New Boiler install (edit) passed inspection :)
Comments
-
-
I know there are one or two books highly recommended (and available?) for steam systems on this site. Do they recommend or explain the engineering behind drop headers?
I admit I know nothing about steam, but it seems that whenever a steam boiler is having fits and repiped with a drop header (among other things), the system runs like a dream.
1 -
In fact, The Lost Art of Steam Heat, Revisited has a section on page 95 called "And Consider Using a Drop-Header" with a nice photo. I'll have that in my evidence stackMaxMercy said:I know there are one or two books highly recommended (and available?) for steam systems on this site. Do they recommend or explain the engineering behind drop headers?
I admit I know nothing about steam, but it seems that whenever a steam boiler is having fits and repiped with a drop header (among other things), the system runs like a dream.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el2 -
ethicalpaul
for some of us who dont do a lot of steam, I prefer you repipe it kinda poorly so we can see the effect on those clear tubes!! Of course I dont mean this, but I really liked your videos and selfishly want to see it done poorly so it further proves the usefulness of a drop header.Tom
Montpelier Vt2 -
What are the ramifications of piping the header the way the inspector wants (other than the work involved), then correcting it after you get permit approval?
0 -
What about getting a PE to sign off on it?0
-
Probably none in practice, but I wouldn't go to the trouble honestly.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Maybe the counterflow diagram in the PB Steam survey could be used to show him that steam can move properly through the drop header? It's mind boggling that this could be an issue. The majority of experiences I've had with inspectors have been positive but I suppose its possible the inspector doesn't want to learn from a homeowner. Or hopefully - perhaps once he has had an opportunity to study it he will understand and approve it.1
-
-
-
STEAM DOCTOR said:Just cross out wherever it's says Peerless on the boiler and write Burnham. i can try to save the jacket of the next Burnham that I remove😉😉😉2
-
I see this in my Peerless manual too, and in this situation it couldn't be more absurd. I would have gladly paid ethicalpaul to do my install had I only known then what I know now, and I would have gotten a properly piped system done in black iron pipe, clean and running at correct pressure from the get go with dry steam. And some other stuff I won't get into.nde said:...
Having looked at their manuals a fair bit over the last year when researching new boilers I am not sure if this disclaimer was always there or they just added it!?!?!
any installation or maintenance techniques described in any of this literature should not be attempted by homeowners.
2 -
Aww thanks! I could use the money to pay my fines from doing installations without a license 😂
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
it's funny, i just read that section for the first time last night. first, let me qualify that i'm not a contractor or PE, but i can't really see any possible downside to a proper dropheader other than the extra initial cost. if you want i'm sure i could find the formula for steam velocity through the header. maybe being able to show the inspector the actual steam velocities would at least help convince the inspector that you aren't just a hack. the other thing i can think of is that section of the book also talks about putting in a steam separator. so if it's gonna be a battle to get your dropheader approved, maybe it'd be easier in the long run to swap in a steam separator and get the same effect (and i'd imagine steam separators are probably even more effective than dropheaders at drying out the steam, so you might get better overall performance to somewhat justify the extra expense). the nice thing is you can ask the inspector ahead of time about the steam separator, and since the separator itself would have install instructions and stuff you'd definitely be able to show it was done properly. hope it helps. you were most helpful with my problems.ethicalpaul said:
In fact, The Lost Art of Steam Heat, Revisited has a section on page 95 called "And Consider Using a Drop-Header" with a nice photo. I'll have that in my evidence stackMaxMercy said:I know there are one or two books highly recommended (and available?) for steam systems on this site. Do they recommend or explain the engineering behind drop headers?
I admit I know nothing about steam, but it seems that whenever a steam boiler is having fits and repiped with a drop header (among other things), the system runs like a dream.1 -
Well I don't actually need the drop header, nor a steam separator. With clean water at the normal water line, the boiler doesn't have a single drop of water getting into the steam supplies, so if it turns out I have to put a wrench on it, I'll just remove the drop header and pipe it with a normal header as per the instruction manual. But thanks for the note and ideas!
Oh and this inspector is not going to be swayed by facts like steam velocity. All he is concerned about is the manual. And I don't really blame him. After spending a couple years on this forum, I wish more inspectors would be concerned with installers following the manual!NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
ok well good luck. i'll be replacing my boiler soon. this insight into Peerless might sway my decision a littleethicalpaul said:Well I don't actually need the drop header, nor a steam separator. With clean water at the normal water line, the boiler doesn't have a single drop of water getting into the steam supplies, so if it turns out I have to put a wrench on it, I'll just remove the drop header and pipe it with a normal header as per the instruction manual. But thanks for the note and ideas!
Oh and this inspector is not going to be swayed by facts like steam velocity. All he is concerned about is the manual. And I don't really blame him. After spending a couple years on this forum, I wish more inspectors would be concerned with installers following the manual!1 -
Such wonderful suggestions. As if challenging the Inspector or telling him you're smarter than him could ever result in a positive outcome.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
-
Thanks everyone. I wouldn't let this issue change my good opinion of Peerless. There are lots of issues that come into play when it comes to the documents that a company puts out into public.
I did communicate to the inspector the purpose of the drop header because he asked me. I don't know how familiar he is with them either way...he might have just been asking so he could understand why I installed one in this tiny residential boiler.
I did get the feeling he was more familiar with hot water boilers, but that's OK. I'm going to gather up pertinent documents and present them to him and I'll report backNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I can't help but wondering if the first thing the inspector did when he had access to a computer is to read up on drop headers. The irony is that he might very well have read or even be reading this thread right now..ethicalpaul said:
I did communicate to the inspector the purpose of the drop header because he asked me. I don't know how familiar he is with them either way...he might have just been asking so he could understand why I installed one in this tiny residential boiler.
1 -
I have passed 😅
I had collected a bunch of documents but the one he cared about was this one:I had the page from Burnham’s manual, I had the page from The Lost Art. I had the web page from @New England SteamWorks. I had 10 photos of installs by Dave and EzzyT. He wasn’t interested in any of that.
he took the email and said “I’m going to file this and then, god forbid, if anything happens I’ll be covered.” As if the drop header is dangerous?? I asked him again what his concern about it was but he didn’t respond. I think his real concern was simply that I installed it myself and he wanted to make sure every possible issue was addressed.
As he left he asked me “why did you want to install your own boiler?” I told him this house was my first experience with steam and the more I learned about it the more interesting I found it. He readily agreed and said it’s the best heat and he has steam himself.So how does a 30 year industry veteran who is a plumbing inspector who loves steam have such a problem with a drop header? It’s very confusing!!NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el6 -
ethicalpaul said:I have passed 😅
I had collected a bunch of documents but the one he cared about was this one:I had the page from Burnham’s manual, I had the page from The Lost Art. I had the web page from @New England SteamWorks. I had 10 photos of installs by Dave and EzzyT. He wasn’t interested in any of that.
he took the email and said “I’m going to file this and then, god forbid, if anything happens I’ll be covered.” As if the drop header is dangerous?? I asked him again what his concern about it was but he didn’t respond. I think his real concern was simply that I installed it myself and he wanted to make sure every possible issue was addressed.
As he left he asked me “why did you want to install your own boiler?” I told him this house was my first experience with steam and the more I learned about it the more interesting I found it. He readily agreed and said it’s the best heat and he has steam himself.So how does a 30 year industry veteran who is a plumbing inspector who loves steam have such a problem with a drop header? It’s very confusing!!You can have it good, fast or cheap. Pick two4 -
Even with everything you said, I'm going with a lack of knowledge, he's either never seen one, never heard of one, or he just doesn't actually understand steam.ethicalpaul said:So how does a 30 year industry veteran who is a plumbing inspector who loves steam have such a problem with a drop header? It’s very confusing!!
3 -
That’s great news! Whenever I go into a situation, I always look for small details to as a preview of what to expect. I am surprised that the inspector, having seen how neatly and carefully you installed things, and how intentionally you designed the install, he didn’t pause and leave some space from you guys to learn from each other. (But, that’s in an ideal world where he didn’t have a next appointment to get to.) But I’m glad everything worked out for you! Well done!3
-
-
-
-
Well, there is your Christmas present, congratulations!
Now you can come back here to concentrate on other people's steam systems.
Does your wife consider herself to be a "Wall Widow" as mine does, as I view/study "Boiler Phorn" ?
Spelling correction..."Boiler Porn".......my kids just informed me I misspelled the critical word.
And to think that I was one of the first...maybe....to use the term here years ago.
I got the idea from a radio ad that kids said mom was saying their farmer dad was on a "Tractor Porn" site looking at equipment all the time. The SD radio station eventually pulled the add because of complaints. Hope that is not the case here on the wall.6 -
Yep, he once again acted like the glasses weren’t even there!
@JUGHNE you nailed it! I’m constantly getting the stink eye from being on HH!NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
@ethicalpaul
Great news congratulations!!!
Most inspectors are not bad guys.
This is strictly a case of him inspecting a "homeowner job" (no offence) and an installation that doesn't conform to the picture in a manual.
It's all about him covering his a,,
An inspector looks at a job. They don't care if it works, if it runs or anything else except for two things:
1. Does it meet code (including mfg. instructions)
2. Is the installer licensed.
In your case you did a great job but how many other homeowners could do that?
So when they get a #2 (as above) there going to look a littler harder2 -
@JUGHNE you nailed it! I’m constantly getting the stink eye from being on HH!3
-
I tell my spouse, “This is nothing. You should just be glad I’m not on an online dating site shopping for my second husband!”foresthillsjd said:@JUGHNE you nailed it! I’m constantly getting the stink eye from being on HH!
This isn't the only forum I participate on, I am also into boats and crabbing on the Chesapeake bay. My wife refers to my boat as "my girlfriend", and I'm obsessive about the crabs. A few people on here (including Paul) see my Facebook posts confirming this.
I have too many hobbies...1 -
-
KC_Jones said:
This isn't the only forum I participate on, I am also into boats and crabbing on the Chesapeake bay. My wife refers to my boat as "my girlfriend", and I'm obsessive about the crabs. A few people on here (including Paul) see my Facebook posts confirming this. I have too many hobbies...@JUGHNE you nailed it! I’m constantly getting the stink eye from being on HH!
YeahBut I don't see you on the monitor top forum so that's like a big kick in the teeth......Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
-
ChrisJ said:KC_Jones said:
This isn't the only forum I participate on, I am also into boats and crabbing on the Chesapeake bay. My wife refers to my boat as "my girlfriend", and I'm obsessive about the crabs. A few people on here (including Paul) see my Facebook posts confirming this. I have too many hobbies...@JUGHNE you nailed it! I’m constantly getting the stink eye from being on HH!
YeahBut I don't see you on the monitor top forum so that's like a big kick in the teeth......1 -
neilc said:ya gonna frame the signed accepted permit and hang it at the boiler? yeah you are.
you can see the one he tore off in the extreme upper right 😂
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
When I was still working I would go " toe to toe" with a stupid, moron, inspector since we represented the manufacturer and had nothing to do with the installer. My boss and owner got many phone calls. Sometimes I could get that inspector to send someone who actually knew how to do his JOB. They were probably happy when I retired. my 2 cents1
-
So there can't be any valves between the BFP and the pump at the water company? Doesn't seem practical or realistic to me.Youngplumber said:@JohnNY is right about the BFP in some cases. It depends of the type of backflow preventer you have and the application. Some can have valves downstream some can't. Some need minimum clearance and some have to be above flood rim of appliance.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
They don’t sign the permit it seems, they just put a sticker on the appliance.ethicalpaul said:neilc said:ya gonna frame the signed accepted permit and hang it at the boiler?
yeah you are.
you can see the one he tore off in the extreme upper right 😂
I would have demanded that he put the stickers on nice and level. A crooked sticker could result in wet steam. ;-)4
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements