do you need two circulators in a primary secondary system

Options
Mail4tommo
Mail4tommo Member Posts: 15

My question is..

For a primary secondary system do you NEED 2 circulators ?? one for the boiler loop and one for the secondary loop? I ask because I believe i saw in Dan Holohan book a pri/sec set up and in the image there was only the one circulator and it was on the secondary side on the supply manifold…

I just need to get this right/wrong image out of my head..

Thanks in advance

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,881

    two loops need 2 circulators. primary loop , secondary loop.

    Mail4tommoIronman
  • Jamie Hall
    Jamie Hall Member Posts: 27,001

    Yes. You do need at least two. But one of them may be part of the boiler and its trim, which can be misleading. Whether you need only one on the secondary or more than one depends on how the system is zoned and the controls for the zoning.

    The other place you need a mandatory circulator is on the output (mixed) side of a mixing valve or tempering valve.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Mail4tommoIronman
  • Mail4tommo
    Mail4tommo Member Posts: 15

    @Jamie Hall That was my understanding as well.. I just was a little mislead by either my imagination or my want to have things easy🤣

    Thanks @EBEBRATT-Ed

  • hot_rod
    hot_rod Member Posts: 27,065

    here is an example where 3 or more circs are required.

    This is a dedicated series primary loop system. It is series because the zone pumps are in series to one another

    Boiler loop, primary loop and zone pumps

    If the expansion tank was connected at the boilers pump, then the boiler loop is the primary loop.

    IMG_1405.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mail4tommo
  • Mail4tommo
    Mail4tommo Member Posts: 15

    thank you for the example.

    So if the "primary circ was removed" and the expansion tank was piped before the boiler loop circ, would this still work? (Im going with no) I'm assuming not because of hydraulic separation.

  • hot_rod
    hot_rod Member Posts: 27,065

    here are some options where only two circs are required. These show multiple zone pumps, but the concept is still two separate piping circuits with either closely spaced tees, or a separator acting as the tees.

    The series P/S two posts up would not work with the primary loop removed.

    IMG_1409.jpeg IMG_1411.jpeg

    more about “separation” here

    https://www.caleffi.com/sites/default/files/media/external-file/Idronics_15_NA_Separation%20in%20hydronic%20systems.pdf

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • psb75
    psb75 Member Posts: 1,109

    Question for hot_rod: do these last two schematics still qualify as "pumping away"?

    ethicalpaul
  • Jamie Hall
    Jamie Hall Member Posts: 27,001

    I"m sure @hot_rod will answer on the "pumping away" — but in my mind they both would. It's as much a matter of figuring out where the lowest pressure in the system is likely to be, and placing your expansion tank (and automatic feed, if used) at that location. And both of those arrangements do that

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Member Posts: 27,065

    The key point on any piping with multiple pumps or zones is the header pipe needs to be LARGE. Sized to handle the flow of all the pumps combined, ideally at a low velocity around 2-4 fps.

    The large (low head loss) header pipes become the "extension" of the PONPC

    In this example lets say the 3 large circs are 8 gpm each, 4 gpm on the smaller, so 32 gpm total through the header.

    Screenshot 2026-01-21 at 8.40.54 AM.png

    So 2" type M copper would be the choice, just over 3 fps velocity.

    Screenshot 2026-01-21 at 8.33.07 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • GroundUp
    GroundUp Member Posts: 2,482

    Yes, but you may be referring to a "bypass" piping system as was common on 80% boilers to help mix return water on low temp systems. The bypass system only needs one circulator, but it has a limited use. True P/S piping needs at least two circulators and that is not negotiable.