Radiators may need flushing..or?
Comments
-
does the thermostat control a separate cooling system or is it just controlling the boiler?
if it is just the boiler either is ok, all selecting 2 will do is lock out the cooling controls.
0 -
Just the boiler. and yes, I had a feeling either setting was OK. thanks
boiler has basic SNF done every season by me and had the burner replaced a few seasons ago.
don't know how to check to see if it's underfired. will need to read a bit..
0 -
A few pics. Pressure setting was when Steamhead was here 15 yrs. ago.
0 -
you need a good oil burner tech to service it.
who tuned the burner when it was replaced?
it could be underfired because it is out of adjustment and not burning completely or because the the boiler is sooted and not moving the heat in to the water or because parts that are worn or out of adjustment aren't causing it to atomize enough oil.
0 -
I'd use 2.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steamhead: Thanks
mattmia2: my local boiler guy tuned it after he replaced the burner
"it could be underfired because it is out of adjustment and not burning completely or because the the boiler is sooted and not moving the heat in to the water or because parts that are worn or out of adjustment aren't causing it to atomize enough oil."
Understood.
0 -
Forgot to ask: why is less (3) cph more helpful than 5 cph? seems counterintuitive
0 -
You are trying to strike a balance between how long it takes the radiation to heat up and cool off feeling the temperature variation in the space.
Steam systems take a while to warm up once the thermostat calls for them — five to ten minutes isn't unusual for the radiators to start to give off heat — but they also take a while for the radiators to stop heating after the thermostat is satisfied. This give you the wonderful even heat of steam as against the on again off again of forced air. But it also means that the boiler doesn't have to fire as often — hence fewer cycles per hour will give more comfortable and efficient results (any heating system is more efficient when it is running steadily instead of constantly turning on and off).
On systems controlled by cycles per hour — which is most modern digital thermostats — somewhere between 1 and 3 cycles per hour seems to work best.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
was the thermostat changed between when it was working well and now? it is possible the firmware somehow factory reset but if it is the same stat it is more likely something else changed.
0 -
Thermal mass. Think of cooking in a skillet: if your skillet is stamped steel it heats up quickly but cools off quickly when you turn the burner off. But it it's cast-iron, it takes a bit to heat up, but retains its heat longer after you turn off the burner. Cast-iron has more thermal mass than steel.
Your steam system is largely cast-iron, whereas scorched-air is mostly steel.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Great and understandable answers, thanks guys.
T-stat is the same.
And I just checked my burner pressure and it's still where Frank and Gordo set it all those years ago, 140. I'll be de-sooting in May.
0 -
How the heck did it ever work properly set at 5 cycles per hour? Anybody? Is it possible it got reset to factory default at some point and you were not aware of it?
0 -
Possibly when I needed to change batteries?
0 -
Honeywell should have their act together. That would be a very annoying feature for all of your configuration settings to revert to factory defaults in the event of power loss. I know my White Rodgers does not do that.
0 -
cycles per hour isn’t actually cycles per hour I think.
It’s just a different way to say “swing”
No thermostat is going to do more cycles if the temperature is above the setpoint.
And no thermostat is going to delay turning on the boiler if it’s below the setpoint.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
sometimes things happen that cause the firmware to factory reset like esd or an overvoltage from a nearby lightning strike or the power getting interrupted just the right way to corrupt the eeprom or someone accidentally holding the right set of buttons to trigger the reset trap.
0 -
"Honeywell should have their act together. That would be a very annoying feature for all of your configuration settings to revert to factory defaults in the event of power loss. I know my White Rodgers does not do that"
Please….as I said, possibly, not probably
"sometimes things happen that cause the firmware to factory reset like esd or an overvoltage from a nearby lightning strike or the power getting interrupted just the right way to corrupt the eeprom or someone accidentally holding the right set of buttons to trigger the reset trap."
This is actually quite plausible. I am out of power with annoying regularity. Isolated mountain top location..My 20KW Generac standby logs over 100 hours of use each year. In fact it will be getting a top end rebuild this month. We are also subject to the occasional power surge. Had one last week in that tripped 3 breakers and blew a few lightbulbs..
0 -
Yeah, no, I was just musing or thinking out loud that it is probably not the case. Sorry I shared it.
Is your thermostat getting power from the 24VAC transformer? If it is only battery powered then it wouldn't be affected by power surges. Sorry if that is also obvious. Just thinking out loud again.
1 -
"Is your thermostat getting power from the 24VAC transformer? If it is only battery powered then it wouldn't be affected by power surges. Sorry if that is also obvious. Just thinking out loud again".
And now I am laughing at how ridiculous I am! Of course it would not be affected by a surge! Ah, the joys of aging…
0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 119 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements