Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

The last word about c-wire thermostats and wiring diagrams.

JohnNY
JohnNY Member Posts: 3,293
edited August 31 in THE MAIN WALL

Not that I actually believe this wiring diagram will eliminate all questions about the topic but this should make it fairly simple to do for the next guy. Or girl.
(photo redacted due to a labeling error)

Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Mad Dog_2EricPetersonScottSecorAlan (California Radiant) ForbesMikeAmannIntplm.Solid_Fuel_ManEdTheHeaterManErin Holohan Haskell
«1

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    It really is just that simple. Thank you, @JohnNY .
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    JohnNY
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    I have posted this one several times in the past couple of years. The only difference is a separate transformer. Solves all the issues for about $40 extra material
    Alan (California Radiant) Forbes
  • PeteA
    PeteA Member Posts: 180
    I know its not the prettiest but this is how I set up a 24v transformer to give me the C wire for the other boiler I installed last year. I'll probably end up doing the same thing on the boiler I just did because I want to install the wifi thermostat here also.

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    I say @Robert O'Brien 's AC Ready or Kool Kit solution is the easiest/simplest solution and the only one I use.

    There was an error rendering this rich post.

  • HomerJSmith
    HomerJSmith Member Posts: 2,635
    edited October 2023
    Ya, John, but you still have to use 3 wires to the thermostat, I want to get it down to 1 wire. Work on that. I've been working on that for years, but I think I'm close. After all, a wire saved is a wire earned. Benny told me that.
    EdTheHeaterMan
  • JohnNY
    JohnNY Member Posts: 3,293

    Ya, John, but you still have to use 3 wires to the thermostat, I want to get it down to 1 wire. Work on that. I've been working on that for years, but I think I'm close. After all, a wire saved is a wire earned. Benny told me that.

    1 wire is going to be tough but I think it's worth shooting for. I'll get back to you shortly.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Solid_Fuel_Man
  • PeteA
    PeteA Member Posts: 180
    @STEVEusaPA I hear ya, not my best moment but it was October 1st and had to have the heat on and ready for my tenants so my plan is to go back and extend the 3/4 along the ceiling and then drop the flex line down from above so it lines up better. :smiley:
    Alan (California Radiant) Forbes
  • Teemok
    Teemok Member, Email Confirmation Posts: 677
    I'm confident that water heater is powering the furnace. Spill the beans! How is it done? One wire? Bro?
    PeteA
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    edited October 2023
    @JohnNY, I had to LOL your discussion post. I believe there are about 50 of those same comments out there. I doubt if yours will be the last. But you can always Dream, Can't you.
    Tommy Dorsey recorded a song with a similar quote in 1938

    And I remember when I was in my teens working on cars, My neighbor thought the Germans figured out the whole 1 wire thing. Every light bulb on that VW he owned, only had one wire going to it. All the way back to the late 1950s when they started building the BUG. Boy those Germans were smart!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    JohnNY
  • Teemok
    Teemok Member, Email Confirmation Posts: 677
    Understanding the C wire might be as elusive as understanding some female anatomy. Everyone has a theory and they also think yours is way off base.
    Alan (California Radiant) ForbesMikeAmann
  • EricPeterson
    EricPeterson Member Posts: 217
    I find the comment relating to female anatomy unnecessary and offensive.
    Maybe it's just me.

    Eric Peterson
    mattmia2Erin Holohan HaskellAlan (California Radiant) ForbesEBEBRATT-EdMikeAmann
  • Teemok
    Teemok Member, Email Confirmation Posts: 677
    Rumor has it, one nest t-stat that is charging draws max 25 milliamps or 0.6va @ 24v x4 for some CYA is 2.4va. Will confirm via measurement at some point. Many people have a single zone with the t-stat acting as a switch only and they need 0.6-2.4va. from the existing 24v system. Different from needing a C wire for 3-12 charging thermostats or larger loads. Less words...hmmm. A picture.







    @EricPeterson You are right. Unnecessary. Not the first time a joke hit that button. Years of the trades have made me insensitive I suppose. You don't want to hear the stuff that's said in passing out here. So uncouth. I'm not sure what the offensive part was. The reference to a human body part or to the general ignorance about it? Anyway, I hope the offense doesn't last.

    Alan (California Radiant) Forbes
  • ChrisJ
    ChrisJ Member Posts: 16,317
    JohnNY said:

    Teemok said:

    Understanding the C wire might be as elusive as understanding some female anatomy. Everyone has a theory and they also think yours is way off base.

    Of course you know this but here's how it makes sense to me.

    A couple decades ago, the electrician we used to hire to wire our boilers gave me a piece of electrical theory that I've never forgotten: "Everything we deal with is either a power source, a switch, or a load." He went on to explain that we start at the source and end up at the load. In our case, the load was most often a gas valve or a pump. Everything in between was a switch.
    The C-wire converts the thermostat from a simple switch to a combination switch and load. It both consumes power (charging, display, integral logic, etc) and allows or interrupts power through it to the burner circuit, terminating at the gas valve. Now, the same can be said of a probe-type low water cut off, and also a motorized vent damper or zone valve. These are combination loads and switches. Simple!

    A switch just needs a power wire to one side of it and the switching action opens or closes the circuit to permit or interrupt the continuity of that path to the load.
    A load requires a path back to neutral or ground to allow for a constant flow of power. That's the third *C wire.
    If someone here can say this clearly in fewer words, please be my guest. My students will thank you.
    The only thing I'd like to add is, if we started calling it the Common wire instead of "C Wire" it might make it easier to more people to understand.



    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    JohnNYSuperTechMikeAmann
  • ratio
    ratio Member Posts: 3,791
    ChrisJ said:

    The only thing I'd like to add is, if we started calling it the Common wire instead of "C Wire" it might make it easier to more people to understand.

    Hmmm. I'm not so sure; at least, I have to distinguish between a common wire & a common terminal of a two pole switch often. I've taken to calling it a C wire & com terminal.

    But source, switch, & load is pretty helpful! Thanks, @JohnNY!

    EdTheHeaterMan
  • mattmia2
    mattmia2 Member Posts: 10,955
    Common is confusing too. In this case common is the unswitched side of the power source that is connected directly to the load but if you just said common to me with no knowledge of hvac I would think of it as the switched side of the power source.
  • ChrisJ
    ChrisJ Member Posts: 16,317
    ratio said:

    ChrisJ said:

    The only thing I'd like to add is, if we started calling it the Common wire instead of "C Wire" it might make it easier to more people to understand.

    Hmmm. I'm not so sure; at least, I have to distinguish between a common wire & a common terminal of a two pole switch often. I've taken to calling it a C wire & com terminal.

    But source, switch, & load is pretty helpful! Thanks, @JohnNY!

    Whatever works for you.
    You can also call it the neutral. Regardless, that's what it is.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    JohnNY
  • ChrisJ
    ChrisJ Member Posts: 16,317
    mattmia2 said:

    Common is confusing too. In this case common is the unswitched side of the power source that is connected directly to the load but if you just said common to me with no knowledge of hvac I would think of it as the switched side of the power source.

    When you hear "common" in electrical, you think of a switched wire?
    I think of neutral.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Hyrdonic_Nut88
  • Teemok
    Teemok Member, Email Confirmation Posts: 677
    Some Trane furnaces call it B. Sometimes labeled as B or C or B/C, just to make it more fun. Then there's W/B and Rc. Keeps people guessing. See? Taco has a 24v and Com terminal on some boards. Theory and knowing how to test for it is best. Not so easy to teach. I've seen the proverbial light bulb go on with a few I've worked with. They are suddenly much more valuable. Always fun when they C the light.
    Alan (California Radiant) Forbes
  • mattmia2
    mattmia2 Member Posts: 10,955
    edited October 2023
    B is for blue which it usually the 5th wire in a t-stat cable. Rh and Rc are red for heating and cooling, the non-c end of the transformer.

    I think of common as the supply(Vcc B+ + etc.), the ungrounded(whether that is a chassis ground or an earth ground) end of a power supply. I think of the end that everything sinks to as ground.
  • ChrisJ
    ChrisJ Member Posts: 16,317
    edited October 2023
    mattmia2 said:

    B is for blue which it usually the 5th wire in a t-stat cable. Rh and Rc are red for heating and cooling, the non-c end of the transformer.

    I think of common as the supply(Vcc B+ + etc.), the ungrounded(whether that is a chassis ground or an earth ground) end of a power supply. I think of the end that everything sinks to as ground.

    Common in this case, (C Wire) is literally the ground, neutral etc.
    The R wire is the unswitched "hot", so to speak.

    All thermostats for decades have had an unswitched "R" wire. They lacked the other side of the circuit, the common.


    My "C" wire literally goes to the grounded jacket of the boiler which is where the other side of the transformer goes to as well.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 10,955
    edited October 2023
    ChrisJ said:

    When you hear "common" in electrical, you think of a switched wire?

    I think of the wire before the switch that everything connects to.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    Common is confusing.

    How about a 3 way switch? Same as single pole double throw. One wire on the switch is always referred to as "the common" even though it is a hot wire.
  • mattmia2
    mattmia2 Member Posts: 10,955

    How about a 3 way switch? Same as single pole double throw. One wire on the switch is always referred to as "the common" even though it is a hot wire.

    It took me a long time to find a diagram of a pair of 3 way switches where they showed the actual switches instead of a black box that 3 wires confusingly attached to.

    ethicalpaul
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    ChrisJ said:

    The only thing I'd like to add is, if we started calling it the Common wire instead of "C Wire" it might make it easier to more people to understand.

    I'm not sure that would work Chris. I myself happen to have placed a very uncommon type of wire on the common terminal of a rare control that in not commonly used in an unusual place when we start talking about this on an regular basis, when in unfamiliar territory.

    It is not uncommon to be irregular when approaching this subject. And talking about the opposite of common, and the whole Irregular thing, I would do the whole exlax® joke but I don't want to offend anyone @EricPeterson. Some of us have grown out of the poop joke stage. Some not. And @pecmsg has a lot to say about this whole Nest thing. Don’t let him fool you, he is actually a secret admirer




    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Alan (California Radiant) ForbesGGross
  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    And then you have the whole colour thing. Electricity, I have sometimes said, is colourblind. Just becasue one colour is normally used for the hot feed to a thermostat -- red -- for instance, and white for the switched lead, doesn't mean that someone didn't decide to switch them (since it doesn't matter to a battery or older conventional themostat.

    Never assume that a certain wire colour has a certain meaning or function! Granted, it should, but... does it? As someone said a few years back -- "trust, but verify".

    I loke the term "common return". It's clear. It's also never switched.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    HomerJSmith
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    @mattmia usually the three-way switches sold now have 1 black (or darker) colored screw which is the common. but I always check them with an ohmmeter before hooking them up.
  • mattmia2
    mattmia2 Member Posts: 10,955

    @mattmia usually the three-way switches sold now have 1 black (or darker) colored screw which is the common. but I always check them with an ohmmeter before hooking them up.

    that it is a spdt switch with the travelers connected to the poles. most diagrams don't show that.
  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,215
    edited October 2023
    Can you define travelers and poles for me?
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • mattmia2
    mattmia2 Member Posts: 10,955
    er, single pole double throw so one pole with 2 throws. i'll draw a sketch later if i think about it.
  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    SPST -- One wire in, one out. Handle one way on, one way off
    DPST -- Two wires in, two out. Handle one way both on, Handle other way, both off
    SPDT -- One wire in, two out. Handle one way input goes to one output, other way input goes to other output. May have centre off.
    DPDT -- two wires in, four out. Handle one way both inputs go to one pair of outputs, other way both inputs go to other pair of outputs. May have centre off.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    JohnNYEdTheHeaterMan
  • mattmia2
    mattmia2 Member Posts: 10,955
    The throw is the number of positions the switch has that connect through the switch.
    Th poles are the number of switches ganged together on a common lever/shaft. For example a double pole breaker switches 2 line connection simultaneously.

    This is a 3 way switch:


    A 4 way switch sits on the travelers and crosses or uncrosses the travelers.

    If the source and load are at the same end a hot can go to the far switch instead of a neutral to the load.
    STEVEusaPAAlan (California Radiant) ForbesMikeAmann
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Yeah I was taught 'travelers' also.

    There was an error rendering this rich post.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    edited October 2023

    Can you define travelers and poles for me?

    A traveler is a person that is taking a trip away from home. They may take a short trip of an hour or so, but those folks are usually called commuters. Traveler is usually reserved for those that are away for weeks at a time.

    As far as Poles are concerned, those folks are from a country in Eastern Europe that is just west of Ukraine and Belarus and east of Germany and just north of the Czech Republic and Slovakia. and just south of Lithuania and the Baltic Sea. Many Poles are Travelers but not all Travelers are Poles.

    I hope that helps you get a better understanding of that situation.

    I asked Matt from out graphics department to draw this illustration for you Thanks @mattmia2

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    TeemokJohnNYCLamb
  • Teemok
    Teemok Member, Email Confirmation Posts: 677
    HAHA! Ed you did it. I wrote it out and erased it. Hats off. Travelers are another name for Gypsy's
    EdTheHeaterManSuperTech
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    @Alan (California Radiant) Forbes

    Looking at @mattmia2 diagram usually a 3-wire cable (black, red, white and ground) are run between the three-way switches. Why they call them 3-way switches is another bad thing because there is nothing 3 way about them. They are just SPDT switches.

    The two hot wires between the switches (normally black & red) only one of them is hot at any given time. Why they are called "travelers" is another mystery.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    edited October 2023

    @Alan (California Radiant) Forbes

    Looking at @mattmia2 diagram usually a 3-wire cable (black, red, white and ground) are run between the three-way switches. Why they call them 3-way switches is another bad thing because there is nothing 3 way about them. They are just SPDT switches.

    The two hot wires between the switches (normally black & red) only one of them is hot at any given time. Why they are called "travelers" is another mystery.

    They are called what someone named them over a hundred years ago because that guy needed to explain it to someone else... Just ask @ethicalpaul about the Equalizer that does not equalize anything. There is even a video about it.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Member Posts: 10,955
    i believe the identified screw on the 3 way switch is called common
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,401
    edited October 2023
    mattmia2 said:

    i believe the identified screw on the 3 way switch is called common

    Is that the same common as the one on the Nest Thermostat?
    Is no one going to let @JohnNY have the last word on this topic?
    Source, switch, load, conductor, are we all just working on the railroad all the live long day? Take that locomotive down to the switch and load up the boxcars on track 9. and don't forget to tell the conductor where the source of that load came from.
    Can't you hear the whistle blowing, Dina blow your horn!
    Tooo many martini's... Time to go to bed!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?