0-3 PSI Gauge
What the specifications for the correct gauge? I found a Sensor and Control (YE-6FDL04.0/3#) however in the specifications i says medium temp max is 140 degrees…and ambient temp from -4 to 140 degrees. I assume these specifications are not going to be sufficient.
Any suggestions a reliable mfg?
Thanks.
  • Intplm.
    Intplm. Posts: 3,156
    i guess the specs pertain to what you are measuring and what it's for. So what are you trying to do?
  • Having trouble finding a low pressure gage for steam that DOES NOT come with a stem.
  • I am trying to get a 0-3psi gauge for my Peerless steam boiler.
    So far I have found 0-3psi with specification of 140 degree Fahrenheit max and a 0-3psi with specification to handle steam but it has a 2” stem.
    I am going to start with a 90 degree pig tail then a tee so I can have both the 0-3psi and the 0-30psi.
    hot_rod Posts: 28,524
    plenty of online gauge suppliers. The more you spend the better the quality and accuracy
    Mad Dog_2
    Jamie Hall Posts: 27,906
    The key to this is the pigtail. If there is water in it — as there should be — the gauge never sees steam, and shouldn't exceed a reasonable temperature rating.
    mattmia2Mad Dog_2Intplm.Ironman
  • Thank you gentlemen.
    109A_5 Posts: 4,617
    edited September 28
    If your gauges are sufficiently above the top of the boiler even without a pigtail they won't see steam if the piping is air tight, there will be a cushion of air in the piping.
    If interested:
    0 - 2" Magnehelic without pigtail, with and without snubber
    https://forum.heatinghelp.com/discussion/158333/0-2-magnehelic-without-pigtail-with-and-without-snubber
    Steam pressure. Single pipe steam heat operating at very low pressure.
    Mad Dog_2GGross
  • one of these and a pigtail works well for me
    https://www.supplyhouse.com/Winters-Instruments-PLP305-2-1-2-PLP-Steel-Low-Pressure-Gauge-1-4-Bottom-NPT-w-Brass-Internals-0-5-PSI
    109A_5 Posts: 4,617
    Depending on what you want or expect to see with your low pressure gauge, you may want to know the actual boiler's / system's operating pressure. My system never goes over 2 Inches of water column so with a 0-3 PSI gauge it would never go past the red line I added to the gauge image.
    mattmia2 Posts: 18,233
    you can also make a water seal out of nipples and tees and plugs. if you do that, you can clean it by just removing the plugs.
    Ironman