Should I choose the local guys or the HH guy who's >30 min away for my boiler replacement?

Options

I just want someone who will be responsive if I have issues. One guy is HH listed, and while I trust he'd do a good job, he's not around the corner if I need help, and I live in a high traffic area that can be a PITA during rush hours. The locals are more old school, they sent a guy who really didn't know his stuff for checking out the situation, and photographed it for the real techs. He asked if I had bled the steam radiators! But they've been here forever, I used them decades ago, the owner was a kid in his 20s then working for his dad, who has since retired but still advises. But when Dad came years ago about another system, he didn't do an EDR, he just wanted to install the same size boiler, which seemed a red flag to me. I chose someone else, who then went out of business!

OTOH the biggest local heating supply house recommended them when I asked for a 'steam whisperer'. They do a lot of work in an area with lots of steam. The HH guy is almost 30% more, but that's not a deal killer for me. I just want the pain to end! Unfortunately I've had multiple experiences with heat guys being undependable, so I want to get this right, if that's possible.

Comments

  • KC_Jones
    KC_Jones Member Posts: 5,916

    My honest answer starts with a question. How many problems are you planning on having? If you get a poor install that increases the chances of needing something. I shouldn't talk about dependability of my own system, lets just say it's been good (knock on wood). A cast iron steam boiler has very little that could actually go wrong with it, I personally would not factor in how far away the company was, I'd want the best install my money could buy because that will end up being the most important part. If some of the local are outright telling you things that you know are wrong, honestly, why even think about them? It won't get better when they start turning wrenches.

    I'm not sure which HH contractor you are talking about so I can't comment directly on that. I can say, in my area, there is no one I would trust to walk into my house….ever. That's why I ended up doing my own. More recently I assisted with picking a contractor for a dual boiler replacement in a historic mansion owned by the Historical Society (I'm on the board). We hired someone from another state, the local "talent" was so poor. We aren't worried about response times, we are worried about proper install and dependability.

    Choose wisely.

    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    mattmia2leonzMad Dog_2GroundUp
  • ethicalpaul
    ethicalpaul Member Posts: 8,405

    30 minutes is nothing

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    PrecaudIntplm.
  • Jack_alltrades
    Jack_alltrades Member Posts: 6

    The last install was by someone who by all accounts was totally qualified, and yet I was left high and dry. Fool me once! And sorry, but distance does matter. I've been told by numerous qualified techs that travel time to me is too far for them to take the job. I get it, who would want to travel 2-3 hrs round trip for a service call? I have friends in the mountains that have a huge problem getting mechanical work done.

    It's extremely hard to be a knowledgeable consumer of this stuff. I am a pretty good DIY, and understand the system, but a full install is beyond me.

  • Jack_alltrades
    Jack_alltrades Member Posts: 6

    It boggles my mind that someone can work on steam as part of their business for 1/4 century and still not know what they're doing, but I know it's totally possible.

    Mad Dog_2
  • ethicalpaul
    ethicalpaul Member Posts: 8,405
    edited January 27

    respectfully you first said 30+ minutes. To that I say again, “that’s nothing”

    But then you changed it to 2-3 hours.

    Now regarding DIY you may be underestimating yourself. I installed my own boiler and I’m a wimpy computer programmer who had zero prior pipefitting experience

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,769
    edited January 27

    @ethicalpaul said: I installed my own boiler and I’m a wimpy computer programmer who had zero prior pipefitting experience

    I have to agree with Paul on this. especially the WIMPY part. But all joking aside, Paul did a great job with his Beautiful Assistant (See profile Pic). Paul had made a study of his residential boiler and has ended up with some really informative videos. 

    You may be able to handle your new boiler install with his help over video chat of some type.  You will need to get friendly with the local supply house and purchase the boiler from them in order to get someone there to help with all the fittings you will need for the install. 

    I wouldn't mind helping you either.

    Sometimes if you want something done right , you got to do it yourself.

    EDIT:

    https://www.velocityboilerworks.com/product/steam-boiler-piping-kits/

    Screenshot 2026-01-27 at 6.21.18 PM.png

    If you find a supplier that sells Crown Boiler (By Velocity Boiler Works in Philadelphia) they have a piping KIT that has all the pipe fittings and nipples you need to install that boiler properly. Just order the kit and put the pieces together like an Erector Set® or LEGO® project. Easier than you think.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    ethicalpaulbjohnhy
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,914

    If the job is installed right then you will have minimal problems. I think you answered you own question. Why would you "hope" it will be installed right by someone local?

    mattmia2IronmanMad Dog_2ethicalpaul
  • Jack_alltrades
    Jack_alltrades Member Posts: 6

    Look, for all sorts of reasons I'm not going to DIY this. But you sort of are inadvertently arguing for the local heating guy. I mean if you think I can do a decent job if I study up, then a guy who's been doing it for at least 25 years has to be far better than that at baseline, right? And the local supply house guys know who the clowns are, they'd not recommend them, I don't think, unless they thought they knew their stuff at least decently.

    ethicalpaul
  • Jack_alltrades
    Jack_alltrades Member Posts: 6

    I'm cynical because of the experience I described of hiring a specialist and it going south AND him not being around to make it right. Some things you can't control, but you have to try your best to make good decisions.

  • 109A_5
    109A_5 Member Posts: 3,695

    I guess the answer is pick the best contractor that is willing to come to your home to do the job. If you are out if their service radius it seems that they are off the list of possible contractors.

    Maybe get references and view some of their steam work.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Gabriel82
    Gabriel82 Member Posts: 19

    You hire the person most qualified and who you know for sure he has done good jobs in the past with satisfied customers.

    If he is that good at what he does he won't have to visit you every week 😁

    I'm talking from experience with house roof...

    I did once one mistake and had to pay twice for fixing the problem previous guy caused AND new materials...

    I'm done with incompetents 😑

    Bad to the Bone

    Song by George Thorogood & The Destroyers ‧ 1982

  • ethicalpaul
    ethicalpaul Member Posts: 8,405
    edited January 28

    no, that’s not at all what I’m arguing. Time and again I have seen with my own eyes the work that “some local guy” does, even the licensed ones!!

    They don’t even open the manual and they seemingly purposely do everything wrong. And they ALWAYS say “I’ve been doing this for 30 years, never had a complaint”

    The reason I was able to succeed was because I cared and because I followed the instructions. And I observed what not to do from those homeowners who came to this forum asking for help after the fact.

    I’m warning you right now because I care about you as a fellow human—do not go with some local guy over someone whose work can be vouched for who is a little farther away

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    dabrakemanEdTheHeaterManmattmia2
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,551

    Once the boiler is correctly installed, emergency troubleshooting is mostly straightforward. Bad gas control, bad ignition module, bad transformer, bad flame sensor.... There is really not that much to go wrong with a properly installed steam boiler. Things like proper maintenance, and cleaning, which are very important, can always be scheduled. To me, it's a no-brainer. I would really recommend stay away from a company that recommends bleeding steam radiators. That's like a cook telling you to put red food coloring into a recipe, to make it look blue.

    ethicalpaulmattmia2MaxMercy
  • ScottSecor
    ScottSecor Member Posts: 1,023

    I agree with using the contractor that knows his stuff. Get it done the right way the first time. Doing annual maintenance might be handled from the local guy?

    We regularly charge for travel time for service and installs. The majority of our business is local, but we certainly drive thirty or more minutes to job sites. We are up front with the added cost to drive to and from jobsites. I am not trying to cause a debate, but should I (as the owner) take a hit financially to take care of job an hour away? For the record., my employees get paid to drive to and from the job.

    mattmia2Larry Weingarten
  • AdmiralYoda
    AdmiralYoda Member Posts: 758
    edited January 28

    Most times the boiler comes ready to go with the pressure controls, probe LWCO, gas valve, etc already installed. The magic is in the proper sizing of the boiler and the correct piping, like the header configuration, proper pipe sizing and the hartford loop.

    Go with a HH guy and you are likely guaranteed to have it installed correctly to at least the minimum manufacturers recommendations and probably even better.

    Any problem that arises will not be due to the install it will be due to the pre-mature failure of a device on the boiler that may or may not ever happen. Any local HVAC tech should be handle that.

    Go with the local people and you are going to get the "I've been doing it this way for 50 years" install. The manual will never get read and it would be a miracle if it is installed even close to correctly. When the problems arise they will be due to the installation and you'll be running around in circles. And your boiler will probably be even more oversized and you'll be fighting short cycling and higher fuel costs for the next 30 years.

    If the HH person says they will come….let them do it. For general maintenance or emergency repairs let the locals do it.

    mattmia2ethicalpaul
  • mattmia2
    mattmia2 Member Posts: 16,058

    i don't know about any local tech, i was watching a video last night of a tech that was still wanting to replace the control board even after he found a a pressure switch filled with condensate and drained it out and the furnace started firing again. he made the video and presumably thought he was doing it right.

  • Intplm.
    Intplm. Member Posts: 2,917
    edited January 29

    @DanHolohan says above "Knowledge is worth more than geography",really says it all.

    I work with a company that takes calls from far away distances that you mention. The reason, we have a reputation for doing things right. And we continue to do the right thing for our customers. its about maintaining a good reputation.

    I would go with the most knowledgable company. And you say you are a doityourselfer. Once the new system is up and running, you can do some of the necessary repairs. With the right install/installer there won't be many repairs, or, anything for you to do..

    One other thing. On this site there is a book you can purchase called "We got steam heat" as a DIY'er I think you will enjoy it.

    ethicalpaulmattmia2
  • Jack_alltrades
    Jack_alltrades Member Posts: 6

    Thanks Dan. I was assuming they sent him mainly to look, photograph, and bring info back to the actually skilled guys who were busy working on customers systems during this very cold time. I'm thinking I would insist on a real conversation with the boss before considering awarding them the job.

    @Intplm. I have The Art.. on the bookshelf next to me as I type! How is We Got.. different?

    I read in an old thread there's basically no difference between a 'Williamson by W-M' and a regular W-M PEG boiler. Still true?

    Thanks for all the food for thought guys. This is nerve wracking. The span of the pricing, and how high it is compared to like 2011 is mind blowing. My high bid is literally 4x the 2011 price I got!

  • mattmia2
    mattmia2 Member Posts: 16,058

    the price of metals has skyrocketed since then as demand has skyrocketed. the piece of type m 3/4" copper pipe that was $5 when i bought my house 25 years ago is now $35.

  • Intplm.
    Intplm. Member Posts: 2,917

    @Jack_alltrades The book "We got steam heat" made me think of you when reading your posts.

    Its best to go to the store on this sight and read the description. It is tremendously helpful.

  • HVACNUT
    HVACNUT Member Posts: 7,312

    We schedule 8-12 or 12-4. We're not all sitting around waiting for the bell to ring and go slide down the fire pole to the emergency. We're out there. There's really no issue here IMO. I work the forks of Long Island and it takes me an hour and a half travel between calls sometimes. I often hop across Shelter Island. Go for the knowledge and reputation. Proximity plays a very small role.

    Long Beach EdIntplm.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,914

    Most of my work was commercial which is different, but we had plenty of customers and installs and service that were a 2-hour drive one way and they were happy to have us.

    Unfortunately for me I seemed to frequently be the long-distance guy. 35000 miles per year driving just the work van.

  • mattmia2
    mattmia2 Member Posts: 16,058

    you should've complained more like the people that didn't get those jobs did…

    EdTheHeaterMan
  • KC_Jones
    KC_Jones Member Posts: 5,916

    I'd suggest you start with doing an EDR survey of the system and then select the proper size boiler from that data. It's a simple task and we can happily assist as needed. This way when you have a conversation with the local guy that is one talking point you can be educated on. If they aren't going to size it properly, that is a big red flag for me. Many don't size properly and it's extremely important to do so.

    Here's an anecdotal story from 2014 when my boiler failed. My old boiler had been running for well over 10 years with 2 burners removed. Those burners were sitting right on top of the boiler in plain sight. When I had one contractor come over for an estimate, he went down and looked at the boiler, checked all the radiators then left. I got the quote and he had a boiler that was bigger than the one I had if all the burners were installed. I have an EDR of 265 and he wanted to install a boiler rated at 408 sq ft, so massively oversized. That was the point I started looking at doing it myself and found this website.

    Not trying to convince you to do it yourself, just giving you information to understand, don't assume these people know what they are doing. Don't assume they have educated themselves. Just don't assume. After the sizing you can make sure they put in the contract to install to manufacturers spec, that gives you leverage if they do something wrong. I also live in a town with virtually no talent in the trades in a state that didn't have state wide building codes until 2003, so I have serious trust issues. Our fire department is quite busy and frustrated though…that's not a joke.

    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    Intplm.
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,810
    edited January 29

    I think the real issue here is that it will cost you 30% more to have the knowledgeable firm do the job correctly. I read this between the lines of your posts.

    Pay once, cry once. Quality work costs a lot more than the garbage I see most shops installing.

    Your local man demonstrated he knows nothing about steam.

    The choice is simple. You'll have this boiler for many years and the proper installation will be much cheaper and less troublesome in the long run.

    clammyepmillermattmia2
  • AdmiralYoda
    AdmiralYoda Member Posts: 758
    edited January 29

    If you go local with a typical HVAC company it wouldn't surprise me when you post the pictures here with copper header pipes, a bullhead Tee and an incorrect Hartford loop. The next question that is typically posted here are….what are my options to have the HVAC correct problems X, Y, and Z.

    One solution is to tell the HVAC guy exactly how you want it installed….as if saying "follow the manual" isn't sufficient. And whether the tech says it out loud or internally he will say "Okay homeowner, I've been doing this for 50 years. I'll do it how I've always done it."

    Then you'll spend countless hours stressing about it, learning what should have been done differently/correctly and then spin your wheels trying to get it fixed or paying another company to fix it properly.

    Often times the 30% difference for having a qualified steam pro to do the work will be the same cost as a poorly installed system that needs additional fixing or may even be cheaper in the long run. And no headaches.

    Pay once, cry once.

    mattmia2
  • ChrisJ
    ChrisJ Member Posts: 17,162

    Asking if you bled the steam radiators, and didn't want to check the size of the boiler.

    If what you've told us is true, you literally have a better chance of winning the Mega Millions / PowerBall than you do of getting a properly sized steam boiler properly installed by them from the sound of it. And that's 1 in 290,472,336.


    Sizing the boiler is extremely important as is installing it correctly. That of course being followed by a good cleaning. With the guy you mentioned, you'll likely get an oversized boiler, pipped completely wrong, full of oil with absolutely no way to skim it and they won't know how to fix it. You'll get the typical "It's an old system, they're always noisy, it's normal".

    The way I see it you have two choices.

    Hire the HH guy, or learn and install it yourself assuming your area allows it.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.