman
  • hot_rod
    hot_rod Member Posts: 22,953
    Somewhere between 20 and 50% is reasonable.

    Although look at the particular brand. 50 % from one brand to another can have different protection numbers. The bargin brand 50% is a different freeze number than the more expensive brands.

    I noticed Grundfos has add a glycol % to the hydronic pump spec. I think that translates into below 50%?

    Also a water hardness spec of 15 gpg.

    Although "lower than approx 15 gpg" leaves some room for interpretation.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,635
    Thanks @hot_rod As usual, you are still teaching me LOL
    @retiredguy Thats a great point. I am just concerned I will get that call on a Friday afternoon telling me there's water everywhere. Thanks
    Ray Wohlfarth
    Boiler Lessons
  • pecmsg
    pecmsg Member Posts: 5,187

    Thanks @hot_rod As usual, you are still teaching me LOL
    @retiredguy Thats a great point. I am just concerned I will get that call on a Friday afternoon telling me there's water everywhere. Thanks

    If that happens I'll guarantee it's been leaking for months.
  • hot_rod
    hot_rod Member Posts: 22,953

    Thanks @hot_rod As usual, you are still teaching me LOL
    @retiredguy Thats a great point. I am just concerned I will get that call on a Friday afternoon telling me there's water everywhere. Thanks

    A glycol crystal ball is needed to predict if there could or will be some seeping if glycol is added :) Probably find one on E-bay!

    What would the $$ be to redo any joints that would leak or seep?

    Maybe adding freeze stats on the coils is a better option. That is common on hydroair units installed in attics.

    I think Dan Foley had a post on that option years ago, here.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • hot_rod
    hot_rod Member Posts: 22,953

    Thanks @hot_rod As usual, you are still teaching me LOL
    @retiredguy Thats a great point. I am just concerned I will get that call on a Friday afternoon telling me there's water everywhere. Thanks

    Brad White had a clever analogy on glycol back about 18 years ago here on HH.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    pecmsgmattmia2
  • WMno57
    WMno57 Member Posts: 1,408
    Glycol in hydronics is somewhat OK if it is maintained every year. The included inhibitor additive package MUST be compatible with everything in the hydronic system, and the local water.

    DexCool is a great ethylene glycol for cars with aluminum engines and radiators. Except for the one GM V6 model that had intake manifold gaskets incompatible with DexCool's Organic Acid Technology inhibitor package. GM had control of and knowledge of everything in their line. They had testing labs and thousands of engineers. GM still screwed up.

    How could a contractor possibly know if the additive package of their locally available propylene glycol is compatible with everything in an existing hydronic system? How would they even know compatibility with a soup to nuts new system where they spec everything?

    So yes, I believe Glycol should be avoided in buildings and hydronic systems if possible.

    https://forum.heatinghelp.com/discussion/190758/new-boiler-or-strip-heaters-in-existing-heat-pump-air-handlers/p1
  • hot_rod
    hot_rod Member Posts: 22,953
    How could a contractor possibly know if the additive package of their locally available propylene glycol is compatible with everything in an existing hydronic system? How would they even know compatibility with a soup to nuts new system where they spec everything?

    I see the brands now promoting multi metal formulas.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    WMno57
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,205
    Seldom if ever need more than a 30% mix in most areas.
    hot_rod
  • Jamie Hall
    Jamie Hall Member Posts: 24,390
    I wonder... if the problems are really all that bad... how often do you have to add coolant to your truck's radiator? Running at 190 F and 15 or 20 psi?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • jumper
    jumper Member Posts: 2,384
    I worry about something galvanized inside. My experience with glycol in chilled water is that glycol is somehow consumed. Of course that adds fresh inhibiter.
  • mattmia2
    mattmia2 Member Posts: 10,626
    edited January 20
    So the summary is glycol will corrode things if you don't maintain it, it flows better than water(but has a higher viscosity), and doesn't evaporate so it can find leaks that water didn't.

    Note that hydronic systems are usually copper, brass, iron, and steel. Not a big deal for compatibility. The o-rings and other synthetic rubber components are a bit of a wild card but they are a bit of a wild card with water and chlorides too. The manufacturers frequently don't pick great materials to begin with.
  • mattmia2
    mattmia2 Member Posts: 10,626

    I wonder... if the problems are really all that bad... how often do you have to add coolant to your truck's radiator? Running at 190 F and 15 or 20 psi?

    2 years to 5 years depending on how its additives are engineered.
  • hot_rod
    hot_rod Member Posts: 22,953
    mattmia2 said:

    So the summary is glycol will corrode things if you don't maintain it, it flows better than water(but has a higher viscosity), and doesn't evaporate so it can find leaks that water didn't.

    Note that hydronic systems are usually copper, brass, iron, and steel. Not a big deal for compatibility. The o-rings and other synthetic rubber components are a bit of a wild card but they are a bit of a wild card with water and chlorides too. The manufacturers frequently don't pick great materials to begin with.

    It’s the low surface tension that can lead to leaks. At room temperature glycol surface tension is 1/2 that of water. It goes lower as you heat the fluid

    It seems both crimp fittings and Victraulic struggle with glycols. The make up of the rings or gaskets?
    We had trouble with the green fiber washers on the glycol solar systems. Months down the road green fuzz appeared on many of those connections. Connections that held 80 psi water tests with no problem.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Larry Weingarten
  • mattmia2
    mattmia2 Member Posts: 10,626
    I'm thinking the chemical compatibility of the synthetic rubber compounds. This mainly comes from my noticing that faucet washers are made of compounds in not recommended column for water and chloride.

    It is hard to say with the composition gaskets if it was a synthetic rubber that was incompatible with glycol that was used in the composition or that it just didn't conform well enough to hold the more fluid glycol. I suppose compressed air would tell you.
  • hot_rod
    hot_rod Member Posts: 22,953
    mattmia2 said:

    I'm thinking the chemical compatibility of the synthetic rubber compounds. This mainly comes from my noticing that faucet washers are made of compounds in not recommended column for water and chloride.

    It is hard to say with the composition gaskets if it was a synthetic rubber that was incompatible with glycol that was used in the composition or that it just didn't conform well enough to hold the more fluid glycol. I suppose compressed air would tell you.

    As I recall Viega wanted you to used a different o-ring on solar glycol systems. Maybe a combination of the glycol and potentially 300 plus degree stagnation temperature. I think it was a grey colored o-ring. Or as they call it a sealing element, they don’t use the word o-ring.
    Or is that two words😏
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,635
    Wow thank you all. m getting a real education on glycol
    @hot_rod Loved the Brad White observation
    Ray Wohlfarth
    Boiler Lessons