115 volt air handler needed
does anyone know of a manufacturer that makes a three ton, 115 volt air handler?
Ducted, straight cooling.
thanks to all
    pecmsg Posts: 7,634
    Straight air, Change the fan motor
    hot_rod Posts: 28,704
    B&D, 1-5 ton unit made Iowa, perhaps
  • Ironman
    Ironman Posts: 7,975
    Trane makes a modular blower that’s 115v designed to replace a gas furnace. You’d have to add the evaporator coil with it.
    Bob Boan
    zepfanHydronicMike
    HVACNUT Posts: 7,784
    Rheem offers the RH1PY in 115 vac with a PSC blower motor and the RH2TY in 115 vac with a constant torque blower motor. Up to 16 SEER. R454B.
    If you have 120 volt you can get 240 off the same cable if you put in a two-pole breaker.
    If it is on its own circuit as it should be.
  • SuperTech
    SuperTech Posts: 2,710
    First Co air handlers are all 115 volt.
    zepfan
  • zepfan
    zepfan Posts: 494
    Thanks to all that responded. I decided to just go with a 240 volt air handler as I think it would be easier to change the breaker and run a dedicated ground to from the panel, that if they did not run 12/2 mc cable and a ground is needed. Just as EBEBRATT-Ed mentioned. Yes I hope it is a dedicated circuit, the existing air handler has been there since the building was built so it should have it's own circuit
    EdTheHeaterMan Posts: 12,947
    Well, you will find out when you power the 12-2 MC with 240 V if some handyman tapped an outlet for your expensive entertainment center off that circuit.   Is there a condensate pump on an outlet near the AHU?  That is something I would check and add a fused disconnect with the rewire from that dedicated circuit to the grounded neutral you are adding.   I'm not sure if that is up to code but you need a separate fuse or breaker for that outlet that will trip if the 120V. Item plugged into that outlet has an over current event.
    i'd be way more concerned about motors or appliances on that circuit. most consumer electronics have had power supplies that will work on 90v-250v for about 30 years.
    pecmsg Posts: 7,634
    I don’t know of many appliances that work well on that range of voltages!
    Whatever they ran for a cable is more likely to have a ground than not. Romex, BX and MC all have a ground. At least they have since air conditioning became popular,
    mattmia2HVACNUTIronman
    If you do run 12/2 with ground converted to 240 VAC, don't forget to mark the white wire with red tape to indicate that it is hot!