How can I use 90 F degree water to heat my new house?
I have a well-insulated 2,000 square foot house on a ranch in northern Nevada that has a hot spring nearby. I can deliver as much 90 degree water to the house as needed. I've thought about using the water as input to a ground source heat pump, but was told a heat pump couldn't take water that warm. I could also use the water for hydronic floor heating, but was told it wasn't warm enough. I've been trying to find someone that I could pay to help me design something that might work, but can't find anyone so far. What about running the warm water through a hydronic floor system to provide most of the heat and having a boiler as a backup? The ranch is 4 - 5 hours from big cities like Reno or Salt Lake, so its hard to find someone to take on the project. I'm also concerned that if it breaks down, it will be hard to find someone to come out. Any suggestions would be appreciated.
Thanks,
Doug Frazer
Sadler Ranch, Eureka, NV
Comments
-
At best you can get 10 Btu/sq/ft from 90F water if that. What's the heat loss?
0 -
It looks to me on casual research that they can handle 90 degrees. Some can go to 120 it appears.
Even if they couldn't, I would consider some kind of bypass loop that recirculated some of the water exiting the heat pump back into the supply in order to moderate/cool the incoming temperature. That nice warm water is too valuable to ignore IMO
NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
in four radiant heat
and a small heat pump to make up the very little difference
0 -
How well insulated is well insulated?
The only type of system which offers any hope is radiant floors or ceilings — or more likely, both. You need to have a very clear idea as to how much heat is required to heat your house, and that means doing a careful and thorough heat loss calculation. Then you can begin to wonder if you can meet that heating load with water at that temperature — and, not irrelevant, if you have enough water available. You may find that you need essentially all of the floor and ceiling surface to be heated. You may also find that you will need 20 plus gpm of flow, 24/7 , to maintain the temperature — 30,000 gallons per day. Do you have rights to that much water?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
The first thing you need to know is the heatload of the home, ideally room by room
This graph shows some common retrofit options and expected btu/ ft output. Radiant walls are about the high output, and you have a lot if surface area availade
Running that water through a plate HX you would only loose a few degrees, do call it 88 degree supply water
A hp adds a lot of cost to boost maybe 10-15 degrees
The biggest issue is that Nevada geo thermal water is very hard, so continual descaling of the hx may be needed
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If you were to use the hot spring with a heat pump you have to understand that if you have an oil leak or refrigerant leak it will contaminate the hot spring.
What you need in order to make use of the heat from the hot spring is to use an insulated buffer tank to store hot water and also deliver it to the home using multiple copper coils in the large storage tank,
Using 2 small circulators where one can feed the hot water from the spring to the tank and the other feeding the hot water from the copper coils to cast iron or steel tube radiators with the cooler water allowed to drain back to the hot spring.
The thermal mass built into the cast iron or steel tube radiators along with the thermal mass in the water from the hot spring can be used to its fullest advantage.
1 -
Is this a flowing well or coming down from an elevation?
How would you get rid of that much water?
0 -
I visited the Peppermill in Reno a few years back and got a tour of their geothermal system which heats and provides DHW for the entire resort, 2.1 million feet of space. They pump and dump.
One pump pulling 176° F from the well, another discharge to help pump back down a well across the property.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
So… we have two critical paperwork steps here. First, does this property have the necessary rights to use enough water? For those unfamiliar with Western water law — like anyone east of the Mississippi! — it is well to remember that just because there is water on a property — or beneath it — does NOT mean that the property owner has the right to use it! Water rights (and mineral rights for that matter) do NOT run with the land.
Then second, how much heat does this place need? Can water at that temperature (85 F mean temp) provide that much heat with a reasonable surface area?
Answer those two, then we can begin think about practicalities…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Put a boiler in with baseboard heat as a booster a stand alone system.
use the 90 degree water through a heat exchanger to run radiant heat and preheat your domestic hot water.
You can go oversize on the radiant tubing to maximize use of the 90 degree water which will probably do the job for a good portion of the winter.
What the radiant can't do the boiler will
.Nice and simple and not overloaded with controls.
1 -
so the house is already built and you want to maybe add a hydronic system?
I’m in the Salt Lake area and to get a building permit you need to have a heating and cooling load calculation. Maybe that was the case in your area?
Without that load calculation, it is just a guesstimate as to what could work.
There are a lot of good hydronic companies around Nevada. They tend to be near the resort areas, but quite a few in the Reno area.
Western Nevada Supply in Reno has an excellent hydronics division. I know hydronic reps in that area that may have contractor options. What town are you in?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks for the ideas.
We have more than enough hot spring water to feed a system. Our hot spring normally just flows out to our meadows. I'm just diverting a part of the flow to the house and back to the fields.
Its and old house stipped to the studs. I live in a county with no building permitting requirements.
I like the idea of radiant tubing with the 90 degree water with a backup boiler for very cold times. I need to do heat loss calculations for the house and the radiant tubing to see how it adds up.
Scaling in the heat exchanger is likely to be a problem given the high mineral content of the water.
Thanks also for the suggestion for Western Nevada Supply in Sparks.
0 -
That water diversion may — or may not — be permitted. Don't assume. ASK. People have been shot for less — and I'm not joking.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 125 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 169 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements