Yellow spot after soot up
Robert_H
Robert_H Posts: 369
I had a no heat call tonight that turned out to be a soot up. Buderus G115WS/3 with a Riello. It had been cleaned by someone last month and now was caked with Nice (if soot can be nice) soft soot.
After cleaning I checked pump pressure which was at 150 and I adjusted it to 185(spec) it had a 75-60A which I replaced with a 55-60A. I also set the air band and head position to spec for starters.
MFR
Buderus
model
G115WS/3
Burner
Riello
nozzle
55-60A
Pump Pres
185
Head, static plate
1
Firing Rate
= 0.75
Draft Breach
Draft OF
0.03
Tstack
612
O2
5.2
CO
99
CO AF
= 132
EFF
79
ExAir
31
CO2
11.8
AT
53
Net Stack
559
Comment
yellow spot
I had to push the head forward to "1" to get the CO to drop (spec is 2)
The CO readings are dropping, and are Post Soot up so I feel they will continue to drop.
I pulled yellow spot on every smoke test I did, that and the High net stack temps tells me high excess air yet, Excess air is a little low for what I usually end up with at a final reading. O2 and CO2 are reasonable.
The head is clean and when I had the door open I pulled the gun and really cleaned the tube and especially the venturi area with a brush and rag. So I don't think there is an impingement issue.
I don't get yellow on the smoke test very often and the few times I have it was confirmed with high excess air. but not the case here.
Ill be back to check Combustion and smoke on Tuesday.
Educate me! Happy Saint Patrick's Day
    EBEBRATT-Ed Posts: 21,026
    Probably some residual soot could be messing with the readings. It may calm down when you go back
    Big Ed_4Robert_H
  • HydronicMike
    HydronicMike Posts: 439
    Is the OF draft .03 negative? Should be slightly positive. What was it at the breech?
    High stack could also be from high draft.
    When you go back I’d put the head position back to where it was and recheck combustion.
    Also CO numbers at light off, at steady state-rising, falling, stable, and at shut down.
    Robert_H
    EdTheHeaterMan Posts: 12,747
    I asked that question here about 30 years ago.
    I think the answer is still the same:
    TOO MUCH AIR. Your flame is too lean. the residual soot that was not vacuumed out completely is making you have a #2 or higher smoke test from an otherwise clean flame. After a week, go back and reduce the air mixture. (probably from the #2 setting back to #1 setting) and see if you get a zero smoke with no yellow spot. That yellow spot is unburned oil vapor that is getting blown out by the excess air
    mattmia2Robert_H
  • SuperTech
    SuperTech Posts: 2,669
    I agree that it is yellow from too much air. On that particular boiler with a Riello burner I am usually able to obtain a true zero smoke in the range of 12.5-13.5% CO2. Make sure to set the draft so it's slightly positive over fire, +.01-.03".
    Robert_H
  • Robert_H
    Robert_H Posts: 369
    that draft reading is positive that's why I didn't put a minus sign in front of it.
    Also, correction I moved the head to position 3 not position one.
  • Robert_H
    Robert_H Posts: 369
    I read the post last night when I got home and have it bookmarked!
    "That yellow spot is unburned oil vapor that is getting blown out by the excess air" that is a perfect explanation.
  • Big Ed_4
    Big Ed_4 Posts: 3,583
    The A or hollow nozzle was designed for the Shell head burner used in 60's and 70's. The flame pattern of the hollow is fragile . Carbon buld up on the flame cone and cracked female porcelains was a normal issue with Shellheads . The standard for fuel oil has changed since then and not for the better Using a W or semi solid is a safer bet .. Just a tip
    Good Luck
    MaxMercyRobert_Hrick in Alaska
    Steamhead Posts: 18,891
    The Riello OEM Spec guide is a bit confused, it shows either an A or B nozzle for that boiler:
    https://www.riello.com/north-america/service/technical-support/oem-settings
    Semi-retired
    Robert_H
  • Robert_H
    Robert_H Posts: 369
    I saw that. Otherwise it matches the burner label
  • Robert_H
    Robert_H Posts: 369
    Thank you!
    So do you not use "A" nozzles at all?
    I noticed that the Riello OEM quide dose spec "W" nozzles in some applications
    I use hollow nozzles where appropriate.
    That OEM spec might be talking about a Danfoss AB nozzle, which is roughly equivalent to a Delavan W.
    Semi-retired
  • Robert_H
    Robert_H Posts: 369
    edited March 9
    It definatly says "A/B" In my mind that means A or B but Im not inside the Tech Writers head :D
    MaxMercy
  • Robert_H
    Robert_H Posts: 369
    edited March 10
    Returned today to re-setup the burner. To start I pulled smoke and checked combustion the numbers were nearly identical and I was pleased to see that CO an CO/AF had improved. Also the yellow spot was clear which I didn't expect.
    I set the head back to position "2" and decreased air, getting a 1 smoke and back to a trace. Then adjusted the draft for .03 OF and readjusted to a trace, added air to get -1.5ish CO2 and check for a zero smoke.
    @SuperTech my final CO2 came in as you commented
    measurement description is at bottom of table
    Date
    3/8/26
    3/10/26
    3/10/26
    3/10/26
    3/10/26
    Time
    20:54
    10:11
    10:25
    10:29
    11:00
    MFR
    Buderus
    Buderus
    Buderus
    Buderus
    Buderus
    model
    G115WS/3
    G115WS/3
    G115WS/3
    G115WS/3
    G115WS/3
    Burner
    Riello
    Riello
    Riello
    Riello
    Riello
    nozzle
    55-60A
    55-60A
    55-60A
    55-60A
    55-60A
    Pump Pres
    185
    185
    185
    185
    185
    Head/static plate
    3
    3
    2
    2
    2
    Firing Rate
    = 0.75
    = 0.75
    = 0.75
    = 0.75
    = 0.75
    Draft Breach
    -0.04
    Draft OF
    0.03
    0.03
    Tstack
    612
    550
    510
    521
    567
    O2
    5.2
    5.2
    1.6
    2.3
    4.2
    CO
    99
    37
    60
    60
    40
    CO AF
    = 132
    = 49
    = 65
    = 67
    = 50
    EFF
    79
    81
    84
    83
    81
    ExAir
    31
    31
    7.7
    11.5
    23.4
    CO2
    11.8
    11.8
    14.5
    13.98
    12.55
    AT
    53
    53
    53
    53
    53
    Net Stack
    559
    497
    457
    468
    514
    Comment
    yellow spot
    Pre test
    1 smoke
    trace
    trace -1.43
    @HydronicMike Once the other readings were steady CO was flat as well.
    CO during burner start
    CO during burner shuts down
    I truly appreciate everyone's help and will appreciate any further comments
    SuperTech
  • Big Ed_4
    After you burn out the left over carbon , if you get a CO reading burning oil you have smoke .. Gas you will get CO before smoke .
    Robert_H
    Yeah. The old soot flying around can screw things up for a while.
    Robert_HSuperTechBig Ed_4
  • Robert_H
    Robert_H Posts: 369
    yeah, I was surprised that it cleared up that much in two days. You learn something every day if work at it.