Options

Comments

  • mattmia2
    mattmia2 Member Posts: 17,666

    i didn't actually see any pictures if any of the failures in that. if the same people that can't make a flare are installing that, the problem isn't the tubing.

    GGrossSteve Minnich
  • ChrisJ
    ChrisJ Member Posts: 17,548

    I believe there were known issues with specific types of Uponor tubing, but I'm not positive.

    As of this time, I'll continue using Uponor white type A pex without fear. I've seen no problems with it for the 20 years I've been around it.

    From what I've heard about some locations and the water, copper will fail with pinholes while Pex will not.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    kcoppSteve Minnich
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,175
    edited June 26

    Hi, Nothing at all was mentioned about water quality. Chlorine and chloramines can cause damage to PEX. I've been installing the non-colored stuff since the early 90s with no problems.

    Yours, Larry

    ps. I have seen failures with kinks, sunlight and rodents. 🙈

    ChrisJ
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,634

    You can google it or you tube it. Many failures all over the country. Lots of lawsuits

    MaxMercy
  • jumper
    jumper Member Posts: 2,587

    Foolproof reliable methods of joining pipes & tubes are probably expensive if they exist.

    mattmia2
  • MaxMercy
    MaxMercy Member Posts: 615

    I've been following this a while - there seems to be two pockets of failed Uponor PEX, one around the greater Atlanta area and the other in California, and most of these are only a few years installed, but it covers maybe 10 years that I can see.

    Uponor never explained what happened, if they even know what happened, or if they fixed the problem assuming they know what went wrong, but it's bad enough where I stopped using it. It's the silence from Uponor that scares me.

    PEX B can often be expanded (look for the F1960 certification printed on the pipe) as can PE-RT. That's what I use for plastic when I'm not using copper.

  • Intplm.
    Intplm. Member Posts: 3,100

    There have been some isolated rumors, or dare I say reports of some pex leaks. Can't tell how big or small the issue is. However, it doesn't seem like another sixty-minute story from decades ago will be warranted.

    I'm wondering if the tubing was left out in the sun for a time before it was installed.

  • hot_rod
    hot_rod Member Posts: 27,962

    Seems there were some issues with the coloring process on some pex tubing.

    This repipe contractor has some You Tube videos explaining failures he has experienced with various brands.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • kcopp
    kcopp Member Posts: 4,710

    We live in a "sue first ask questions later" litigious society. Some lawyer out there will take on a case if there is money in it for them… They hope to settle out of court and make a payday.

    The Poly Butylene case come to mind.

    Less of an issue that it is rumored to be. Lots of disinformation.

    Larry WeingartenIntplm.Steve Minnich
  • Sal Santamaura
    Sal Santamaura Member Posts: 547

    This month marks exactly ten years since Joe Ludlow's Integrity Repipe crew completely replaced the leaking copper in my then-23-year-old home. They used Uponor PEX. So far, no PEX leaks have become apparent. Perhaps the fact that I've got a whole-house pressure regulator set to 45 PSI has minimized stress on those joint areas. I'm not going to open any walls to look for this problem. If the PEX lasts as long as the copper did carrying our alleged water, I'll be too old to worry about it. 😊

    ChrisJethicalpaulSteve Minnich
  • pedmec
    pedmec Member Posts: 1,473

    We are having trouble with some restaurants up in the state of New Hampshire. They ran the Pex-A underground to feed the bar and hand sinks at the bar and the are leaking just above the floor. We are assuming nothing is happening in the floor at this time.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,634
    edited July 15

    Spilling to much beer on the pex. Floor washing chemicals. etc

    ethicalpaul
  • ChrisJ
    ChrisJ Member Posts: 17,548

    Pex and polyethylene shouldn't have any issues with ethanol even 100%.

    Floor washing chemicals on the other hand……..

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • kcopp
    kcopp Member Posts: 4,710
  • pedmec
    pedmec Member Posts: 1,473

    @kcopp I'm not sure. All i have seen is pictures that my guys have sent. Every leak they have seen is above the floor and they just cut it back but there ain't much left to cut back. Next phase will be saw cutting the floor unless they find a different way to feed the bars.

  • mattmia2
    mattmia2 Member Posts: 17,666

    could it have to do with expansion and the stuff in the concrete can't move anywhere but it can once it is out of the concrete?

  • Steve Minnich
    Steve Minnich Member Posts: 2,928

    I did my first in-slab radiant floor in 1982 using Pex A or B. I don't remember which. I was a first year apprentice helping on the job. Going back all those years using various brands and types of pex tubing, I have never experienced a failure. I've had my favorites throughout the years and always kept using what I considered the winners. Rehau, Wirsbo which then became Uponor, Weil McLain's AlumiPex, Watts Radiant Pex-Al, among a few others. WM's AlumiPex is long gone, but I've used miles of the other three. It wouldn't be fair to mention my favorite.

    Steve Minnich
    ethicalpaul
  • hot_rod
    hot_rod Member Posts: 27,962

    I think the most current failure issues were a specific brand of potable water pex in the blue or red color, only. Sounds like failures start 4- 5 years after the installation.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • MaxMercy
    MaxMercy Member Posts: 615

    I've seen the same type of failures in the white Uponor pipe as well. I think the colored pipe got the bad press because it's simply installed far more than the white pipe is. The red gets the worse press of all because whatever it is that aggravates Uponor pipe to premature death, heat just adds to it, and if the red pipe is also used in recirculation setups, it's now seeing another factor (total water moving through pipe) that will cause premature wear and tear. When the red pipe starts failing in year 6 (for instance), you can expect the blue to fail in year 10.

    ethicalpaul
  • hot_rod
    hot_rod Member Posts: 27,962

    There was some concern as to how the various manufacturers were getting the "5" code on their tube.

    Rehau played it safe with a "3" listing.

    It seems it takes a few years of that high chlorine, high temperature (140F) recirculation for failures to show up.

    I don't know if that test standard ASTM F2023 is for extended periods? Is it an actual extend duration test or just some number crunching?

    From Viegas website:

    Screenshot 2026-07-18 at 9.00.18 AM.png Screenshot 2026-07-18 at 9.01.17 AM.png Screenshot 2026-07-18 at 9.02.04 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • ChrisJ
    ChrisJ Member Posts: 17,548

    I've never seen red or blue installed only white because guys buy the 1000' spool and install it for everything.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • hot_rod
    hot_rod Member Posts: 27,962

    I think red/ blue is more of a convience factor, and to help prevent cross connections for the unskilled, or lazy installer.

    I see tract home plumbers around here with two uncoilers on the job.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • ChrisJ
    ChrisJ Member Posts: 17,548

    I'm sure.

    My point was I feel the white gets installed far more.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,634

    Plumber that use a lot of pex probably buy the colors because they know they will use the whole coil. Small users may buy 1 white coil.

  • hot_rod
    hot_rod Member Posts: 27,962

    The white is probably a color that is added to the tube like red or blue. I wonder why the red and blue are the colors that are the most common failures.

    If it was the color adding process that is causing the failure? According to the lawsuits.

    IMG_2770.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • ethicalpaul
    ethicalpaul Member Posts: 8,944

    Now I don't know how accurate the author of this sentence was, but your highlighting missed the beginning of the sentence which indicated that of the colored pex failures, it is the Uponor red and blue that are most commonly linked. Whether it's correct or not I don't know, but the sentence isn't saying that most pipe failures are colored pipe.

    image.png

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • MaxMercy
    MaxMercy Member Posts: 615

    Could be a regional thing. Most installations I've seen around here are the red/blue. Personally, I never used the color pipes because to me, it looks cheap and unprofessional. One can argue that any plastic is cheap and unprofessional, but that's a different discussion.

    In any case, the expansion rings are made of the same material as the pipe itself, these are not colored red or blue, and they show the same yellowing and cracking as the colored pipe.

    image.png image.png