Propress...this is leaking right?
FloMo201
FloMo201 Posts: 75
edited October 6 in THE MAIN WALL
Good morning all,
This fitting is on my heating system. Thoughts….leaking? I have boiler service scheduled for thursday.
Thank you, Flo.
  • leonz
    leonz Posts: 1,945
    Have it repaired with new copper pipe, fittings and lead free solder.
  • HydronicMike
    HydronicMike Posts: 443
    Do you have glycol in the system?
    Either way, I've never had a problem with Viega fittings.
    Ironman
    hot_rod Posts: 28,391
    it could be lack of proper prep on the tube, or the tool out of calibration
    Even with a proper press, they sometimes develop micro leaks. Glycol seems to be more prone to that green fuzzing
    An opinion from one manufacturer on glycol systems
    pecmsg Posts: 7,565
    edited October 6
    I don’t see the dimples on the fitting to show that it was pressed properly.
    might be able to clean it up and re-press it but it’ll probably have to be cut out
  • FloMo201
    FloMo201 Posts: 75
    @HydronicMike , no glycol in the heating system.
    @pecmsg , the dimples are there, just hard to see due to the black staining. To me, they look the same as the dimples on the fitting above it.
    This was installed about 6 years ago and I do not recall ever seeing the green residue. I recall black staining on the pipe but not on the fitting itself….I always though the black was from a sharpie.
    Thanks, FloMo
  • FloMo201
    FloMo201 Posts: 75
    All…I wiped away some of the residue from one side of the fitting. This should give you all a better vantage point. Thank you all, FloMo
    EBEBRATT-Ed Posts: 21,063
    Either way it is a very small leak. Not an emergency but if the system is drained for any other reason, it should be fixed
    pumpcontrolguy
  • FloMo201
    FloMo201 Posts: 75
    Thank you all. You are all so very helpful and it is very much appreciated.
    Flo
  • PC7060
    PC7060 Posts: 1,961
    I was taught if it isn’t dripping it’s not a leak! 😂.
    i’ve seen that type of corrosion on pro , none of which leaked. Maybe originally and self sealed, or got repressed, who knows
    Carefully use a Scotchbrite to clean off the connection. Many sharp edges on press fittings.
    If the oxidation returns you have what might be considered a micro leak.
    Two 45's and a short piece of tube would be an easy replacement for that ell.