Hole in Steam Boiler
The patch will be exposed to steam from inside the water jacket at 232 deg F and flue gas on the outside of the patch surface. Two possible issues with this repair, one is temp degradation and the possible different expansion rates of the two dissimilar materials during heating cycles.
I did the repair and the next day I ran the boiler all day. Pressure built indicating the patch seemed to have corrected the problem. The next day I took a peek and the patch looked perfect. Time will reveal the wisdom of this approach.
Question: Before the repair, raising the temp 5 degrees would empty the boiler requiring a refill. After the repair, raising the temp 5 degrees lowered the water in the sight glass by 3/4" which seems excessive to me. Pressure built to 2psi and I couldn't find any leaks in the return or the radiators. Do I still have a problem?
Thanks,
dlipter
Comments
-
-
Raising the pressure will lower the water level in most systems. How much depends on the cross section are of all the drips at the elevation of the water line.
Now as to the repair. As @pecmsg implies, unless you pressure tested that puppy at 30 psi (twice the pressure relief valve pressure) you have a potential bomb there. Let us consider this matter. You have a patch which holds at the moment at 2 psi. Now you run the boiler at 2 psi; water temperature inside is 215 Fahrenheit or thereabouts (3 degrees above boiling). What happens when that patch lets go? Now the boiler point of the water inside is 212 Fahrenheit. Now all that water wants to boil. Not all of it will, of course, because in boiling it will also cool -- but a good bit of it will; enough to push a good bit of what doesn't out of the hole. You can try the experiment on your car's radiator, if it overheats... it's pretty spectacular.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Unfortunately that most likely isn’t the only corroded area, you just patched the most obvious one that rotted through. More will continue to rot through. That boiler is the most notorious boiler to corrode when used for steam. If it’s still under warranty Burnham may replace it with a Megasteam boiler.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
If the patch lets go while under 2psi pressure, what will happen? Will the steel canopy above it and the steel housing around the boiler be breached?0
-
Bomb is a strong word.... Will I have just a wet floor or will I have metal fragments flying if the patch fails. Consider that the patch is surrounded front, back, left and right by cast iron and two layers of steel above it.0
-
You will have a boiler full of water that is heated to greater than the boiling point at normal pressure.
If the patch fully fails, the boiler water will turn to steam pretty quickly (due to the suddenly lower pressure) and the steam will shoot out of that hole.
So I wouldn’t call it a bomb, but rather a steam gun.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
You will have a good mess.
The other question is why are you running the boiler at 2psi? 1 pound or 1/2 pound should be plenty.
You really need to get a new boiler.
And we don't talk pricing on this forum....
0 -
The boiler was set up by the installer with the pressuretrol set for 2 psi. I dont have a 0-3 psi gauge yet so I am guessing using the pressuretrol scale as a measure.0
-
-
I’ll be honest. You were better off doing nothing. I had a hole bigger than yours and ran the boiler from January until the end of the season, heated just fine, just used a ton of water. It had a hole so at that point who cares how much water it uses?
I hope while doing the repair you also formulated a plan to replace the boiler in warmer weather, it’s dead it needs replaced you aren’t avoiding that.0 -
And you'll probably have to re-do the near-boiler piping as well. This thread has pics of one such V8-to-MegaSteam upgrade:
https://forum.heatinghelp.com/discussion/168108/most-times-when-we-post-a-diy-installAll Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Bomb is, perhaps, a bit strong. It probably won't disrupt much metal when it lets go, unlike a water heater. What you will have will be a basement which has been filled with live steam and liberally sprayed with boiling water.
In the OSHA manuals, this is a situation which is correctly called "IDLH". Immediately dangerous to life and health. The best case? No one was down there when it let go, and all you have to do is replace all the electrical equipment which was. All of it. Plus anything else which was water or steam sensitive -- power tools, electronics, files, whatever. Worst case? Someone was down there and got sprayed with boiling water while the steam asphyxiated them.
I don't usually do the OMG routine but... a lungful of live steam is 100% fatal, although not, usually, instantly.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
wonder how his insurance company would respond if something bad happened...0
-
I wouldn’t use bomb, but at 2 PSI you would be shocked how much steam will come out if it lets go all at once. You could run the numbers, but based on some personal experiences I’d say it will fill your basement pretty handily and you don’t want to be there if it does. Steam displaces oxygen and as Jamie said will cook your lungs quite effectively.
Of course all these are worst case scenarios, but they are based on a lot of personal experiences and knowledge of steam.0 -
OK I get the picture.
Replacement is in order!
What is "Sizing the heat loss EDR'?0 -
Steam boilers are sized so that the amount of steam they produce matches the amount of steam the radiators can condense.dlipter said:...
What is "Sizing the heat loss EDR'?
Fortunately, there is an easy way to do this, and it's EDR. EDR stands for "equivalent direct radiation", and is a measure of the actual surface area of the radiator -- all the tubes and everything -- with a factor for the configuration. It's a pain to actually measure, but happily there are tables -- available on this site, or in the book "Every Darn Radiator" -- to do the math for you. Just go around and tally up all your radiators and how big they are and add that up.
Then, to make it really easy, all residential steam boilers (and some commercial ones) have, as part of their specifications, the EDR rating of the boiler -- what it will produce in terms of steam.
So... you've tallied up your radiators and have a number, and then you go and find a boiler which matches reasonably closely (doesn't have to be exact). And there you go.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
OK....
I"m learning so much here!
King Valves, Return Valves, Mud Leg Valves, Drop Headers....
I live in the NYC area and will need to find a good steam contractor. I don't think my oil delivery company Petro will satisfy me as an installer with all this new found knowledge.0 -
@dlipter
Most important don't order a replacement until you have measured all your radiators. This is the only way to size the boiler.
Then you need an installer that really knows steam and will actually read the installation manual and pipe the boiler according to the manual.
Most won't read the manual they already know everything and have installed boilers by the thousands.....beware1 -
I appreciate the wealth of knowledge shared here.
If the patch fails why wouldn't the released steam just go into the vent pipe and up the chimney? Is the volume so great that the steam will travel down and out the bottom of the boiler too?0 -
Do you have natural gas available?dlipter said:OK....
I"m learning so much here!
King Valves, Return Valves, Mud Leg Valves, Drop Headers....
I live in the NYC area and will need to find a good steam contractor. I don't think my oil delivery company Petro will satisfy me as an installer with all this new found knowledge.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
> @dlipter said:
> I appreciate the wealth of knowledge shared here.
>
> If the patch fails why wouldn't the released steam just go into the vent pipe and up the chimney? Is the volume so great that the steam will travel down and out the bottom of the boiler too?
No one knows. But they have described some possibilities. People don’t like situations where if something fails, no one knows what will happen.
One possibility is that everything would be fine, but that one isn’t the one anyone is concerned about.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
@dlipter -- try John Cataneo -- @JohnNY -- Gateway Plumbing and Heating (he's in the Find a Contractor tab). Or @EzzyT . Or @Dave0176 . You have a wonderful choice of really good contractors to help you out here!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Yes I do have natural gas available. Is that a better choice over
Oil?0 -
It will certainly help the house's resale value. At least around here, according to several realtors I've worked with, no one wants a house with oil heat.dlipter said:Yes I do have natural gas available. Is that a better choice over
Oil?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Why is oil heat not wanted by buyers?0
-
Well, for starters, no tank taking up space and that can possibly leak, no running out of oil when the oil company doesn't deliver on time, no smells............All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
@Steamhead +1
Also every home buyer fears being the one to deal with switching over and/or dealing with a tank failure.
Underground tank being the worst possible scenarioNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
In every market that I know about, natural is cheaper to operate than oil.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
One person I know wound up with a small EPA monitoring station in his yard and a five figure expense after their above ground tank leaked. Not worth the risk IMO0
-
-
In that case, I'd use a double-wall tank.Jamie Hall said:I'd switch if I could -- but those of us out in the boonies don't have natural gas, and aren't likely to get it in the foreseeable future. Sigh...
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I’d use a ground-source heat pump
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
For steam?????ethicalpaul said:I’d use a ground-source heat pump
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
No, to replace oil steam. I’d go water-water. I hate oil, probably more than I should
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Yesterday I found a boiler leaking water falls from a middle sections.. the property manager was begging that i do something temporarily so they would have heat during Christmas.
Unfortunately the leak was dripping all over the burners and pilot assembly so a patch or anything of that nature was out of the question. 50 apartments without heat on Christmas, all because of a lousy hole
Did I mention that this is a 6 section monster boiler and there are 6 old leaky sections laying about 10 feet away from the boiler..
Merry Christmas to those who have heat and to those who don’t!!0 -
Probably a severe lack of maintenance and now a lot of folks are without heat on Christmas .Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I don't "hate" oil, but my earlier post reflects the market in my area. Everyone wants gas. Have to work within that.ethicalpaul said:No, to replace oil steam. I’d go water-water. I hate oil, probably more than I should
Converting a steam system to hot water is a bad move. HW runs at over ten times the pressure of steam, and this WILL cause leaks if there are any weaknesses in piping or radiators. Also, a HW radiator gives off only 2/3 the heat of the same size steam rad, so the building may not heat well. And even if it does, the rads would need to run hot enough that a mod-con would be out of condensing range, reducing its efficiency.
So a double-wall tank, as made by Roth or Granby, is the answer. Unless you do a complete system tear-out and replacement, in which case only a one-percenter could afford it.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
Oil is great. Don't let the plumbers put you off!
Mostly because the greatest, most efficient, and longest lived steam boiler on the market is the MegaSteam, -and it is oil only.
You'd be nuts to switch. Keep oil. Get a MegaSteam.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements