Yellow Smoke Spot
EdTheHeaterMan
Member Posts: 9,130
What causes the Yellow/Amber smoke spot on an oil burner smoke test? Is this an indication of a combustion problem that should be corrected? How do you go about correcting the problem?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Comments
-
Yellow Smoke Spot
excessive air causing un burned fuel to pass to the flue. Cut back on your co2 a half a degree and check again (reduce air)
al0 -
yellow spot
it could very well be too much air. but it could also be either the wrong spray pattern,and or degree(wrong nozzle). even the end cone or retension head may be carbon'd up.0 -
Another thing
I've run into a yellowish discoloration caused by condensation. Once in a while with a good furnace (thermopride) and a good burner (riello) on the right duct system, I've had efficiencies get up in the high 88% range causing moisture in the flue gas. I don't know if that's what you have there but we've seen it more than a few times. They just have to be opened up a tad on the air shutter and it disappears at the expense of a point or two in efficiency.0 -
yellow smoke
Yellow smoke readings usually mean too much air. What's the O2 or CO2 reading? If carbon dioxide is low (or oxygen is high) you need to close the air shutter a little at a time til it cleans up. CO2 below 8% is low. You didn't mention what type of burner you have; is it flame retension?0 -
I would be looking for an impingement in the combustion area especially near the retention ring or you have way too much air to the flame. Try running at about 11 1/2% CO2.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements