Hi I just had my 1906 asbestos caked boiler and pipes removed from my basement. Old gravity hot water 2 pipes to each radiator system. I will be installing a new high-efficiancy boiler with pumps and two zones. As part of the prep, I need to get these pipe ends able to accept the new PEX. For those who have done this before, would it be easier for me to try and remove, I.E. unthread the bit of pipe they left, or to cut new threads on the stub outs? I tried one with a maybe 18" pipe wrench I have and it didn't budge. I have not tried heat or a bigger wrench yet. Harbor Frieght has a pipe threading kit for about $75. Here are some photos, and some photos of the boiler that was removed. I have about 16 pipes I need to address. 1-1/4" I think.
Comments
-
-
Didn't think of that!
0 -
You could rent a Megapress tool and use this fitting.
https://www.supplyhouse.com/Viega-25145-1-1-4-Viega-MegaPress-Adapter-Press-x-Female
Either way, I'd cut back further and remove those unions.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
Never seen those. Interesting. Pricey little devils. I might try heat and brute force first. Some radiators are on the floor above, so I could always cut the pipes off there, open the union, and thread a new piece of 1-1/4 down the hole, add a new elbow and reducer to the PEX size.
0 -
That old boiler was probably 40% efficient……………
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Probably, but in 25 years I did absolutely zero repairs on it. Heated the home smoothly, evenly and comfortably. Problem is if I ever go to sell the house that thing would get red tagged so fast. All the asbestos would be a no-go too. I just hope the new one doesn't become a maintenance nightmare, with all the moving parts. Amazing on the old system the only moving part was the gas valve opening and closing.
0 -
unscrew back to the ells, get rid of the union two hammers, one for backing and tap around the fittings to help loosen them
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Were your radiators used as a closed expansion tank system by leaving an air charge in each radiator creating the point of no pressure change or do you have an open to air expansion tank in the attic?
You could use an EFMDF520 stoker boiler with a gas burner with its large steam chest and tapping and leave your existing system intact. It would save you a lot of work and money giving you a boiler that would work just like your snowman conversion boiler.
The EFM DF520 coal stoker boiler is certified and pressure tested for steam heat as a standard certification. You would not have to use the coal stoker if you have no desire to do so.
1 -
I had an expansion tank in the ceiling near the boiler. No air in the radiators. Now that the boiler and pipes are out I need to run new PEX lines to the radiators. I'm not changing out the old cast iron radiators.
0 -
Did exactly this a while back on a 100 year old system. Pipe wrench with a 6' cheater bar got them out. Did bend the pipe wrench a bit on one of the pipes.
Remove the elbow and install adapter for there. Does feel wrong to connect a 5/8 pipe to a 1" riser but works great. The new piping completely eiminated the cold rad at the end of the run issue the house originally had.
That steel piping was keeping your rads from tipping over originally. Depending on how much pipe you have left in the wall, you will most likely have to anchor the rads to the wall. Threaded rod with ceiling flange hanger plates between the rad columns works well.
0 -
Good point about them tipping over. They are taller radiators.
0 -
Cut a "tooth" out of the piece and pound it out with a Lump hammer....Don your safety goggles. Mad Dog
1 -
I'm seriously considering that Megapress system. I tried one of the fittings with some penetrating oil overnight, then Mapp gas heat today with a 36" pipe wrench. Nothing. Not a bit of movement. I have a total of 14 fittings, all stuck up high in the corner and in hard to reach places. They were cut at all sorts of angles, so I would have to recut them nice and square, which is not a big deal. May be worth the money on those Megapress fittings ($35 each) just to get it done. Alternative is all kinds of grunt work, some I would have to cut at the radiators, etc. All sorts of messing around.
0 -
The less yanking you do on that old piping the better!
Many plumbing suppliers rent or loan the press tool if you buy fittings from them.
Get some coarse open mesh sand cloth and get the outside of the pipe as smooth as possible for the press fitting.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
For the first floor I would go all the way to the rad. Put new drops in with copper or black and connect the pex to it. It will take less time.
Second floor it's unlikely you have no elbows between the ff ceiling and the second floor so snaking the pex through the existing pipe is probably not happening. In that case thread, mega press or unthread back to a fitting
0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 128 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements