Near-boiler piping : what do you think ?
Hi Dan,
I saw your YouTube video on near boiler piping and wanted to know what you think of my current setup for my new boiler installed 3 months ago to replace a very old one. Both units Weil McLain.
Check the diagram in the manual for the pipe sizes. The header may be too small. The part we can see looks good if the mains are parallel flow(have separate returns from the far end of the mains) but we need to see the part wedged between the wall and the boiler. It will be a pain to service, they should have slid it out some or turned it 90 degrees or both but unless that was specified it would be hard to argue that it is a problem.
The manual says the EG 40 ( model I have ) needs a 2.5” riser and header pipe. Here are pics of what’s between the wall and the boiler
thanks !
make sure the pipe is 2.5". i think it is but i'm not good at judging pipe sizes in pictures.
It definitely has a “2” cast on the ell.
Bob Boan
To bad he faced the service side towards the wall ,possibly should have spun it 90 degrees hopefully the next service tech is not large . I usually try to make the sight glass and lwco on a side that has access but ya cant always get what you want or need .Piping looks fine as for the size its about what 99 % do cause no one is really checking usually and steam is quite forgiving and most of the time it no noticeable difference not everyone wants eye candy they just want it to work . i would gather that larger risers and header would have increased the price somewhat and when your bidding against others you bid what they do unless ya dont mind loosing most of the jobs ya look cause your more money and usually higher priced bids end in the waste paper basket .Its always easier to let the home owner make the decision over using a doom and gloom pressure to get the job that's never been my angle .
peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
the circumference of the riser and header pipes is approximately 7.75” . So dividing that by 3.1416, the diameter comes out to 2.42 inches.
The boiler generates a given amount of steam. If the pipes are too small the velocity of the steam (think miles/hour) is moving faster than it should be. This can cause the steam to pull water out of the boiler and create an unstable water line.
Check the boiler manual and show it to the installer. The manufacturer of the boiler tests the boiler and specifies what size pipe to use. For good operation the mGS instructions need to be followed.
Would you want to drive a 1 ton pick up truck with Volkswagen tires on it?
Most contractors don’t have the equipment to thread anything above 2”, so that’s the maximum size you get.
Bob Boan
With that boiler if they ran two 2" risers fairly high, I'd bet a 2" header would perform fine.
That lets them use the tools they have to get the job done and a happy customer.
when I did that work NO we didn’t like threading over 2” BUT, it wasn’t my choice. The boss paid the labor to do it.
2 1/2 and up took longer, a little more break time.
for something like that you can easily buy pre-threaded nipples. the risers to the main and to the equalizer can be reduced.
2 1/2 and up is a PITA but you do what you have to do. With something like that the most important thing is to be able to visualize and know how to measure.
That job is a cinch if you know what you are doing. You measure it up buy what you can (which in this case is everything) and have a supply house cut and thread some 2 1/2 inch that you measure up > In this case you wouldn't have to.
Here is a chiller I did about 10 years ago. I was about 62 at that time. We cut back the supply and return 6" pipe and welded on 2 flanges. Ran 6" vic into the chiller.
Picture going to a job 1 1/2 hours from the shop lugging a groover and something to cut 6" pipe with all the pipe and fittings. You not lugging those tools to the roof so you would be up and down the ships ladder all day. No fun. Even with two guys it would suck.
So I spent 2 hours measuring it up and ordering the fittings. Turned my sketch in to the shop and had the pipe cut and grooved there. there.
Loaded it into my truck and went back myself. Pulled it all up to the roof with a rope myself and piped it. That's why I am a mess now.
I had the welder build the angle Iron support the same day we put the flanges on.
Its all about knowing how to measure.
the manual says the minimum recommended riser and header pipe diameters is 2.5 inches. Would it be better if we went to 3 inches instead ?
the boiler tapings are probably 2.5" so it would be complicated to do it to the risers. if i were to upsize anything i'd only do it for the header itself
No, it would not be better.
@EBEBRATT-Ed wrote:
I have yet to hear of a boiler piped to the MFG minimum that doesn't work right. And I keep asking.
You're going to like my next video!
If the header is 2.5” , does the supply main pipe also need to be the same diameter ?
What does the manual say? We could go look up the manual for your model and find out for you, but you should try it, it's a good learning exercise.
Oh Sorry I misread what you were asking. Yeah, the boiler manual won't say what your main should be, it's not their responsibility, and you might have multiple mains. Usually the main was designed back when the house was built or when steam was added to it and is probably fine. The piping problems we see here are usually the near-boiler piping that was re-done by some rando installer when the previous boiler failed.
I'm sure Dan's book The Lost Art of Steam Heating tells what size main is appropriate for a given amount of radiation that it supports.
the larger header size is to slow the steam down in the header and make it easier for any water entrained in the steam to drop out. after the header it doesn't need to be slower.
- 87.7K THE MAIN WALL
- 127 Chimneys & Flues
- 121 Geothermal
- 79 Pipe Deterioration
- 396 Solar
- 17 Recall Announcements
