Pressure testing and leak help
hi.
I just added 3 radiant zones w/manifold and pressure tested that section with 40psi overnight and all good.
Separately I had to replumb and create a primary/secondary loop for baseboard zones. I pressure tested that section separately with 25psi incl boiler and it didn’t hold over night. I used soapy water every joint and nothing! Wondering if relief valve or air escape valve (closed) could be the culprit?
Also did find/fix one threaded leak at the new 3 way mixing valve I added and retested. Do you usually pressure test older systems after adding plumbing upgrades?
Any ideas on locating air loss/leak before I fill it?
Comments
-
assume you have the boiler air vent and other vents capped?
How fast does the pressure drop? Are the expansion tanks isolated from system during the test?
0 -
-
the gauge block is always a suspect. The Schrader valve, and sometimes up inside the gauge itself
Inert gas is another option, or a water test
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If you can isolate the boiler it will probably be easier to just fill it with water if you can drain it easily if need be.
0 -
-
-
unfortunately I cannot isolate the boiler
0 -
so no shuttle valves on the inlet and outlet of that boiler
0 -
-
unfortunately when I moved the circulator to after the boiler to “pump away” , I replaced the flange valves with straight pipe on the inlet side 😱
0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 122 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements