Yellow spot after soot up

Options
Robert_H
Robert_H Member Posts: 349

I had a no heat call tonight that turned out to be a soot up. Buderus G115WS/3 with a Riello. It had been cleaned by someone last month and now was caked with Nice (if soot can be nice) soft soot.

After cleaning I checked pump pressure which was at 150 and I adjusted it to 185(spec) it had a 75-60A which I replaced with a 55-60A. I also set the air band and head position to spec for starters.

MFR

Buderus

model

G115WS/3

Burner

Riello

nozzle

55-60A

Pump Pres

185

Head, static plate

1

Firing Rate

= 0.75

Draft Breach

Draft OF

0.03

Tstack

612

O2

5.2

CO

99

CO AF

= 132

EFF

79

ExAir

31

CO2

11.8

AT

53

Net Stack

559

Comment

yellow spot

I had to push the head forward to "1" to get the CO to drop (spec is 2)

The CO readings are dropping, and are Post Soot up so I feel they will continue to drop.

I pulled yellow spot on every smoke test I did, that and the High net stack temps tells me high excess air yet, Excess air is a little low for what I usually end up with at a final reading. O2 and CO2 are reasonable.

The head is clean and when I had the door open I pulled the gun and really cleaned the tube and especially the venturi area with a brush and rag. So I don't think there is an impingement issue.

I don't get yellow on the smoke test very often and the few times I have it was confirmed with high excess air. but not the case here.

Ill be back to check Combustion and smoke on Tuesday.

Educate me! Happy Saint Patrick's Day

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,711

    Probably some residual soot could be messing with the readings. It may calm down when you go back

    Big Ed_4Robert_H
  • HydronicMike
    HydronicMike Member Posts: 398

    Is the OF draft .03 negative? Should be slightly positive. What was it at the breech?
    High stack could also be from high draft.

    When you go back I’d put the head position back to where it was and recheck combustion.
    Also CO numbers at light off, at steady state-rising, falling, stable, and at shut down.

    Robert_H
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,602

    I asked that question here about 30 years ago.

    I think the answer is still the same:

    TOO MUCH AIR. Your flame is too lean. the residual soot that was not vacuumed out completely is making you have a #2 or higher smoke test from an otherwise clean flame. After a week, go back and reduce the air mixture. (probably from the #2 setting back to #1 setting) and see if you get a zero smoke with no yellow spot. That yellow spot is unburned oil vapor that is getting blown out by the excess air

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mattmia2Robert_H
  • SuperTech
    SuperTech Member Posts: 2,669

    I agree that it is yellow from too much air. On that particular boiler with a Riello burner I am usually able to obtain a true zero smoke in the range of 12.5-13.5% CO2. Make sure to set the draft so it's slightly positive over fire, +.01-.03".

    Robert_H
  • Robert_H
    Robert_H Member Posts: 349

    that draft reading is positive that's why I didn't put a minus sign in front of it.

    Also, correction I moved the head to position 3 not position one.

  • Robert_H
    Robert_H Member Posts: 349

    I read the post last night when I got home and have it bookmarked!

    "That yellow spot is unburned oil vapor that is getting blown out by the excess air" that is a perfect explanation.

    EdTheHeaterMan
  • Big Ed_4
    Big Ed_4 Member Posts: 3,557

    The A or hollow nozzle was designed for the Shell head burner used in 60's and 70's. The flame pattern of the hollow is fragile . Carbon buld up on the flame cone and cracked female porcelains was a normal issue with Shellheads . The standard for fuel oil has changed since then and not for the better Using a W or semi solid is a safer bet .. Just a tip

    Good Luck

    There was an error rendering this rich post.

    MaxMercyRobert_Hrick in Alaska
  • Steamhead
    Steamhead Member Posts: 18,770

    The Riello OEM Spec guide is a bit confused, it shows either an A or B nozzle for that boiler:

    https://www.riello.com/north-america/service/technical-support/oem-settings

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

    Robert_H
  • Robert_H
    Robert_H Member Posts: 349

    I saw that. Otherwise it matches the burner label

  • Robert_H
    Robert_H Member Posts: 349

    Thank you!

    So do you not use "A" nozzles at all?

    I noticed that the Riello OEM quide dose spec "W" nozzles in some applications

  • Steamhead
    Steamhead Member Posts: 18,770

    I use hollow nozzles where appropriate.

    That OEM spec might be talking about a Danfoss AB nozzle, which is roughly equivalent to a Delavan W.

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

  • Robert_H
    Robert_H Member Posts: 349
    edited March 9

    It definatly says "A/B" In my mind that means A or B but Im not inside the Tech Writers head :D

    MaxMercy
  • Robert_H
    Robert_H Member Posts: 349
    edited March 10

    Returned today to re-setup the burner. To start I pulled smoke and checked combustion the numbers were nearly identical and I was pleased to see that CO an CO/AF had improved. Also the yellow spot was clear which I didn't expect.

    1000007280.jpg

    I set the head back to position "2" and decreased air, getting a 1 smoke and back to a trace. Then adjusted the draft for .03 OF and readjusted to a trace, added air to get -1.5ish CO2 and check for a zero smoke.

    @SuperTech my final CO2 came in as you commented

    measurement description is at bottom of table

    Date

    3/8/26

    3/10/26

    3/10/26

    3/10/26

    3/10/26

    Time

    20:54

    10:11

    10:25

    10:29

    11:00

    MFR

    Buderus

    Buderus

    Buderus

    Buderus

    Buderus

    model

    G115WS/3

    G115WS/3

    G115WS/3

    G115WS/3

    G115WS/3

    Burner

    Riello

    Riello

    Riello

    Riello

    Riello

    nozzle

    55-60A

    55-60A

    55-60A

    55-60A

    55-60A

    Pump Pres

    185

    185

    185

    185

    185

    Head/static plate

    3

    3

    2

    2

    2

    Firing Rate

    = 0.75

    = 0.75

    = 0.75

    = 0.75

    = 0.75

    Draft Breach

    -0.04

    Draft OF

    0.03

    0.03

    Tstack

    612

    550

    510

    521

    567

    O2

    5.2

    5.2

    1.6

    2.3

    4.2

    CO

    99

    37

    60

    60

    40

    CO AF

    = 132

    = 49

    = 65

    = 67

    = 50

    EFF

    79

    81

    84

    83

    81

    ExAir

    31

    31

    7.7

    11.5

    23.4

    CO2

    11.8

    11.8

    14.5

    13.98

    12.55

    AT

    53

    53

    53

    53

    53

    Net Stack

    559

    497

    457

    468

    514

    Comment

    yellow spot

    Pre test

    1 smoke

    trace

    trace -1.43

    @HydronicMike Once the other readings were steady CO was flat as well.

    CO during burner start

    1000007274.jpg

    CO during burner shuts down

    1000007279.jpg

    I truly appreciate everyone's help and will appreciate any further comments

    SuperTech
  • Big Ed_4
    Big Ed_4 Member Posts: 3,557

    After you burn out the left over carbon , if you get a CO reading burning oil you have smoke .. Gas you will get CO before smoke .

    There was an error rendering this rich post.

    Robert_H
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,711

    Yeah. The old soot flying around can screw things up for a while.

    Robert_HSuperTechBig Ed_4
  • Robert_H
    Robert_H Member Posts: 349

    yeah, I was surprised that it cleared up that much in two days. You learn something every day if work at it.