Spacepak loses 24 volts after brief power glitch, returns if 240 volt breaker cycled off/on

Options
2

Comments

  • mattmia2
    mattmia2 Member Posts: 17,921
    pumpcontrolguy
  • 109A_5
    109A_5 Member Posts: 4,346

    Since you went to the time and expense of installing the ICM493 what did it report during the power anomalies that upset your Spacepack ? Was the ICM493 set up for the most sensitive activation ? Like 5% with a minute or two of interruption.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Intplm.
    Intplm. Member Posts: 3,134

    I haven't read the entire post, but what is causing the brief/power glitch? Can that problem be solved first?

    Is this glitch happening when a generator kicks on? Is there a delay in the generator's switchgear that shouldn't be there?

    Why the power glitch?

  • 109A_5
    109A_5 Member Posts: 4,346

    Understanding what state the unit is in after it gets glitched is key to resolving the issue. Is there 24 VAC at the 230V-24V transformer, is there 24 VAC between R and C ? Any Fault flash codes active ?

    You could bring the 24V and COM to a place easier to measure, however you still need to see if there are any Fault Flash Codes. It is interesting the Thermostat goes dead.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 4,346

    Looking at the control board there appears to be three self-resetting fuses (Red arrow) and an MOV (Yellow arrow). If your AC power anomalies that upset the board are actually mild over-voltage events the circuitry on the control board may clamp the rising Voltage causing the self-resetting fuses to trip. Typically to reset a self-resetting fuse you have to remove the power source or the load, so the device can cool down.

    I would also make sure the 208 / 230 to 24 VAC power transformer is using the correct primary side tap. If it is erroneously tapped at 208 the voltage to the control board maybe prematurely high to start with.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Jamie Hall
    Jamie Hall Member Posts: 27,701

    @EBEBRATT-Ed has some good thoughts there. Reclosers can sometimes be a bit elusive, particularly if there is an intermittent on the primary. BUT they drop the primary, which then drops several people's 240 volt service — sometimes a whole bunch of people. And it is a full drop of the primary, not just a voltage dip. If there's a problem between the service transformer and an individual service — or just two or three from the same transformer — that may be a dip, but in these modern days when almost all service drops are triplex, that's really kind of rare.

    I still think that somehow you have to catch the dang thing in the act. But that circuit — other than the inner workings of the control board — is pretty darn simple, so other than checking to make sure that you do have 24 VAC on the output of that transformer… you can check the input from the transformer to the board (you may need needle probes to back probe the connector) and see if there is 24 VAC on the R and C terminals (both of the Cs). But if you have 24 VAC on the board input, but not on R and the Cs, kind of suggests that the board is having a fit. You could try also rapping (gently) on the two relays — one of them might be stuck…

    I'm rambling.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • 109A_5
    109A_5 Member Posts: 4,346

    If one of the self-resetting fuses trips causing the control portion of the system and the thermostat to appear dead I would suspect you would find 24 VAC where the power enters the control board an a very low but maybe not zero voltage between R and C.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 4,346

    There are 8 relays on the control board, presently I'm not convinced any of them would interrupt the 24 VAC to the thermostat, but maybe ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Jon_23
    Jon_23 Member Posts: 29

    You are all correct in your suggestion. I don't think I'll get the POCO to do much (it has been like this for years, lots of lines through trees…). I simply need to visit the control board after one of these rare events (and not reset) to check the 24 volts at various points. I suspect it is either the control board or the WS-1 Wetswitch (which, if flakey, could cut the 24 volts to the control board until reset.)

    FYI, The ICM493 is set at 5% and has reported absolutely nothing after any of these events! But the events exist. Sometimes the oven clocks need to be reset, often I can hear my 120 volt UPS's cycle on/of, lights dim or blink… Not all of these crash my air handler, just often enough to drive me crazy (or leave me with a very hot house if I"m returning from work).

  • Jon_23
    Jon_23 Member Posts: 29

    How about the WS-1 Wetswitch? Wouldn't it interrupt 24 volts to the entire control board (and thermostat) until reset. Can't it be reset by cycling the 240 volt breaker to the air handler?

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,864

    @Jon_23

    With no disrespect.

    Its always better to start with the simple things first. It will cost nothing but a little time to check with the neighbors about lights dimming and resetting stuff etc.

    Is changing the control board or futzing around with the controls going to fix these problems?? Like the oven clock or the UPS??

     ""But the events exist. Sometimes the oven clocks need to be reset, often I can hear my 120 volt UPS's cycle on/of, lights dim or blink… Not all of these crash my air handler, just often enough to drive me crazy (or leave me with a very hot house if I"m returning from work).""

    You said lots of wires running through the trees.

    "

    Intplm.
  • 109A_5
    109A_5 Member Posts: 4,346

    You would have to experiment. I found no documentation (and I may have missed it) that claimed the thermostat would go dead if the Float Switch was tripped.

    Just that the AC power has to be reset to restore normal operation, there certainly could be a relay involved.

    That's why I am curious about the Fault Flash codes, if any.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 4,346

    The apparent absence of 24 VAC (R to C on the control board) should be verified, since maybe the power anomaly is actually just messing with the thermostat only. Dead thermostat, nothing works. Not sure if you ruled this out yet, I did not re-read the whole thread.

    I hate to add another Band-Aid type resolution to the situation, but I will. Since you stated the thermostat goes dead when the issue happens, if the 24 VAC (R to C on the control board) is truly absent, that absence of 24 VAC (R to C on the control board) could trigger a timer that would interrupt the power to the ICM493's contractor (T3 or T4) for a specific delay time, effectively resetting the Spacpak unit. So far I have not found a suitable inexpensive timer. The timer would be powered by the 24 VAC at T3, T4.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 4,346

    There are many timer types or modes. Basically the timer type needed would be similar to a 'Watchdog Timer'. However a Watchdog Timer's typically use a cyclic trigger refresh to avoid changing to the reset state. And in this case they don't seem to have a provision to end the reset state.

    So presently, as far as using a timer type device, is the use of an inexpensive PLC programed to do the job.

    The 24 VAC is monitored at the control board R and C. If 24 VAC goes away the PLC shuts off the ICM493's contractor for a short time (one method) or maybe just interrupt the 24 VAC to the control board. After a short delay the power interruption is restored. Operation should be back to normal.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • HVACNUT
    HVACNUT Member Posts: 7,626

    Instead of cycling the circuit breaker, just smack the unit. Its a little more humane than shock therapy with likely the same results.

    Intplm.
  • Jamie Hall
    Jamie Hall Member Posts: 27,701

    Somewhat off topic. You mention the power line goes "through lots of trees". Several points here. First, exactly who is responsible for clearing those trees depends on where you are located (State) and who owns the lines. In some jurisdictions, the drop from the transformer to the customer service entrance is owned by the power company and it is their responsibility to maintain, but in almost all situations (there are a very few old installations) the drop is triplex, and contact with trees will not create a problem. It may create a failure if the line is actually broken, but even if it falls to the ground it will still be conducting normally (note to homeowner: don't mess with it).

    Now if the primary lines are affected by trees, that can cause a problem. Your power company has the responsibility for clearing the trees, but in most jurisdictions it must obtain permission from the landowner who owns the trees to do that. This is not all that easy to do in some cases, and may account for a lack of tree trimming in your area. If the landowner refuses, the power company can obtain an injunction to go on the property to clear, but it takes years (literally) to do that.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • 109A_5
    109A_5 Member Posts: 4,346

    If the Float Switch simply interrupted the 24 VAC to the entire board, two things, there would be no Fault Flash error code, since the board would be dead, and why would you need to cycle the 240 VAC to reset that fault.

    I believe once the Float Switch is tripped (and even if then corrected), that trip event is captured by the control board's logic and locks out operation, so the unit now requires attention to restore operation, the only way to restore operation is to cycle the 240 VAC, which clears the logical fault state if it no longer exists.

    image.png

    And as I said before;

    You would have to experiment. I found no mention in the documentation (and I may have
    missed it) that claimed the thermostat would go dead if the Float
    Switch was tripped.

    The documentation could be wrong or simply left out some interesting details.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 4,346

    @Jon_23, Looking at the bottom side of the control board. For the R terminal of the transformer to get to the R terminal for the thermostat it does go through the Float Switch and a relay. Apparently when the control board acts up the utility's power quality issues are causing very short (probably fractions of a second long) gaps (or dropouts) in the power and this trips the Float Switch lockout. This theory could be proven if the 1 flash Fault Flash Code is present.

    To me this is one of the perfect storm type situations, the unfortunate power quality issues and possible poor embedded software issues in the control board. IMO there is no need to capture a Float Switch fault event in a fraction of a second time period. With the electronics that detects the Float Switch fault, I see no intentional detection delay, so any real detection delay would be in the software. So replacing the control board without any software improvements would probably not help any.

    The manual probably does not mention the thermostat going dead, since not all thermostats have a display or any indication of a power loss.

    IMO to correct this issue the proper way is to get the utility to repair their power quality issue or fix the control board's embedded software (that may never happen). The other way (a Band-Aid repair) is a method to detect the lack of power to the thermostat and cycle the power to the control board, initiating a normal power up.

    Sadly setting up a means to cycle the power to the control board (like a custom timer system) may cause some odd behavior like the added timer system constantly cycling power to the control board if there is actually a situation that is actively tripping the Float Switch.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 4,346

    @Jon_23, I believe I have found a suitable inexpensive timer. The Omron H5CX-AD which was here under my nose all along (Omron H5CX-AD-G). It checks all the boxes for me.

    24 VAC power.

    Trigger signal input via dry contacts (from a relay).

    Isolated relay output (to briefly interrupt 24 VAC power to the control Board).

    An appropriate timer mode.

    Inexpensive when strategically procured.

    image.png

    Understanding the 10 timer modes and their options is always interesting. It appears Mode A-1 with the output time interval set for a One-Shot time period would do what is needed to automatically reset the Control Board after a poor power quality event.

    image.png image.png

    The way this would work, upon a poor power quality event and the control board cuts off power to the thermostat terminals shutting the AC system down. With a 24 VAC relay coil placed across the R and C terminals of the thermostat wiring, this constantly energizes the relay so its Normally Closed contacts are Open.

    With a poor power quality event the relay's coil wired across the R and C of the thermostat wiring would loose power and the relay's Normally Closed contacts would then Close. This would trigger the timer, the timer would then start an On Delay, say 30 Seconds. When the 30 second delay expires the relay inside the timer changes state interrupting the power to the control board (directly or via the ICM493's contactor control). Also the timer's One-Shot delay is started. When the One-Shot delay expires the relay inside the timer changes state again restoring the power to the control board. Restoring the power to the control board should restore the power to the thermostat circuit and energize the trigger relay, disabling the timer's trigger signal. So the timer system sits and waits for another poor power quality event.

    In practice I would probably have both delays at least about 60 Seconds each to let the refrigerant pressures equalize a bit.

    If there is an actual Float Switch fault, the timer system would keep cycling trying to restore normal operation. However since the Float Switch is open the A/C will never come back on until the Float Switch situation is dealt with.

    image.png

    The 24 VAC power that powers the timer could be from the Spacepak unit, the ICM493 or its own dedicated transformer. The trigger relay should be as small as conveniently possible, I would not use a Fan Center relay which is huge for this application. There are some reasonably sized and priced relays with sockets on eBay.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Jon_23
    Jon_23 Member Posts: 29

    'IMO to correct this issue the proper way is to get the utility to repair their power quality issue or fix the control board's embedded software (that may never happen). The other way (a Band-Aid repair) is a method to detect the lack of power to the thermostat and cycle the power to the control board, initiating a normal power up.'

    I'm still waiting for the next event so I can check the board and voltages. As these episodes are very rare and weather related, this could take a long time. Over the last year, the power company has been good. The entire drop from my transformer to house has been replaced and they had a recording voltmeter on my line for over 2 weeks (of course, no storms or episodes during this time).

    While I agree that the embedded software on the control board could be the problem, I would think that if this was the case, there would be other SpacePak users would have this problem. I cannot find any other online complaints and the company (SpacePak) does not find this a problem.

    Just waiting now. Will update but this may take some time. Thanks to everyone for their thoughts and great ideas.

  • 109A_5
    109A_5 Member Posts: 4,346

    @Jon_23, As I described your situation may be the perfect storm. So others may not experience what you do as often as you do, so it is not really on their radar. For example I am not far from my substation, my power never glitches, I can't remember the last time I had to reset a clock other than for a DTS time change. If your situation happened to me once every 3 years would I be complaining about it ?

    Utility re-closure devices shut the power off as a result of an over-current fault. And it is off for a very noticeable amount of time, not just a glitch. When they re-close you should get a normal equipment restart. I believe you have a loose connection somewhere. The loose connection is agitated by the storm, probably wind related. Just replacing the aerial drop to your home without discovering a real defect is just lame in my opinion. It makes it look like they are being proactive but they really are not. Have they done an Infrared inspection of the entire primary back to the substation ? Also like monitoring the voltage during good weather, lame, monitor the voltage when a known bad storm is coming.

    Without the utility doing a proper investigation to find out who is affected and then carefully inspect the wiring they may never find the issue. Bad weather may eventually rip down the bad section and when it is replaced the problem may be gone, but that is a poor way of repairing power quality issues.

    And yes I understand it may take time for you to capture the next event and document the state your equipment is in when it happens.

    In the mean time I'm just putting out some thoughts and ideas if the utility never repairs your issue properly.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Jamie Hall
    Jamie Hall Member Posts: 27,701

    If it's the utility at all… which we haven't found out yet…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • pecmsg
    pecmsg Member Posts: 7,450

    any time I’ve seen a unit that needs a power shut down to restart that’s a safety shutdown. High or low voltage doesn’t matter.

  • 109A_5
    109A_5 Member Posts: 4,346

    @Jon_23 stated

    " Have a Spacepak ESP-G air handler that works great, except when there
    are brief power glitches (power out for no more than a second or two).
    When this happens, the 24 volts seems to shut down (thermostat goes
    blank) and the only way to get it back is to cycle the 240 volt breaker
    off for a few seconds and then back on. "

    @Jamie Hall & @pecmsg I'm having a hard time dismissing @Jon_23's observations.

    Presently I believe (until proven otherwise) the Float Switch is the microcontroller's detected cause of the lockout. As far as I could find it is the only Fault that causes a lockout that requires the power to be cycled to restore operation. However it appears to be an erroneous lockout in this case. So it appears to me as a poor engineering issue, the microcontroller's capture window to detect Float Switch activity and thus activate a lockout does not have to be in milliseconds.

    Ask the question, if the Float Switch never actually opens, a brief power glitch is doing what ? I can only think of a few things that a power cycle would reliably cure.

    1. An erroneous Float Switch lockout. The microcontroller stays active but sees a brief loss of power at the load side of the Float Switch, causing the lockout.

    2. The microcontroller is glitched. If the microcontroller is being glitched, we are back to poor engineering, no or ineffective Hardware and/or Software watchdog timer.

    3. Float Switch contact bounce. The storm is shaking the house and the Float Switch has noisy switch contacts. However that would be ignoring @Jon_23's observation.

    The data to determine this has not been captured yet. The data would be the Power indicator flashing normally and any flash codes after a storm that causes a lockout.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 4,346

    How Linemen find Bad Connections - Thermal Camera

    https://youtu.be/nhREcg_PyQU

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Jon_23
    Jon_23 Member Posts: 29

    Just a few comments until I wait for an 'event' and some data:

    1. Not only could it be the controller board float switch circuit, but it could also be the 'lower pan' WetSwitch which is not part of the control board, but if flakey with power glitches, could latch and cut the 24 volts to the control board (and therefore the thermostat). This also requires a power cycle (or reset button on device) to reset.
    2. While the power to my house is not perfect, the issues are very, very rare and almost always with storms. As suggested, this is NOT a recloser issue as recloser interruptions last long enough to reset everything properly.
    3. I have bothered the power company plenty. Short of buying a very expensive Fluke line monitor, it is going to be hard to catch anything to get them to look harder. I am one of 3 customers on my transformers and my neighbors also notice some 'glitches' during storms but it doesn't seem to cause any problems to their equipment.

    Again, I'll wait and will check the board, voltages, WetSwitch status after the next episode…

    Thanks again to all.

  • 109A_5
    109A_5 Member Posts: 4,346

    Ahhh… I did not understand there was actually two different switches to detect condensate issues.

    Either way if there is no satisfaction from the utility the timer method would still most likely work for an automatic and timely recovery. The timer's interruption point of the power to the A/C equipment may need to be different.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 4,346

    Is it known how the 'lower pan' WetSwitch is wired into the system ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • pecmsg
    pecmsg Member Posts: 7,450

    @109A_5 I'm having a hard time dismissing @Jon_23's observations.

    But didn't he say there were no trouble codes?

  • Intplm.
    Intplm. Member Posts: 3,134

    @Jon_23

    @Jamie Hall , @EBEBRATT-Ed and @Intplm. have all made some reference to the power utility. Their power supply. Have you inquired with your utility provider about this issue?

    Fixing the issue at the unit is fine, but having the glitch/brownout continue from the source will only have you fixing the same things over and over again.

  • 109A_5
    109A_5 Member Posts: 4,346
    edited August 19

    Possibly, I'm not sure, I will go back and look. I thought he simply did not know, since he was just cycling the circuit breaker to restore the operation of the A/C.

    Also up until recently I did not realize there is actuality two methods to detect a condensate overflow. I incorrectly thought the WetSwitch he mentioned in the past was the device connected to the Float Switch terminals on the control board.

    Now I wonder if the two condensate switches are wired directly in series or if the WetSwitch actually interrupts the power to the control board or just interrupts the thermostat circuit.

    EDIT:

    @pecmsg I found no mention of any inspection for trouble codes. Just the access to the unit was a pain and/or the A/C interruption was inconvenient for troubleshooting, so the circuit breaker was just cycled.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • pecmsg
    pecmsg Member Posts: 7,450

    @109A_5

    I found no mention of any inspection for trouble codes. Just the access to the unit was a pain and/or the A/C interruption was inconvenient for troubleshooting, so the circuit breaker was just cycled.

  • 109A_5
    109A_5 Member Posts: 4,346

    Not sure what this follow up posting means ???

    Are you agreeing with me or trying to point out something that I missed ???

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • pecmsg
    pecmsg Member Posts: 7,450
    edited August 19

    I agree the OP Hasn't looked for a trouble code. He's guessing!

  • Jamie Hall
    Jamie Hall Member Posts: 27,701

    I think I need to clarify something. I do NOT think the first place to look is the utility company. It's handy, and big, and distant, and therefore a nice target. It can't possibly my equipment!

    Wrong.

    We don't know that. We don't even know what it is about this particular individual unit is the problem, or whether it's a characteristic of the overall Spacepak design. We hear a lot about a float switch. But are we sure?

    I will agree — quite happily — that intermittent failures are really really hard to find. I've chased a few from time to time.

    So. A few more comments about the utility. What I think I'm hearing is that there is something, somewhere in the Spacepak control board or logic, which causes it to lose 24 VAC power after a brief power glitch. To be blunt, and I don't mean to dump on Spacepak, this simply should not be able to happen. But the first thing which needs to happen is to determine from the full control circuit diagram, what controls the 24 VAC output from the board; it's likely to be an integrated circuit controlling a relay, either ground side driven or power side driven. Then one needs to find out what the logic of that control is.

    I can think of a number of possible scenarios where a timing conflict within the control logic could do what I THINK I'm hearing: a situation where some control does NOT reset properly after a cycle or two of power loss, but does reset properly after say 10 to 20 cycles. It would be nice to know what it was.

    But in the meantime either come up with an on delay timer — which has been suggested and would probably work, but is a kludge, or stop blaming the power company or the float switch or warp drive or whatever and figure out the problem instead.

    For what it's worth (nothing!) my money is on a bad solder connection on a capacitor in the board's power supply section…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Jon_23
    Jon_23 Member Posts: 29

    Quite honestly, this thread is getting a little too long and repetitive, since, because of its length, some folks haven't read the older posts. To answer some of the recent questions:

    1. I believe the Wet Switch is wired between the 24 volt transformer and the control board (as per the instructions) so this could, if flaky, drop the power to the board (and thermostat) requiring a power cycle to reset. If this is the case, the Red LED on the Wet Switch should be on after an 'event.'
    2. I have spent many hours with the power company (and what they have done is listed above). If anybody has a high end power quality recorder they want t lend me (for possibly a long time), let me know.

    I will check for error codes and voltages when this happens again, but it could be a long time (next summer?)

    Thanks again. Jon

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,679

    I have been following this since the beginning and still cant believe the problem source has not been discovered. This reminds me of a rather similar situation form my time as a Lennox Dealer.

    In the 1980s, Lennox Industries had a problem with an electronic ignition control on one of their furnace models. The furnace would fail to start after some unknown electrical event. Even though the thermostat was calling for heat and the power to the furnace was on, the burner would not operate.

    Resetting the furnace by cycling the power off and then back on, solved the problem. The furnace would then operate as it should and cycle off by the thermostat, limits and everything else for days or even weeks before the glitch happened again, and you ended up with no heat until someone manually cycled the power.

    Since this was a problem that many furnaces encountered, and the engineers at Lennox Industries could not easily correct it, they came up with a Band-Aid-type fix. They added, at no cost to the consumer, a duty cycle that would break the thermostat circuit every hour if the thermostat had been calling for heat that long. It was called the Watchguard control WC-1

    Since most calls for heat were less than one hour, the consumer never actually knew it was happening because the duty cycle only started after one hour of continuous calling for heat. Although Lennox no longer offers that control, you can find it on sites like eBay that offer New Old Stock. Here is one you can get right now (August 2026): eBay Lennox Watchguard Control WC-1.

    Screenshot 2026-08-19 at 9.30.30 AM.png

    Since it was good enough to solve the Lennox ignition failure problem, I think you can use it to restart your AC whenever it fails. The only difference; I would add is a 5-minute time delay for the compressor contactor, since some air-conditioning units do run nonstop for several hours during extreme weather. You don’t want the short off-and-on interruption of the 24 volts to cause a compressor event as a result of this device.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • pecmsg
    pecmsg Member Posts: 7,450

    when this happens again you have to get in the attic and look for trouble codes and stop guessing

  • 109A_5
    109A_5 Member Posts: 4,346
    edited August 19

    @EdTheHeaterMan, as much as I considered a cyclic solution like your Lennox example, I did not like it so I came up with an inexpensive solution that only activates when actually needed.

    Since the control board could be the issue or the WetSwitch and the ICM493 now exists in the basement, I would simply (unless not practical) extent the thermostat circuit's R and C wires to the basement and add the timer circuit I illustrated above to briefly interrupt ICM493's contactor control. Easy, at least for me from here.

    I think @Jamie Hall missed a bit of the posts in the middle of the thread. @Jon_23 amusingly this thread is short compared to some. You seem correct, folks appear to be missing information.

    In a situation like this, my impatience and aggravation may overrule the my strong curiosity's need for data.

    I like evidence based troubleshooting.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Jamie Hall
    Jamie Hall Member Posts: 27,701
    edited August 19

    Did Lennox ever get to the root of that problem, @EdTheHeaterMan ? Be interesting to know.

    I must admit that the whole thing sounds to me like a timing error in the control logic, and I'd love to know what it is — and why.

    Detailed recording of the incoming power (preferably oscilloscope with event capture) will almost certainly find odd dropouts. These should not cause a problem to a well-designed circuit operating properly — even if it can be determined that a dropout to less than 98 RMS volts of exactly 3.1415 cycles duration or whatever is correlated with the failure. NOTE: correlated, not causal. While that would be lovely and interesting, it doesn't tell anyone what the problem is.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England