smart thermostats
I have an oil fired hydronic boiler with three zones running off a taco sr503 relay, the old thermostats all connect with 18/2 wire(red & white). The new thermostats require a c wire Other than running new 18/5 wire through the house, how would I wire these to the switching relay. I know I can use a nest power connector but can the relay handle three of them.
    HVACNUT Member Posts: 7,308
    I had it out with a client yesterday who just installed four 4th gen Nest thermostats. No common, and the main zone isolation heat relay keeps dropping out every 5 seconds. 27 vac going to R on the Nest. 22 vac coming back on W. He's swearing up and down he was told he doesn't need a Common, and the old Nest thermostats worked fine. I rewired the thermostat and air handler and used Yellow as Common, and the problem mysteriously disappeared. Now he's calling his electrician. I love everybody.
    As far as YOUR scenario, @DaveM , I believe there's only a 15 va transformer in the SR503, so, no. The Nest 4 draws about 4 va, so three Nests wouldn't work. Or it would be cutting it very close. A seperate 40 va transformer and isolation relay would be needed. I'm not sure if Taco would allow you to replace the 15 va with a 40 va.
  • DaveM
    DaveM Member Posts: 77
    can you help with a simple wiring diagram Thanks so much
    EBEBRATT-Ed Member Posts: 19,892
    @DaveM PM @EdTheHeaterMan he probably already has the drawing you need stashed somewhere on this site. In the meantime
    I will post a simplified drawing I made which will give you an idea
    If you add a 40 va transformer you can power multiple Nest thermostats and relays off 1 transformer.
    EdTheHeaterMan Member Posts: 11,759
    edited December 2025
    If you are asking if the transformer in the Taco SR503 can power everything in the control along with three Nest thermostats I would say NO. You are better off using the power connector or a separate transformer to power the thermostat in each room like this one: Smart Thermostat transformer. You can plug it in a wall socket in the room where the thermostat is located and connect the R and C directly to the Rc and C on the thermostat.  Like this:
    You want to use the Rc or R terminal when you have only heat connected to the smart thermostat.  The only time to use the Rh terminal is when there are separate air conditioning controls and heating controls in order to keep the transformers separate.  With heat only this is not the case.
    109A_5 Member Posts: 3,691
    "I know I can use a nest power connector but can the relay handle three of them."
    I believe it depends on which version of the SR503 you have.
    The latest version:
    bjohnhy
  • DaveM
    thanks Ed the wall plug-in is not an option taco makes one that connects at the relay itself. I might look into the new version which has larger transformer. How would I wire an external transformer next to the sr503 thanks for all your help
  • pjg
    pjg Member Posts: 5
    Good video on this subject, 3 ecobees no problem with 15 va transformer.
    I would go with the venstar color touch they draw less than the ecobee.
    DaveM
  • DaveM
    I understand needing a separate transformer to power my three thermostats but I don’t understand how to wire it to the sr503 relay I only have 18/2 wire coming down from each thermostat to the boiler room thanks for the help
  • pjg
    pjg Member Posts: 5
    Running a new 18/5 wire to 1st and 2nd floor is what I did, 1st floor should be easy, 2nd floor will be a little harder but can be done.
    Jamie Hall Member Posts: 27,014
    Can't be done with 2 wire. You need to run at least 3 — and I'd run 5 — wires, as @pjg said.
    @DaveM
    As others have mentioned you need 3 wires for heating, more if you have cooling. How old is your house?
    In the old days thermostat wires were fished in with no staples holding the wire. If that's the case, you can tie a new cable to the old and pull a new cable in.
    If the wires are stapled to the studs then its more work. Try pulling gently on the cable and see if it moves easily
  • DaveM
    thank you all for the help. I’ve just been reading about adding a diode on the switching relay between W and COM or a nest power connector which adds a C wire. Was thinking if that would work
    They have all kinds of work arounds. I haven't herd of one that works.
  • DaveM
    I’m sure you’re right as usual I’m going to give taco tech a call and see what he says
    I'm pretty sure it is not a diode. Sometimes a 1000 Ohm 1/2 Watt resistor. The resistance and the wattage may be situational dependent. 3 wires is best practice.
    The NEST power connector may work.
    It can be done with 2 wires, but it'll cost more. And it won't be Nest. Honeywell with RedLink uses 2 wire, 24 volt powered thermostats connected to an interface. They use their own router for a wireless WiFi connection.
  • DaveM
    this is becoming more ridiculous than its worth I’m going to tell my daughter to get normal Honeywell thermostats, she doesn’t need to control her thermostat from Guam
    pecmsgHVACNUTrick in Alaska
    If Dad is the one who was going to install the Nests, Dad will now be the one house watching.
  • DaveM
    you got it my brother. What ever happened to old school if Ai is so intelligent why is it artificial
  • DaveM
    someone just told me about Fast-stat do you guys think that will work
    There are a number of gadgets — including this one —which provide the constant 24 vvolt AC power to the wireless thermostats. They do work. They require a 120 volt AC power supply. There are also kludges which claim to be able to power these thermostats across two existing wires. Some of them work, too. Some of the time.
  • DaveM
    I think the fast -stat does not require 120volts ac it has a transmitter at the thermostat and connects to the taco switching relay using the com port
  • SlamDunk
    SlamDunk Member Posts: 1,796
    The nest gen 4 is an interesting device. I bought one for a second home we have so we can fire up the furnace or A C before we leave. We have a 2025 HVAC unit and the common wasnt hooked to the common terminal on the board so I didnt hook it up on the nest( The original tstat didnt need it.)And, it worked. It worked for a month until we went back and I hooked the C on both ends. Apparently, the nest can "steal" a common from "elsewhere" to stay charged.
  • yellowdog
    yellowdog Member Posts: 287
    I have had success with fast stats and taco relays.
    Nest may work without a common….for a while.
    My Nephew wired one to an oil burner cad cell relay and you know how tiny those transformers are.
    Somehow, he swore it worked for a year or so until it went dead. I am surprised the cad cell control survived. I hooked it up with a separate trans former and a Rib relay 5 years ago. no issue yet
  • SlamDunk
    @EBEBRATT-Ed , I have read of them discharging without a common but my brother has had one on his boiler for years without any issues and no common. Like I said, I find it to be an interesting tstat. I like that you can also get nest co and smoke detectors that would shut a furnace/ boiler off.
  • DaveM
    ok guys I ran new 18/5 to two thermostats on first floor and used the taco power connector for the one the second floor working perfectly so far Taco sr503 with 15va transformer handling the load
    rick in Alaskabjohnhy
    I guess my question would be; will it work correctly when it is zero degrees outside and you need the heat. Since the charge / discharge duty cycle is a bit different since the call for heat duty cycle is different.
  • DaveM
    what are you talking about
    3 NEST, so 6 VA consumed continuously doing nothing. Assuming it is actually a 15 VA transformer in your SR503, only 9 VA left for the internal load of the SR503. Not sure what a "taco power connector" is, I'm guessing it consumes power also. If there is no C wire to to second floor NEST then that battery needs to be topped off when there is no call for heat, an additional load.
    So you added at least 6VA of extra load to a transformer that was sized to probably just power the internal load of the SR503. The colder it gets outside the 'Call for Heat' duty cycle gets longer so less time for the now undersized transformer to cool down.
    The newer versions of the SR503 have more robust transformer options.
    @SlamDunk I don't think my Nephews oil burner controls transformer was large enough to recharge the Nest but it worked for a year that way.
    I added a transformer and a relay, and it must be 3-4 years now and no issues.
    Hooked up without a C wire I guess they are supposed to charge on the off cycle. I just like asure fix.