Replacing / Installing main line air vents on one pipe gas steam system
I found 2 locations for air vents on my steam system basement piping. One has an air vent, the other does not.
What size of air vent's should I buy? I didn't want to pull them off without having replacements in hand.
Also pulling them off - as simple as PB Blaster and plumbing wrench? Or are they likely to be "steam welded" on like other steam fittings?
Thanks.
    Jamie Hall Posts: 27,738
    What vent -- or vents -- to put on depends on the length and diameter of the steam mains. Can you get us that information?
    As to replacing them -- you should be able to get those off OK. Sometimes just some muscle, sometimes PB Blaster or other confections (someone on the Wall swears by a 50/50 mix of acetone and WD-40) and patience. They'll usually give up. That said, that location is not really ideal for vents, though it can work. What you need to do is protect them from condensate and possible water hammer, and the easiest way to do that is to raise them and offset them using a few nipples and elbows.
    branimal
  • branimal
    branimal Posts: 304
    Diameter is 2".
    The 90 with the vent on it is 55-60 ft from the boiler.
    The 90 without the vent (just a plug) is 10-15 ft from the boiler.
  • BobC
    BobC Posts: 5,576
    You will probably need a lot more venting on the 60 ft main. I would try putting that Gorton #1 on the 15 ft main and then a B&J BigMouth on the long main. Getting the plug out of that one main is likely to be a real chore.
    Bob
    3PSI gauge
    branimalGrallert
  • branimal
    branimal Posts: 304
    Bob
    Thanks Bob. The B&J big mouth is $84 vs $28 for the Gorton #1 at supplyhouse.com. Worth the extra money?
  • JUGHNE
    JUGHNE Posts: 11,633
    You would need 5 of your $28 G1's to equal one B&J BM vent.
    Don't need a calculator for this one.
    branimal
  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,648
    YES! Will pay for itself in no time.
    branimal
    > Bob
    Barnes and Jones says Amazon is the cheapest place to get a big mouth since that where they sell them directly to the customer. You also get free shipping and possibly no tax depending where you live.
    branimal
  • branimal
    branimal Posts: 304
    B&J big mouth it is. Hopefully that plug on the main will come out with an impact wrench and square bit. If I can even fit it in there. Thx
  • branimal
    branimal Posts: 304
    I know this is an old thread, but I'm finally getting around to get these main vents on. The plug on the 90 won't budge. I tried heating it with MApp gas (60 seconds) and loosening with a large crescent wrench with a cheater bar). I smacked the plug with hammer, tried tightening it, and repeated heating. Nothing. I don't want to risk any damage to the system b/c its freezing outsise.
    I tried loosening the little vent on the far (60ft) vent. Didn't budge. Can I heat the black nipple with mapp gas to get it off? PB Blaster?
    Plan is to upsize to 3/4 (reducer), put a 90 el + nipple +90 el + nipple then Big mouth vent to get it away from the condensate.
  • AdmiralYoda
    AdmiralYoda Posts: 801
    More heat, you won't overdo it unless you are using an oxy-acetylene torch! Penetrants like PB Blaster probably won't help much because of the pipe dope or teflon tape in the way.
    What length pipewrench are you using? Try adding a section of pipe to the wrench for more leverage.
    I was in the same situation as you with a 1.5" plug at the end of my main. PB Blaster didn't help at all. I used a 3ft pipe wrench and it took some effort but it finally budged.
    branimal
    ethicalpaul Posts: 8,993
    crescent wrench not my fave. Try an 18 or 24” pipe wrench on the base of the vent.
    The vent is brass, it will give
    branimal
  • bburd
    bburd Posts: 1,324
    The piping to your new vent must be pitched to drain condensate back to the main. This may be a bit tricky if you're using elbows. You don't want condensate pooling in there.
    Bburd
    branimal
  • branimal
    branimal Posts: 304
    I'll give the stuck vent a shot with an 18" pipe wrench.
    Good point…. I was thinking I just needed to distance the vent from that elbow on the main. But I guess condensate will shoot up my 3/4" 90 elbows vent path. I'll use a couple of 45els so I have pitch. Thanks for the heads up.
    Condensate doesn't shoot up, it trickles. The "slug of water" is mythical.
    Now if you have full-on carryover, you could have gallons of water getting forcefully shoved through your main, but that is a problem you should solve, not work around with extra pipe and fittings on your main vent.
    branimal
  • branimal
    branimal Posts: 304
    edited January 29
    What do you mean by "full-on carryover"?
    Btw, got that vent loose with a pipe wrench.
    AdmiralYodaethicalpaul
    I mean the boiler puking gallons of water up into the main resulting in a dramatic drop in water level as viewed from the gauge glass, like in this classic video from early in my steam experience:
    https://youtu.be/WSRvvNQ5WLc?si=cHCNs7W_WFEBAHQj&t=46
  • bburd
    bburd Posts: 1,324
    edited January 29
    Regardless of the condensate load, we do not want it to pool in low spots in the vent runout where venting air may push it into the vent itself and make it spit, or worse.
    Bburd
    I agree and never meant to say otherwise 🙂
  • dabrakeman
    dabrakeman Posts: 1,022
  • bburd
    bburd Posts: 1,324
    Certainly, using two 90s at each joint. But that is not the piping plan the OP described above. The way I read it, he seemed to be proposing one 90 per elbow.
    Bburd
  • branimal
    branimal Posts: 304
    Got it installed. Not an ideal location as it's b/w the joist bays.
    On the first boiler cycle, I saw a little steam and a gurgle of water come out of the Big Mouth vent. Next cycle I saw just a bit of steam.
    Next step is to remove the 3/4 plug off the steam main vent location closer to the boiler. Will try more mapp gas on the 90el and use a pipe wrench plus cheater bar. I have a Gorton #1 on hand.
  • branimal
    branimal Posts: 304
    I've been heating this 90 el vent port with Mapp gas, allowing it to cool for 5 minutes, and spraying PB Blaster on the plug. I've done this 2x a day since Monday. Am I just spinning my wheels here? Will patience win over this plug? I am not in a rush. I'm willing to do this for another week if it will help.
    FYI: monday i tried removing the plug with a pipe wrench and a cheater bar, with a backup wrench on the pipe. No luck.
    edited February 5
    Please expand on "no luck"
    What happened with the big wrench on it?
    I personally don't think PBBlaster can get in there. How hot did you get it? Did it glow? I'd try the wrench while it's still hot.
    Did you try tightening in addition to loosening?
    branimal
  • branimal
    branimal Posts: 304
    "No luck" - I gave it a good push with a 4' cheater and it didn't budge. I'm afraid of breaking something. I had a cheater on the backup wrench so it was an awkward position. Maybe I'll phone a friend to hold the backup wrench. Again, I'm in no rush to get this done.
    In terms of heat, I heat it for 2 minutes at a time. So - no where near glowing. Again I'm afraid of damaging that 90 el. Can I get it glowing without compromising the fitting?
    Am I being too cautious?
    I have tried the tighten trick. Maybe i'll give that another shot.
    I think you're being too cautious, but it's not my house in cold weather so I completely understand. I have helped friends remove stuff sometimes who aren't so familiar with pipes and they are much physically stronger than I am but they can't do it (or they think they can't). It's about knowing (with at least some certainty) how much force stuff can take and needs to take.
    You can put the wrench on so that the force is in line with the main and then you need less or no counter on it. It's difficult in a corner like that, I completely understand what you mean about awkward.
    I've never had to heat anything to remove it, but I hear people say it should be glowing. Heat the tee not just the plug, if you heat the plug it will enlarge it (I don't honestly know how much that matters). People say the idea is by heating it you kind of crystalize the oxidation so it can be crushed by applying the wrench on it.
    It doesn't hurt to wait until it's warmer, for sure
    branimal
  • AdmiralYoda
    edited February 5
    You won't overheat that metal unless you are using an oxy/acetylene torch! Get it as hot as you can and give the plug some good hits with a hammer. Repeat the heating and hammering multiple times.
    Putting PB Blaster on while super hot is beneficial (aside from the smoke). It boils and really wicks its way into the threads. If a penetrant is going to help in this situation, heating first will give it a chance.
    And try remove the plug when it is as hot as can be.
    branimal