Also search for "steam orifice", both show some older postings.0
-
0
-
I am in northern Nebr. and found my first ones in my 1955 high school. Still had original traps, most probably still working.
The orifices saved them.0 -
Before
After
Update: Today my plumber took out the copper boiler piping and installed all threaded black piping with a 3" drop header and a vaporstat. I can't thank each of you especially, Dan, for giving me all this knowledge involving the art of steam. For the first time in 4 years my home is warm in every room.
What a feeling! Next up orifice plates customized for each radiator from Tunstall. I shall keep you all posted.2 -
-
Excellent!
That looks great! I’m not at all surprised that the whole system has improved. You may even notice that fuel consumption per degree day is reduced as well.Your saga is particularly illustrative since the only thing really different is the boiler piping itself. In the interests of science it really helps.Congrats!On to the orifice plates!Terry T
steam; proportioned minitube; trapless; jet pump return; vac vent. New Yorker CGS30C
0 -
Do you know the lowest pressure the system will work at?
A 0-3 PSI gauge would be needed to know this.0 -
Wow, that looks a whole lot better at the boiler,
remind us who came out and did that work,
was it the original install company ?
known to beat dead horses0 -
@JUGHNE at the moment I have my vaporstat set to cut out 1/2 pound of pressure but it has yet to cycle off due to pressure. My run cycles are 20 mins long because of the cyclegard installed. I may eventually install a safgard in the future.
And yes, I only have a high pressure gauge installed but my neighbor has a setup with a low pressure gauge that I may mimick.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements