115 volt air handler needed
does anyone know of a manufacturer that makes a three ton, 115 volt air handler?
Ducted, straight cooling.
thanks to all
    pecmsg Member Posts: 7,194
    Straight air, Change the fan motor
    hot_rod Member Posts: 27,709
    B&D, 1-5 ton unit made Iowa, perhaps
  • Ironman
    Ironman Member Posts: 7,918
    Trane makes a modular blower that’s 115v designed to replace a gas furnace. You’d have to add the evaporator coil with it.
    Bob Boan
    zepfanHydronicMike
    HVACNUT Member Posts: 7,508
    Rheem offers the RH1PY in 115 vac with a PSC blower motor and the RH2TY in 115 vac with a constant torque blower motor. Up to 16 SEER. R454B.
    EBEBRATT-Ed Member Posts: 20,397
    If you have 120 volt you can get 240 off the same cable if you put in a two-pole breaker.
    If it is on its own circuit as it should be.
  • SuperTech
    SuperTech Member Posts: 2,669
    First Co air handlers are all 115 volt.
    zepfan
  • zepfan
    zepfan Member Posts: 464
    Thanks to all that responded. I decided to just go with a 240 volt air handler as I think it would be easier to change the breaker and run a dedicated ground to from the panel, that if they did not run 12/2 mc cable and a ground is needed. Just as EBEBRATT-Ed mentioned. Yes I hope it is a dedicated circuit, the existing air handler has been there since the building was built so it should have it's own circuit
    EdTheHeaterMan Member Posts: 12,448
    Well, you will find out when you power the 12-2 MC with 240 V if some handyman tapped an outlet for your expensive entertainment center off that circuit.   Is there a condensate pump on an outlet near the AHU?  That is something I would check and add a fused disconnect with the rewire from that dedicated circuit to the grounded neutral you are adding.   I'm not sure if that is up to code but you need a separate fuse or breaker for that outlet that will trip if the 120V. Item plugged into that outlet has an over current event.
    mattmia2 Member Posts: 17,218
    i'd be way more concerned about motors or appliances on that circuit. most consumer electronics have had power supplies that will work on 90v-250v for about 30 years.
    I don’t know of many appliances that work well on that range of voltages!
    Whatever they ran for a cable is more likely to have a ground than not. Romex, BX and MC all have a ground. At least they have since air conditioning became popular,
    mattmia2HVACNUTIronman
    Jamie Hall Member Posts: 27,519
    If you do run 12/2 with ground converted to 240 VAC, don't forget to mark the white wire with red tape to indicate that it is hot!