MegaPress fittings on condensate return
Comments
-
Was the original piping that lasted all these years black steel? Or was it wrought iron?gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
It was schedule 80 steel for the most part0
-
I don’t see an issue with mega press but Monday call them. They’ll give you the documents needed. The
Condensate Too Corrosive?
Tell him if that’s true is the boiler Stainless Steel?0 -
Then wouldn't the same still work?petewarfield84 said:It was schedule 80 steel for the most part
gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
But @gerry gill -- that's so old fashioned!gerry gill said:
Then wouldn't the same still work?petewarfield84 said:It was schedule 80 steel for the most part
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
There should not be a issue.
Is the contractor suggesting that you use Stainless steel mega press? As opposed to the originally specified press fittings?
I would get some documentation from the manufacturer about this.
Is everything else that comes in contact with the condensate also going to be changed to stainless?0 -
-
The Lochinvar Crest is a modulating condensing boiler. The 8000’ of piping you’re referring to must be distribution piping. The flue gas condensation is acidic and with that size of boiler, there will be plenty of it. I’d be concerned about press fittings too. Why not schedule 80 PVC?Steve Minnich0
-
-
-
Lochinvar Crest is not a steam boiler.Steve Minnich0
-
Fair enough --and stupid me. I assumed wrongly that when the OP was speaking about condensate return, that was what was meant.Steve Minnich said:Lochinvar Crest is not a steam boiler.
If it is combustion condensate -- which may be what was meant -- it should be PVC, as @EBEBRATT-Ed said. If it's boiler water, like recirculation from hot water, and it's sufficiently corrosive to pose a problem to the fittings, they have a boiler water treatment problem. However, if it is a concern about chemicals in the treated water, that could be a problem with the O-rings -- but that's not something which stainless steel would fix.
So now I'm confused...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
0
-
-
Sorry
Steve if you misunderstood so I’ll be clearer. There are two systems here .
1. Original bld.1950’s steam system 8000 ft of condensate to be replaced the feed lines all tested good. Venders says the corrosive return H20 will effect MegaPress fittings. *There are 3 separate Smith boilers feeding this system.
2. Second system - Addition 2 Heat exchangers to be replaced with 3 Lochinvare Forced Hot Water boilers. That pipe is all copper and not being replaced all tested good. The flue’s will be stainless steel and that condensate will be treated to Lochinvare spec.(not an issue)
Back to my Question “ can MegaPress fittings be used on the 8000 ft run of schedule 80 Steam returns?..
I have sent Manufacturer a message and asked this question but have not heard back yet,0 -
Yes @petewarfield84, they can. The condensate return for the steam system shouldn’t be acidity really. If it is for whatever reason, the water should be treated.2
-
You can disagree but this post is far different from your first post so the use of quotation marks really doesn't work.petewarfield84 said:Sorry
Steve if you misunderstood so I’ll be clearer. There are two systems here .
1. Original bld.1950’s steam system 8000 ft of condensate to be replaced the feed lines all tested good. Venders says the corrosive return H20 will effect MegaPress fittings. *There are 3 separate Smith boilers feeding this system.
2. Second system - Addition 2 Heat exchangers to be replaced with 3 Lochinvare Forced Hot Water boilers. That pipe is all copper and not being replaced all tested good. The flue’s will be stainless steel and that condensate will be treated to Lochinvare spec.(not an issue)
Back to my Question “ can MegaPress fittings be used on the 8000 ft run of schedule 80 Steam returns?..
I have sent Manufacturer a message and asked this question but have not heard back yet,
Yes, as mentioned above, MegaPress should be fine.Steve Minnich1 -
@petewarfield84
Here's my take. Chop into a 100 year old system and what do you find? Basically the old Cast Iron fittings last forever they don't really rot. The steel or wrought iron pipe is what rots.
Megapress fittings are steel so they will rot the same as the pipe eventually.
If it was me it would be threaded CI fittings and schedule 80 pipe.
Depends on how much make-up water is added and the water treatment. I have seen schedule 40 condensate lines last a long time as well.
So the real question is, how old is the stuff your replacing? And what was the old material. That will give you an indication0 -
EBERATT, thank you for your response, ideally yes I agree with your choice of fittings and connection. Contractor is choosing a real aggressive approach 3 months for all work to be done, most work is in crawl space/ basement locations some places it’s 3 ft high.
I spent 30 plus years dragging 4 ft pipe wrenches through these locations so I get that it’s not easy.
During the design phase I thought that this project would take a year plus . The Mega Press is ideal for these locations and aggressive time frame ,my hope is Apollo will agree with most of you and say their product will work.
Thank you all for your input.0 -
@petewarfield84
Megapress is approved for low pressure steam and condensate so of course they (Viega) will say it's ok to use , and it is.
May not be the best choice or the most long lasting in my opinion
0 -
Use a condensate neutralizer.0
-
It’s lasted since 1950, and they want to try something different? As Dan says,” you can have it cheap, good, and fast.....pick two”!0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements