Steam Mystery
Comments
-
That’s makes sense to me Charlie .just wondering is that drip on the Hartford loop side I would hope so and how far did they drop down on peerless I use a 18 inch nipple and far done a few counterflows and never has a issue .peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
-
> @JUGHNE said:
> Paul, I did not see a specific box to check for squirrel....Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment6 -
-
You can borrow my FLIR camera for an iPhone.0
-
My money's on this:
Cheap gate valves will do that.Steamhead said:King valve stuck shut?
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Here’s the results. Blockage of the main is the popular favorite
“Other” responses in 2nd screenshot.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
I forgot to vote. I would have voted for a bad king valve.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
-
> @Hap_Hazzard said:
> I forgot to vote. I would have voted for a bad king valve.
Voting remains open 😀NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Still waiting on photosCost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating1 -
What my mind sees from my house,
- 2 steam mains, 1 counter flow, 1 parallel flow.
- Steam won't enter counter flow main.
- isolating Parallel flow main doesn't let steam into counter flow main.
- made sure counter flow main king valve is fully open
- removing plug at end of counter flow main causes water to leave boiler and exit system through open plug
- water can only leave boiler through the end of the counter flow main 2 way. Eater surging through supply piping or built up pressure pushing it up drip line near boiler.
My experience with broken gate valves is when there broken the handle will spin continuously.
@New England SteamWorks said his guy opened it until it stopped making me think the handle is still connected to the gate.
I have seen boiler water so muddy it looks like oil.
I have never seen enough mud to clog a 2" steam main.
I have seen a decent amount of mud collect in the spuds on a single pipe radiator.
I have seen TRV'S completely clogged to the point no steam was passing.
I have had customers who turn off radiators at the supply valves, attempting to reduce their fuel bills by heating less of the home.
Maybe the last owner of this system did just that.
I'm guessing the king valve is good and the radiator valves are off.0 -
There are two kinds of gate valves. The kind pictured above is the industrial type where the stem is threaded into the gate. If the threads strip out, the handle spins but nothing happens. The other kind has the stem threaded into the bonnet and the end of the stem anchored in the gate, so when you turn the stem, the stem is withdrawn as it pulls the gate open. The latter generally have more compact bodies and cost a lot less and are way more prone to flutter. They frequently fail when the gate becomes stuck in the seat and the end of the stem pulls out when you try to open it. The stem still unscrews, but it doesn't move the gate, so it's hard to tell the valve is still closed. This is what I think happened to the king valve.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
> @AMservices said:
> I'm guessing the king valve is good and the radiator valves are off.
Wouldn’t matter. By removing the plug at the end of the main the radiators became a non-factor. It’s the main that’s not heating at this point.
It is certainly possible there are issues with the radiators, but we are not that far yet.
P. S. Headed there now.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com1 -
If the main is filling with water, but isn't heating, the water must be getting forced up through the drip, which would only happen if both king valves were closed.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
And the correct poll answer is:
King valve, human error (valve not open)
Que @ChrisJ “egg on face” meme...New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com4 -
And your requested photos:New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com3 -
That sucks0
-
-
@New England SteamWorks beautiful job as always.1
-
Wow, thanks for the update, glad it was easy to fix!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
In defense of the guys, the valve was initially very hard to open and required a great deal of torque to break it lose. However, they are trained to always open the valves immediately upon installation (they ship closed) which obviously was not done. Then when they went back to be sure all valves open and it wouldn't turn easily, they assumed it was already open. Had they followed procedure it would have been avoided....New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com3 -
-
Don't know how many times I've laid in bed wondering...……………New England SteamWorks said:And the correct poll answer is:
King valve, human error (valve not open)
Que @ChrisJ “egg on face” meme...
Did I turn that switch back on?
I'm sure the Human will not be making that mistake again for a long time3 -
This job reminds me of so many jobs I've been on or had my employees take care of. I can only imagine the amount of tools and materials you loaded into your truck for the trek to this customers house. How much time you spent responding to out ridiculous ideas and thinking of some of those same ideas yourself. Then to finally make the time in your schedule drive all the way out there only to find you needed no tools, no extra materials, and perhaps the customer could have been coached over the phone to fix it themselves.
This is a reminder (for me and I suspect many others) that most often the problem is actually a simple fix, not some oddball quirky thing that no one on the Wall has ever witnesses before.
Glad to learn it was a simple fix.0 -
No question I over thought this one!ScottSecor said:This job reminds me of so many jobs I've been on or had my employees take care of. I can only imagine the amount of tools and materials you loaded into your truck for the trek to this customers house. How much time you spent responding to out ridiculous ideas and thinking of some of those same ideas yourself. Then to finally make the time in your schedule drive all the way out there only to find you needed no tools, no extra materials, and perhaps the customer could have been coached over the phone to fix it themselves.
This is a reminder (for me and I suspect many others) that most often the problem is actually a simple fix, not some oddball quirky thing that no one on the Wall has ever witnesses before.
Glad to learn it was a simple fix.
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
In my opinion you didn't.New England SteamWorks said:
No question I over thought this one!ScottSecor said:This job reminds me of so many jobs I've been on or had my employees take care of. I can only imagine the amount of tools and materials you loaded into your truck for the trek to this customers house. How much time you spent responding to out ridiculous ideas and thinking of some of those same ideas yourself. Then to finally make the time in your schedule drive all the way out there only to find you needed no tools, no extra materials, and perhaps the customer could have been coached over the phone to fix it themselves.
This is a reminder (for me and I suspect many others) that most often the problem is actually a simple fix, not some oddball quirky thing that no one on the Wall has ever witnesses before.
Glad to learn it was a simple fix.
The guys made a mistake, it was a long day, they just wanted the damn thing to work. After a long day it's hard to think clearly.
You wanted all your bases covered when you got there.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment3 -
Would you’ve had felt better if it was a plug or rag in the piping? I don’t think so, instead it was the easiest service call you’ve done in a while, besides you get to show the Yutes you can still do it!0
-
The good new is it was easy to fix, you didn't have to take it apart and rebuild. I had a car that I restored and spent hours taking the wiring harness apart trying to track down a fault only to find a light bulb with crossed filaments to be the culprit. We have all been there, live and learn.
Don't be to hard on your employees, they are humans and we all have a learning curve and tend to rush things at the end of the of the day. They did a nice job on install otherwise.
I wish I could convince the other owners of my building to let me have you install one of your drop headers. They are piping works of art. Look forward to seeing you on Friday. You have done wonders for my system and many other in my area.0 -
What ever happened with this job..?0
-
Bill_Kitsch69 said:
What ever happened with this job..?
New England SteamWorks said:And the correct poll answer is:
King valve, human error (valve not open)
Que @ChrisJ “egg on face” meme...Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
@gfrbrookline Years ago a neighbor's wife blew the engine in her '67 chevy. He was able to buy a brand new engine from GM and paid a local mechanic to swap everything over and install the new engine.
A week later i came home and found him putting that engine back together, he said one of the rocker arm nuts came off, I told him that shouldn't happen. A few days later he was tearing the engine down again and he found the same nut came off again.
I looked at it and told him the nut was missing the crimp that is supposed to act as a thread lock. He was upset as hell and was going to go **** at his mechanic, I told him if he wanted ti **** to start with GM - they were the ones who let that uncrimped nut get into the engine. He got a crimped nut and the car ran fine from then on.
In this case it was that missed crimp in yours it was a closed valve, all it proves is that **** happens and we are here to make sure it unhappens.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge2 -
A friend of mine [really no kidding not me ] heard about another guy who left the rubber plug in the end of the refrig. pipe. My friend started up his new job that went into a deep vacuum on start up. He went to every joint and cut it out looking for that plug only to find it was a bad TEV. The moral is do the easy stuff first.0
-
My dad was on an old diesel submarine in the 60s- these things were 300 foot long steel tubes jam packed with plumbing from end to end. There were valves in every compartment, controlling all the numerous fluids (water, oil, high and low pressure compressed air, hydraulic oil, fuel oil, etc) that stood between 80 sailors and a watery grave. One of the rules dad taught me was "never jam a valve open". The reason being: if it is jammed open, you can't tell which position it is in (in a hurry, in the dark, while depth charges are going off outside). On the sub, if the valve is jammed, it must be closed. To this day, I still turn the garden hose back a bit after turning the valve all the way open, just to save all of our lives in case the boat is attacked...1
-
they still teach that same procedure in regards to the valve on the air tank when you take your scuba diving certification0
-
That is a valve you would quickly know the position of once under water!
FWIW, when shutting fire hydrants off you crank CW closed to the end and then back off to keep it from jamming up over time.
This is another situation where you want the valve completely open or closed. There is a drain down waste port UG to make the hydrant dry for freezing weather. If partly open then this will put full pressure under ground and eventually bubble up in a soggy mess. You check for drain down by putting your hand over one of the 2 1/2" ports and feeling the suction.0 -
What ever happened here?
0 -
Closed valve.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Thanks Charlie..Charlie from wmass said:Closed valve.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements