Location of thermostat low voltage.
How can you find the low voltage source to a thermostat that powers several wall heaters. No central system just the thermostat and the heaters. I am thinking maybe the same transformer as the door bell but that works. 1982 home. I replaced the mercury thermostat but still not working.
Thanks Frank
Comments
-
If the thermostat is low voltage there is a transformer somewhere unless the equipment is a POWER PILE system where voltage is generated by the gas flame.
Is it several wall heaters with one thermostat? If so, look in each heater. I assume that there is 120 volt in the heaters to run the fans.
If the transformer is in the basement, then look (usually) around the breaker panels
0 -
-
Low-voltage HVAC control transformers are 24 V. Doorbells are 16 V. They are not interchangeable, and I've never seen one transformer used for both purposes.
—
Bburd0 -
First problem is that you replaced the mercury thermostat. If it wasn't actually broken, it was superior to any other non-smart thermostat you could bu — at any price.
But what's done is done.
Now the next point is that a simple thermostat — like the mercury one you junked — is just a switch. It does not need a power source. It is possible the the device it controls needs a power source to operate — most do — but all the thermostat does is close a circuit. The controlled device is where the transformer would be — if there is one. If a single thermostat is controlling several devices, there may be relays taking the thermostat signal to transmit the call for heat on to the devices — in which case there would be a transformer. probably near the relay, to power the relay.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements