Weil-McLain EG-50 (repipe job)
HO called me, I did an EDR first and came up with 280 EDR load against the boilers output of 454 EDR, so I recommend a two stage gas valve and a repipe because the piping wasn’t great. We did it in stages with the gas valve last winter and now the repiping. Boiler manual calls for 1) 2-1/2 riser into a 2-1/2 header, however this as far as I’m concerned is waaay too small so in goes 2) 3” risers about 40” above the water line into a 3” header with a 2” equalizer.
Also during a recent kitchen renovation someone installed a radiator or should I say repiped and moved a radiator, anyway they pitched the pipe towards the radiator so you know how well it drains condensate. I’m going pull the pipe down which will put the pipe below the main, so to remedy this it will be dripped into its own return.
To get the old plug out of the boiler I cut it in half with a sawzall then made two vertical cuts, then a chisel and hammer and caped it right out easily.
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
I prefabbed the header in my garage, takes the bulk of the work away on the job.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
All finished and working beautifully.....
Is this a two-pipe system? If so, where did you vent the condensate return side to atmosphere?0
Single pipe steam Zack.zackwatt said:Is this a two-pipe system? If so, where did you vent the condensate return side to atmosphere?
I noticed your Hartford loop looks different than a traditional one with a close nipple. Is there any benefit to doing it your way, perhaps less chance for water hammer your way? I ask because I have to pipe an EG 50 and am gathering info. Thanks
@Ldallas_87 It's the preferred way but the wye is not all ways available.
just follow the diagram in the manual and you can’t go wrong
Around here most steam installers have decided that two-inch riser and header is all you ever need to feed a house steam heating system. Does not matter if the EDR is 300 or 900. By the way, two inch pipe and fittings cost about half of what three inch cost. Oh, and many contractors do not own threading equipment that will do anything larger than two inch.
2 -
I see someone's revived one of Dave's old posts from 2018. Dave was a great installer who moved on from the industry. I hope he's well.