Yellow spot after soot up
I had a no heat call tonight that turned out to be a soot up. Buderus G115WS/3 with a Riello. It had been cleaned by someone last month and now was caked with Nice (if soot can be nice) soft soot.
After cleaning I checked pump pressure which was at 150 and I adjusted it to 185(spec) it had a 75-60A which I replaced with a 55-60A. I also set the air band and head position to spec for starters.
MFR | Buderus |
model | G115WS/3 |
Burner | Riello |
nozzle | 55-60A |
Pump Pres | 185 |
Head, static plate | 1 |
Firing Rate | = 0.75 |
Draft Breach | |
Draft OF | 0.03 |
Tstack | 612 |
O2 | 5.2 |
CO | 99 |
CO AF | = 132 |
EFF | 79 |
ExAir | 31 |
CO2 | 11.8 |
AT | 53 |
Net Stack | 559 |
Comment | yellow spot |
I had to push the head forward to "1" to get the CO to drop (spec is 2)
The CO readings are dropping, and are Post Soot up so I feel they will continue to drop.
I pulled yellow spot on every smoke test I did, that and the High net stack temps tells me high excess air yet, Excess air is a little low for what I usually end up with at a final reading. O2 and CO2 are reasonable.
The head is clean and when I had the door open I pulled the gun and really cleaned the tube and especially the venturi area with a brush and rag. So I don't think there is an impingement issue.
I don't get yellow on the smoke test very often and the few times I have it was confirmed with high excess air. but not the case here.
Ill be back to check Combustion and smoke on Tuesday.
Educate me! Happy Saint Patrick's Day
Is the OF draft .03 negative? Should be slightly positive. What was it at the breech?
High stack could also be from high draft.When you go back I’d put the head position back to where it was and recheck combustion.
Also CO numbers at light off, at steady state-rising, falling, stable, and at shut down.1 -
I asked that question here about 30 years ago.
I think the answer is still the same:
TOO MUCH AIR. Your flame is too lean. the residual soot that was not vacuumed out completely is making you have a #2 or higher smoke test from an otherwise clean flame. After a week, go back and reduce the air mixture. (probably from the #2 setting back to #1 setting) and see if you get a zero smoke with no yellow spot. That yellow spot is unburned oil vapor that is getting blown out by the excess air
2 -
that draft reading is positive that's why I didn't put a minus sign in front of it.
Also, correction I moved the head to position 3 not position one.
The A or hollow nozzle was designed for the Shell head burner used in 60's and 70's. The flame pattern of the hollow is fragile . Carbon buld up on the flame cone and cracked female porcelains was a normal issue with Shellheads . The standard for fuel oil has changed since then and not for the better Using a W or semi solid is a safer bet .. Just a tip
Good Luck
3 -
The Riello OEM Spec guide is a bit confused, it shows either an A or B nozzle for that boiler:
I saw that. Otherwise it matches the burner label
Thank you!
So do you not use "A" nozzles at all?
I noticed that the Riello OEM quide dose spec "W" nozzles in some applications
I use hollow nozzles where appropriate.
That OEM spec might be talking about a Danfoss AB nozzle, which is roughly equivalent to a Delavan W.
Returned today to re-setup the burner. To start I pulled smoke and checked combustion the numbers were nearly identical and I was pleased to see that CO an CO/AF had improved. Also the yellow spot was clear which I didn't expect.
I set the head back to position "2" and decreased air, getting a 1 smoke and back to a trace. Then adjusted the draft for .03 OF and readjusted to a trace, added air to get -1.5ish CO2 and check for a zero smoke.
@SuperTech my final CO2 came in as you commented
measurement description is at bottom of table
Date
3/8/26
3/10/26
3/10/26
3/10/26
3/10/26
Time
20:54
10:11
10:25
10:29
11:00
MFR
Buderus
Buderus
Buderus
Buderus
Buderus
model
G115WS/3
G115WS/3
G115WS/3
G115WS/3
G115WS/3
Burner
Riello
Riello
Riello
Riello
Riello
nozzle
55-60A
55-60A
55-60A
55-60A
55-60A
Pump Pres
185
185
185
185
185
Head/static plate
3
3
2
2
2
Firing Rate
= 0.75
= 0.75
= 0.75
= 0.75
= 0.75
Draft Breach
-0.04
Draft OF
0.03
0.03
Tstack
612
550
510
521
567
O2
5.2
5.2
1.6
2.3
4.2
CO
99
37
60
60
40
CO AF
= 132
= 49
= 65
= 67
= 50
EFF
79
81
84
83
81
ExAir
31
31
7.7
11.5
23.4
CO2
11.8
11.8
14.5
13.98
12.55
AT
53
53
53
53
53
Net Stack
559
497
457
468
514
Comment
yellow spot
Pre test
1 smoke
trace
trace -1.43
@HydronicMike Once the other readings were steady CO was flat as well.
CO during burner start
CO during burner shuts down
I truly appreciate everyone's help and will appreciate any further comments
yeah, I was surprised that it cleared up that much in two days. You learn something every day if work at it.
- 87.8K THE MAIN WALL
- 129 Chimneys & Flues
- 123 Geothermal
- 79 Pipe Deterioration
- 396 Solar
