Yellow spot after soot up
I had a no heat call tonight that turned out to be a soot up. Buderus G115WS/3 with a Riello. It had been cleaned by someone last month and now was caked with Nice (if soot can be nice) soft soot.
After cleaning I checked pump pressure which was at 150 and I adjusted it to 185(spec) it had a 75-60A which I replaced with a 55-60A. I also set the air band and head position to spec for starters.
MFR | Buderus |
|---|---|
model | G115WS/3 |
Burner | Riello |
nozzle | 55-60A |
Pump Pres | 185 |
Head, static plate | 1 |
Firing Rate | = 0.75 |
Draft Breach | |
Draft OF | 0.03 |
Tstack | 612 |
O2 | 5.2 |
CO | 99 |
CO AF | = 132 |
EFF | 79 |
ExAir | 31 |
CO2 | 11.8 |
AT | 53 |
Net Stack | 559 |
Comment | yellow spot |
I had to push the head forward to "1" to get the CO to drop (spec is 2)
The CO readings are dropping, and are Post Soot up so I feel they will continue to drop.
I pulled yellow spot on every smoke test I did, that and the High net stack temps tells me high excess air yet, Excess air is a little low for what I usually end up with at a final reading. O2 and CO2 are reasonable.
The head is clean and when I had the door open I pulled the gun and really cleaned the tube and especially the venturi area with a brush and rag. So I don't think there is an impingement issue.
I don't get yellow on the smoke test very often and the few times I have it was confirmed with high excess air. but not the case here.
Ill be back to check Combustion and smoke on Tuesday.
Educate me! Happy Saint Patrick's Day
Comments
-
-
Is the OF draft .03 negative? Should be slightly positive. What was it at the breech?
High stack could also be from high draft.When you go back I’d put the head position back to where it was and recheck combustion.
Also CO numbers at light off, at steady state-rising, falling, stable, and at shut down.1 -
I asked that question here about 30 years ago.
I think the answer is still the same:
TOO MUCH AIR. Your flame is too lean. the residual soot that was not vacuumed out completely is making you have a #2 or higher smoke test from an otherwise clean flame. After a week, go back and reduce the air mixture. (probably from the #2 setting back to #1 setting) and see if you get a zero smoke with no yellow spot. That yellow spot is unburned oil vapor that is getting blown out by the excess air
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
-
that draft reading is positive that's why I didn't put a minus sign in front of it.
Also, correction I moved the head to position 3 not position one.
0 -
-
The A or hollow nozzle was designed for the Shell head burner used in 60's and 70's. The flame pattern of the hollow is fragile . Carbon buld up on the flame cone and cracked female porcelains was a normal issue with Shellheads . The standard for fuel oil has changed since then and not for the better Using a W or semi solid is a safer bet .. Just a tip
Good Luck
There was an error rendering this rich post.
3 -
The Riello OEM Spec guide is a bit confused, it shows either an A or B nozzle for that boiler:
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
I saw that. Otherwise it matches the burner label
0 -
0
-
Thank you!
So do you not use "A" nozzles at all?
I noticed that the Riello OEM quide dose spec "W" nozzles in some applications
0 -
I use hollow nozzles where appropriate.
That OEM spec might be talking about a Danfoss AB nozzle, which is roughly equivalent to a Delavan W.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
It definatly says "A/B" In my mind that means A or B but Im not inside the Tech Writers head :D
0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 431 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements