Old Watts LWCO sill available
GW
GW Member Posts: 5,152
is there any likelihood I could rebuild this low water cut off?
Or, chuck it and put on a 67
it’s a millivolt so that adds to the joy
The lady somehow overfilled the boiler, I took 20 gallons out of it, brought it down to the very bottom of the boiler still wouldn’t shut off.
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com
    mattmia2 Member Posts: 15,984
    it is millivolt but it is all wired in romex?
    you could probably take it apart and clean, the float is probably just hung up on muck it although replacing it with a MM would be a great idea for safety reasons.
    GW
    Steamhead Member Posts: 18,317
    That Watts hasn't been made in a long time. Get a 67-G, not a regular 67- the G is millivolt rated.
    Consulting
    GW
  • Intplm.
    Intplm. Member Posts: 2,906
    edited January 26
    Disconnect the copper tubing off of the top and use a hose from a sillcock or any source of street pressure and run water through the top. That should flush the thing clean and get it working.
    GW
  • tim smith
    tim smith Member Posts: 2,902
    Old Roberts Gordon burner, worked on many of those over the years. Agree on the Macdonal Miller 67-G with quick connects. Supply house is out of stock but cheaper than others. Not avail till around february 11th. https://www.supplyhouse.com/Mcdonnell-Miller-149600-67-G-67-Float-Type-Low-Water-Cut-off-for-millivolt-service-Steam?srsltid=AfmBOoq3m8nT5e2fZVDmT9PO_xSAmXMtLJkk00wNVatR0kXE3YtvlMue
    Looks like maybe State supply has one or more in stock, you would need to verify.
    https://www.statesupply.com/mh1066?srsltid=AfmBOopIPUDeVFFjYlVIFAPvFENvPurDzQn9EmOvJBXzHZkQufckwvmP
    GW
    sometimes stuff that supplyhouse.com shows as out of stock or with long lead times miraculously shows up when you order it
    GW
  • GW
    @tim smith a couple years ago I posted the same boiler on the wall, I believe. We are chewing through powerpiles, every couple years we have to replace. Somebody mentioned, might’ve been you, we are overheating the powerpile. And there was some gadget that was there at one point, no longer there, that kept the from it from overheating.
    Does that make sense? Can you think of any way that we could make the power pile last longer?
    tia
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    edited 3:17AM
    some here have sad that the baso thermopiles are better quality than the wr or residio resideo? residewell?
    GW
    109A_5 Member Posts: 3,684
    I have cleaned my M&M 67 twice in 50 years. I bet that LWCO could be cleaned, you may have to make some custom gaskets. I stopped using the paper gaskets, although they are available for the M&M 67. I made reusable gaskets out of 1/32" silicone rubber sheet material. Makes the job easier.
    EBEBRATT-Ed Member Posts: 19,881
    edited 6:01AM
    @GW the Watts is still listed on their web site. Don't know if parts are available. looks like a Smith model 24. They lasted forever.
    How many wires into the LWCO. That looks like K & T wiring or maybe old Romex.
    Vapor system.
    GW
    either early romex or individual wires in loom.
    EBEBRATT-Ed
    @mattmia2
    Looks like loom to me as well. That's why I asked about # of wires in LWCO. Loom it's two Romex is 4. Looks like conduit going up overhead from burner so probably a JB up overhead
    If you look at the cable placement, it looks like there is only one cable to the pressure switch, so I would say two wires per cable assembly (or loom).
    One wire per cable assembly would not work unless they used the piping for a return at the pressure switch.
  • GW
    pretty sure its Resideo in there now. It's definitely overheating. The burner drops out, and I then measure the MV (where the pp connects to gas valve, and the stat-safety is off the vale/disconnected). The numbers slowly climb on the off cycle. When the numbers climb enough, the main burner comes back on (when I reconnect the stat-safetys). And the process repeats.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • GW
    Nice, I guess making gaskets can't be super difficult, I will google that 1/32" silicone rubber sheet material
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    you can probably just use permatex too unless the gasket is shimming some critical clearance but i doubt it is in something like that.
  • GW
    I ordered the 1/32"
    I forgot to get some exacto knifes, i'll hit up amazon again
    Not sure why I am trying to keep this on the cheap, the lady pays full price and she also kicks cash tips. Yesterday she asks" do you have kids". I say I have two adult kids and two grandchildren. She pops a $50 in my hand and says this is for your grand kids 😊
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    ethicalpaulratio
    I used something like this. It was years ago when I bought it.
    Red Silicone Rubber Sheet 60A 1/32 x 9 x 12 Inch Made in USA Gasket Material
    https://www.ebay.com/itm/234098580147
    When I take it apart I just rinse it off with warm water, and reuse it, no more gasket scraping. So far I like it.