Pressure testing and leak help
hi.
I just added 3 radiant zones w/manifold and pressure tested that section with 40psi overnight and all good.
Separately I had to replumb and create a primary/secondary loop for baseboard zones. I pressure tested that section separately with 25psi incl boiler and it didn’t hold over night. I used soapy water every joint and nothing! Wondering if relief valve or air escape valve (closed) could be the culprit?
Also did find/fix one threaded leak at the new 3 way mixing valve I added and retested. Do you usually pressure test older systems after adding plumbing upgrades?
Any ideas on locating air loss/leak before I fill it?
assume you have the boiler air vent and other vents capped?
How fast does the pressure drop? Are the expansion tanks isolated from system during the test?
the gauge block is always a suspect. The Schrader valve, and sometimes up inside the gauge itself
Inert gas is another option, or a water test
If you can isolate the boiler it will probably be easier to just fill it with water if you can drain it easily if need be.
unfortunately I cannot isolate the boiler
so no shuttle valves on the inlet and outlet of that boiler
down the road you will regret that decision.
A good, healthy living circ can run 10, 15 years or more. In many cases the iso valves are seized after that many years and you drain down anyways. Those screw slot type iso valves were mostly useless after a few years. IF they did turn off and back on, they leaked around the screw anyways.
Nice to have iso if you swap or remove circs constantly, like a test wall, or you keep getting circ samples :)
Living the hydronic dream1 -
It depends on where isolation valves are located. A valve at each side of a circulator may not isolate the boiler for draining or replacement.
I like a full port Webstone purge ball valve at the boiler return. Then with pump isolation on the boiler supply side you have isolation.
Here is a nice purge detail both boiler side and distribution side. As well as pump isolation
- 87.8K THE MAIN WALL
- 133 Chimneys & Flues
- 79 Pipe Deterioration