Commercial Boiler replacement
IDK. I know MA writes its own plumbing code (or used to) then they would adopt NFPA 54 for nat gas and 58 for propane and print all that stuff together and sell it.
I guess they got caught printing it so now when you buy the code you just get the mass rules and regs and plumbing code and you have to go by NFPA 54 7 58 yourself.
I would say no as long as each boiler does not exceed 250,000 btu. But that is just my opinion. Since it is a commercial job the inspectors may want it.
The states adopt the CSD-1 but some states modify it so you will have to check.
Another thing I was thinking about for this job is breaking the old 2-1/2" piping and fittings.
Has anyone ever used an induction heater to remove fittings on an old boiler system ?
If you install high efficiency boilers seriously consider installing a dirt mag. There is probably rust and mud in the system piping. NOT good for new style boilers. May even want to flush out system and add inhibiter.
They will not be high efficient boilers. They will be cast iron.
Any recommendations on breaking loose the existing 2-1/2" pipe fittings?
I will finally be getting started with this job next week.. So I called the inspector to ask a couple questions about the boiler room and he mentioned something I wasn't prepared for…
He told me that the emergency stop switches (at each boiler room entry door) should also shut off the gas supply to the domestic hot water tank. Now I'm not sure, but I don't think this is in my scope of work since I'm there to do the boiler replacement… The current / existing domestic hot water is a stand alone 80 gallon gas water tank with natural draft.
So how am I supposed to kill the gas supply to water heater with the emergency stop switches? Is there a 120volt solenoid available to install "in-line" on the gas supply? It would have to be "hot" all the time and then break the circuit with the e-stop switches. This just seems like another future problem to me..
Any advice on this ?? And technically , is this really my responsibility ?
Any advice on the gas supply to domestic water heater ??
@gpjazz I suppose if the inspector insists you would have to put a solenoid valve in the water heater supply pipe. I guess it would have to be a NC valve and the power is shut off with the emergency switch. The other option (which he may not like) is a NO valve that would be closed in an emergency that would prevent having a valve energized 24/7.
We (Gateway Plumbing and Heating in NYC) have in the past 9 months installed two single-family-home boilers with mid-level boiler room renovations for well into 6-figures each.
This week I'm compiling a proposal for two 800,000 BTU commercial water heaters in a high volume kitchen operating 24-hours that will come in around a quarter million dollars.
If you're not used to commercial installations, and the equipment and codes involved, then the numbers may scare you into thinking you're not pricing the job correctly. Be careful (it sounds like you are). You should make some money on a job like this if you do it smartly. Or you could lose your shirt on endless return trips.
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2 -
Please forgive my ignorance, but this is my very 1st commercial boiler job and I'm getting confused on some things per the inspector..
To clarify again, I am installing (3) Weil McLain cast iron boilers that will be piped into a single main loop to the building. Each boiler has it's own factory installed LWCO and high limits. The inspector told me that I need to add an additional manual reset LWCO and also an additional manual reset high temperature limit control.
Now my confusion on this is where do I need to install these manual reset controls ???
Can I install one additional manual reset control on the main piping loop in boiler room at ceiling level? Or do I need to install the manual controls on EACH individual boiler?
Yes, I will be installing ball valves on each boiler supply/return to isolate for servicing if needed. (But I will be removing the handles of each ball valve) So does this make any difference in this situation?
Also, I'm confused on the combustion air requirements? Is it based off of the total btu's in the room, or the free air opening of the flue piping? The boiler room has a total of 2,152 cubic feet of space. What is the requirement of combustion air per btu's ?
Let me add that my plan is to use 120 volt manual reset controls wired in thru the main 120v feed line.
So therefore any fault of low water or high limit will kill all 3 boilers 120 volt circuits at once
Depends on the size of the boiler and the state code. In MA. if the boilers are over 250K input each we have to have and LWCO and a manual reset LWCO on each boiler for steam and an operating pressure control and a man reset pressure control on steam. for each boiler.
Hot water would require a 1 man reset LWCO on each boiler and a man reset aqua stat on each boiler along with an operating aqua stat (non manual reset) on each boiler
Thease are not arbitary. You need to find the state code in your area and read what they want. it exists somewhere.
Contact: Call 717-214-4319
PA Dept of Labor and Industry
Boiler Division
651 Boas Street, Room 1606
Harrisburg, PA 17121
Another dumb question in regards to the inspection process once I install these boilers…
Will I need to have the entire system 100% complete and FILLED with water and ready to run before the inspector comes to inspect ?
My concern is that if the inspector says that something different needs done in the main water piping to building, I don't want to have to drain the entire building again and re-fill.. It's a LOT of water…
So would the inspector possibly come to inspect the install and check that all controls / safety devices are in place before I fill the system with water? Obviously with an empty system, the manual reset LWCO and high limit could not be "tested".
Are you going to use direct immersion type Low water cut off switches like the McDonnel and Miller RB-122-E, I HOPE you do.
I will never trust digital low water cut off switches no matter the brand based on my past experience with the hydrolevel 3250 plus which failed on me twice.
The McDonnel & Miller RB-122-E has a self cleaning water sensing probe that rotates to scrape any scale or off the probe when water passes over it.
The McDonnel & Miller RB122-E can be mounted in the steam chest, the return to sump piping or the pressure line feeding hot water to the heating system.
McDonnel and Miller recommends that two RB-122-E Low Water Off Switches be mounted on the steam chest of a steam boiler and using two of them in a hot water boiler is cheap insurance to protect the boiler or boilers as long as they are properly wired in series as the first electric controls that will automatically shut the boiler off completely in the event of a water loss.
The McDonnel and Miller RB-122-E has an LED light that shows green when operating and red when the switch senses a low or no water condition. The manual test button that breaks the power connection will indicate a water loss and light up as a red light.
I would have the system filled and ready to run. I have never heard of a "rough inspection" and a "finish inspection" for heating except for gas piping maybe.
But all states and inspectors are different I guess.
In your case (these are replacements correct) the existing system is presumed to be ok. You just need to get the controls and boiler piping correct.
Correct… just replacements in an existing building. And I figured that I need to have it complete and ready to run.. These are just things I think about in the middle of the night.. LOL
Thank you for your direct and helpful response
Yes, I have ball valves installed on the main supply and return lines to the building.
I can't imagine a piping change that they would require that would need you to shut down the entire building except one. I believe that just recently in Illinois there's been a change so that if you have a multiple boiler system each boiler there has to have two low water cutoffs and you can no longer have a shared one. You used to be able to have each boiler with one standard low water cut off and there could be a Central manual reset one above all of them. But that's no longer allowed and they each need their own individual secondary low water cut off so a total of six I think in your case. But that depends on the rules. And there can't be any valves between the boiler and those low water cut offs.
Owner
Steamnowrockford.com
Think your right.
I Know 40 years ago everyone had a big lovefest with Hydrotherm boilers as they were the first "modular boilers" They had no valves on the individual modules and a common factory-made header so as far as the code was concerned it was just 1 boiler. I also installed some Utica's years ago that were designed to be modular but those you had to build your own headers. But as long as you had no valves, they were ok with common controls on the header and just operating control on the boiler.
Well, I have it piped with only one additional manual reset LWCO on the main piping,, not on each boiler. It is a 120 volt man.reset, so it will shut down all 3 boilers at once on a fault
But there are NO valves between any boiler and the man.reset LWCO on the main piping. I did try to ask/clarify this with the inspector, but that's another story. The inspector assigned to me for this job has been very "vague" and very "short" with me whenever I have tried to ask questions. (I'll just leave it at that for now) So that's why I've been here asking questions. Trying to get it right !
So here is my actual piping arrangement..
Keep in mind that all of the main piping is 2-1/2" and space is limited.
Let me know your thoughts please.
Are you eliminating the 2 steel compression tanks hung in the ceiling or eliminating them?
Based on your drawing and my experience with hydraulics repair and maintenance you will have trouble maintaining the flow of hot water because of the weight of the water above it because of the laws of fluid dynamics.
Has the system been so badly butchered that a gravity system would not work? I would contact Bell and Gossett and ask for help with this as a bottom fed gravity hot water system leaving the basement steel compression tanks alone as is would still work if there is no room for a tank on the top floor fed by a circulator with a single riser to act as a nurse tank.
If the old boiler is not leaking it would make more sense to install a second boiler of the same size in series with the old one and a third steel compression tank in series parallel and have bypass piping and valves of the same size as the main piping installed at the same time that would allow for bypassing the old boiler in a worst case scenario in my opinion.
The Dual fuel boiler information and product material I forwarded to you with its correct pipe size would do this and you would only open the loading door on the boiler to brush out the boiler walls and remove the gas burner from the secondary fire chamber to clean out the fire box for the single gas burner when needed. You would be able to leave the current steel compression tanks in place as well. You would need three additional barometric dampers; one for each boiler as designed.
If you install a bladder expansion tank you would not be able to use the steel compression tanks at the same time as the steel compression tanks are the management system where a an expansion tank system is an air elimination system.
As Mr. Holohan is so fond of saying "be the ball" and you will see where the water is going down the pipe. having smaller piping entering the larger piping in the basement will increase the resistance to water flow simply because of the water weight above the boiler(s).
It would help a great deal if we had more pictures of the radiators and the piping in general.
The other worry is the chimney and its condition and whether you can install three separate flues to breech the chimney.
You can never outrun the laws of fluid dynamics and physics unless you have a properly designed bottom fed or top fed system. I believe you will need to make the hot water much hotter to simply get it to rise faster in the water column to the top floor.
Finding out if the radiators have restrictor discs in them would be the first thing to check on the list. If the radiator piping has not been butchered and this was a gravity fed system at one time you can use the existing piping to your advantage.
How is the domestic hot water handled in this system? Does is use separate gas fired water heaters or a common hot water system using a circulator feeding all the hot water lines in the building?
The original steel compression tanks will still be used..
I don't know for sure, but I do not think this was ever a gravity system..
And there is a completely separate gas fired domestic hot water tank
Make sure you use an air separator that has a pipe connection to route the air back into the tank. This will keep it from waterlogging. Also install an Airtrol fitting on the tank.
Also be sure to follow the Airtrol installation instructions regarding pipe size (3/4" minimum) and pitch. If you undersize the pipe and/or don't provide at least the minimum pitch, air will not migrate up the pipe into the tank as it should and the Airtrol will be useless.
Ok, yes I will have an "air scoop" and proper size piping to the compression tanks, and Airtrol on both tanks.
But what about my drawing of the piping arrangement?? Does everything look OK and will it work ??
Not a heating pro, just a homeowner/mechanical engineer who maintains our condo building's two Weil McLain WGO-5's. You aren't showing any bypasses for protection against low water return temps. Those bypasses are required by Weil McLain for high water volume systems like this, if you consult their piping diagrams.
Our cold-start oil-fired WGO-5's don't have bypasses and have run low water temps without damaging the boilers for 20+ years. However, I am continually warned/reminded by the pros here that our boilers lack the "required" bypasses. Maybe because our oil-burner flue gases have less water vapor, or because they run very long cycles, we haven't experienced condensation. However, you're installing gas boilers with high water vapor content in the flue gases, in a system with a massive water volume, and cast iron rads that will keep water temps low. Also with outdoor reset and cast iron rads, your water temp for most of the season is probably going to be under 130 F. That is a recipe for condensation disasters, especially when you divide the load up among several smaller boilers.
It looks to me like you could just add a bypass loop to each boiler with a Caleffi 280 or an ESBE VTC thermostatic bypass valve, but I'm not an expert. @hot_rod or @EdTheHeaterMan may have some suggested piping diagrams. Meanwhile, here's a whole thread on that bypass subject from when I was planning to re-pipe our whole building with two new boilers, with a number of bypass temperature control methods discussed, such as thermal bypass valves, aquastats with circulator holdoff, motorized 3-way valves, etc:
https://forum.heatinghelp.com/discussion/200989/bypass-for-a-buderus-g115-3-boiler/p1
Isn't the bypass achieved thru the closely spaced tee's on the return main?
This is primary / secondary which I thought would also "bypass" some water to / from each boiler.
Let's imagine you have one boiler firing from cold start. The main circ is pumping high flow rate through those large diameter "secondary" pipes. The boiler circ is pumping somewhat lower flow rate through the smaller near-boiler piping. All the return water to that one boiler will be low-temp water coming in from the secondary. And now you have no protection preventing that boiler from getting a very long dose of cold return water while it tries to heat up 100's of gallons.
The primary/secondary does provide hydraulic separation for mismatched flow rates between primary/secondary. What it doesn't do is actively keep the return water temperature above 130 at each boiler, which is what you need to prevent condensation. So you need an active thermal control mixer like a Caleffi 280 or an ESBE VTC on each boiler return, with a branch from the supply feeding hot water into the mixing valve.
Ok.. Another thing I should mention is that I will be using a Tekmar 294 smart control with supply and return temperature sensors. So won't the Tekmar fire all 3 boilers if return water is too cold to prevent ( or lessen ) condensation issues ??
Each boiler will need either an air scoop feeding the bubbles to the series parallel piping to the Steel compression tanks or preferably an Internal air separator sized for the circulator used to remove the air bubbles in the system and feed them to the steel compression tank through the series piping to each airtrol.
The Bell & Gossett Internal Air Separaor(IAS) has a cast in place baffle that forces the water coming off the top of the boiler steam chest to force the bubbles upward to the riser that gradually reaches the airtrol valve or in your case a series parallel header to both steel compression tanks.
Please talk to someone at Bell & Gosset as you need help with this system. I do not believe even piping the boilers in series with common headers for supply and return will solve your condensation problem.
Using Honeywell L8124L mechanical triple aquastats will save you a lot of work and they pair well with the direct immersion self cleaning McDonnell & Miller RB-122-E low water cut off switches. I have them on my coal stoker boiler and they have never failed me in 10 years.
Again, I am not an expert, so take an expert's advice if they can show I'm wrong. But AFAIK, the Tekmar 294 can only tell which boilers to run based on ODR target temp of the supply. You say there's a return sensor, but I don't see one on the Tekmar 294 wiring diagram. And even if all three boilers are running simultaneously from a cold start, depending on how much water volume there is in the system, it could take 30+ minutes for all three boilers to raise the return water above 130. Meanwhile you spent 30 minutes condensing. Then in mild weather when ODR is targeting, say, a system water temp of 120, what do you think the average return water temp is going to be? It's going to be under 120 all day long, for most of the heating season.
I manage a 4-unit 100-year-old building in Boston with all cast iron rads and two cast iron boilers about the size you're installing, and I can guarantee with all your cast iron rads, your ODR water temperature is going to be 130 degrees or less for most of the heating season. So how is the Tekmar going to make the return water hotter than 130, when the supply water temp itself is only 130 or less? The only way to do that is to program the reset curve to give you, say, 150 degree water all year so your return never drops below 130…which kind of defeats the whole point of ODR.
The way to take maximum advantage of ODR is to run as low a supply water temp as possible, which is going to be below condensing temp most of the season in your situation. So as far as I can see, you will absolutely need return water temp protection on each boiler. And the savings from ODR is going to far outweigh the cost of adding three bypasses.
Thanks for all of the insight and information.. I can add by-pass to each of the boilers if required. That can still be done.
I plan to work on this job more this coming week and want to make sure the main 2-1/2" piping and controls is correct. As this is the hardest part to pipe.
Does anyone see any major problems with the main piping arrangement? Will it work ok, per my sketch ??
If you build a pump module for each boiler you can be sure to remove all the air out of the system by using an Internal Air Separator for each boiler placing it at least 12 inches before the circulator.
Mr. Holohan has well drawn pump module drawings in his well written book "PUMPING AWAY" that you could use to create the pump modules to pump away from the boiler and quickly remove the air bubbles in the system.
Using Isolation valves for each circulator in a pump module will allow you to change a circulator if needed without out draining the boiler. Using Isolation valves with gauge ports will let you keep track of the vacuum created by the suction side of the circulator and the pressure side of the circulator. I was able to find a screaming vacuum leak tracing it back to the packing nuts on my steel compression tanks gauge glass and I tightened the packing gland nuts 1/4 of a turn and that stopped the vacuum condition.
You will be able to connect all three boilers 3/4" tapping of each Internal air separators to a single common 3/4" header that will reach the two steel compression tanks at the front of the tanks and install Tees to reach both airtrol valves at the proper slope to allow the warm water to rise to the airtrol valves and the warm water with the air bubbles will rise past the cold water that is dropping back into the water flow entering the supply piping.
If the steel compression tanks have tapping's in the front of the tank you can add Drain-O-Tank valves to make pushing the water into the tanks through the Airtrol valves quickly. The Drain-O-Tank valves will allow you to drain the tanks easier as well if the need arises.
Adding ball valves to the 3 risers to the common header piping that connects to the Airtrol valves will allow you to keep the water in the steel compression tanks if one of the boilers has to be drained as well.
Have you called Bell & Gossett to find out who the local representative is in this area that can help you with this design issue?